Quote:
Originally Posted by ecglstec
If you plug in to an outlet with two straight slits and one hole in the bottom ( 15 amp outlet) then you can only load your pack to 1800 watts total before you blow the circuit breaker at the venue.

Here is why:

Watts = Volts * Amps

Watts = x
Volts = 120 (Common US voltage)
Amps = 15 (Your plug is a 15 amp plug)

x = 120 * 15
x = 1800 Watts
Yes - but only if the internal wiring in your dimmer is rated for 15A!

If not, (depending upon the internal protection) you could seriously damage your dimmer.

If in doubt - ALWAYS follow the instructions on the dimmer.

Zac - 1000W is 1000W regardless of the percentage of dimming. Triac and SCR dimmers work by turning the lamp on and off at a high rate. Our eyes then see this “high speed flashing” as changes in the intensity of the light.
__________________
You are not the messiah wolf, you're just a very naughty boy.