Re: Circuit breaker tripping
Well,
Amps
= Watts/
Volts
, so, Amps = 1200W/120V = 10 Amps. That's right on the mark. I can certainly see the breaker blowing here. You might consider turning the intensity level down five or ten percent to allow some room in the power draw.