Hi all. I’ve searched the Control Booth info db and have found some valuable info but not quite what I'm looking for. I hope you can help.

I'm designing the lighting and sound for ‘the Sound of Music’ being performed in an out door venue this summer.

The site of the make shift amphitheater is in the back of a resort hotel. There is a grassy hillside for the audience to sit and a flat gravel area at the base of the hill where the stage will be built. The area does not have any electrical power.

As I'm designing the lighting and sound I figure I'm going to need at least 120 amps @ 120v. 100 amps for lights and 20 for sound.

There is a gazebo to one side of the seating area about 80 feet away which has both 240v and 120v outlets. There is also a large condo building about 100 feet behind the stage area.

The resort maintenance manager told me that he has 2 construction breakout boxes (?) with 125 foot 240v cables. From what I understand, these construction boxes are designed when contractors are building a house and power has been brought to the property line. You plug the 240v cable to the electrical service and the other plugs in to the breakout box. The box then has several 20Amp 120v outlets and a 30A 240v outlet. I don’t know about earth ground…but, I'm using 2 arch trusses on the hillside and using guy-wires with steel stakes in the ground to hold the arches up, so I figure I can bolt a wire on a stake and use it for local earth ground…I don’t know if this would matter or not.

So the manager says he can plug one cable into the gazebo 240v service and another to the condo building and give me 6- 20A 120v circuits.

Has anyone out there worked on a similar electrical setup?

We are using 6 DMX 4ch. dimmer packs. I'm wondering if the electrical setup might confuse the DMX signal?

Any advice is appreciated.
Reply With Quote
Old April 28th, 2009, 07:46 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,535
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Temp electrical service at amphitheater

Quote:
Originally Posted by taneglaus View Post
...Has anyone out there worked on a similar electrical setup?
We are using 6 DMX 4ch. dimmer packs. I'm wondering if the electrical setup might confuse the DMX signal?
Done similar many times. The electrical setup will have no effect on the DMX signal.

You're skirting on a taboo subject here, taneglaus (see FAQ/Content Policies/Safety), but as long as a http://www.controlbooth.com/forums/g...n-per-nec.html (no reason that can't be the resort maintenance manager) does all the electrical set-up and connections, and you just plug into to NEMA 5-15/20 outlets, you shouldn't have a problem.

Quote:
...so I figure I can bolt a wire on a stake and use it for local earth ground...
DO NOT go taking matters into your own hands to create your own earth ground. Leave that up to the http://www.controlbooth.com/forums/g...n-per-nec.html.
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
Old April 28th, 2009, 07:48 PM
avkid's Avatar
 Premium Member 

 
Join Date: Feb 2004
Location: Endicott, NY
Posts: 4,631
Thanks: 50
Thanked 59 Times in 53 Posts
Blog Entries: 1
Send a message via AIM to avkid Send a message via Skype™ to avkid
Default Re: Temp electrical service at amphitheater

Your dimmers don't care where their power comes from as long as the voltage and frequency are correct.
__________________
Philip LaDue
Endicott Audio
ADR Audio
"The loudspeaker has more of an effect on the sound we hear than anything else in the audio reproduction chain"- Alan Frank
Reply With Quote
Old April 28th, 2009, 09:43 PM
Footer's Avatar
Senior Team
 Premium Member 
 
Join Date: Nov 2005
Location: Saratoga Springs, NY
Posts: 3,753
Thanks: 1
Thanked 134 Times in 129 Posts
Default Re: Temp electrical service at amphitheater

You're dealing with a spider box. Odds are it will be a Hubbell box. This is a pretty common thing when dealing with large amounts of portable power around a building during construction.

http://www.grainger.com/Grainger/items/4D572
__________________
Kyle Van Sandt
Technical Director
Home Made Theater
Van Sandt Designs

Last edited by derekleffew; April 28th, 2009 at 11:16 PM.. Reason: added pic
Reply With Quote
Old April 29th, 2009, 03:41 AM
gafftaper's Avatar
Senior Team
 Premium Member 
 
Join Date: Jan 2006
Location: Seattle, Washington
Posts: 6,652
Thanks: 46
Thanked 231 Times in 191 Posts
Blog Entries: 6
Default Re: Temp electrical service at amphitheater

Only 20 amps for sound? That's a pretty small rig. You sure?
__________________
Community College Technical Director
Reply With Quote
Old April 29th, 2009, 01:45 PM

 
Join Date: Apr 2009
Posts: 7
Thanks: 0
Thanked 0 Times in 0 Posts
Smiley Re: Temp electrical service at amphitheater

I appreciate your input. I appreciate the controlbooth.com’s policy on not endorsing electrical setups due to potential of electrical shock and/or property damage. I wasn’t asking for a ‘stamp of approval’ although I now realize I wasn’t quite clear on what my ? was…

Often times I find that when troubled with something, if I pose the problem to someone else, during the process of openly describing the problem I often answer my own ?

After submitting the post I realized that I'm nervous about this electrical setup because I've never worked with this type of ‘spider box’…the image is correct. But as I thought about it, I wouldn’t have any problem with running a 100’ 12g extension cord and pulling 20 amps through it…this setup is about the same thing just much more power. In effect I'm using a high power extension cord with a power strip that has circuit breakers on each circuit.

I guess I was most concerned that when we got it all setup that there would be voltage fluctuations or not enough current capability or poor earth ground…or whatever. But I've worked with long extension cords before without problem so as long as the resorts electrical service has been installed correctly, and I believe is has, then I should be ok. And I've looked up a local electrical contractor who will stop buy to check it all out. So I'm feeling much better about this setup.

The sound is only reinforcement so I don’t have massive power amps, a 24 ch. mixer, 4 JBL powered speaker cabinets, and 4 stage monitors running off of a 250w/ch. power amp. So 20 amps for sound is close, I might need 10 more amps for the monitor amp…I hope. I've never had to budget my power so tightly like I am at this venue.

Thanks again for your feedback.
Reply With Quote
Old April 29th, 2009, 11:31 PM
 Premium Member 

 
Join Date: Jun 2005
Location: Malden MA
Posts: 112
Thanks: 2
Thanked 5 Times in 5 Posts
Default Re: Temp electrical service at amphitheater

If you really want to play it safe, you can use an optoisolated splitter on your DMX with a separate branch feeding the dimmers plugged into each spider box. I would also make sure all of the audio gear is on the same spider to avoid problems caused by different grounds.
Reply With Quote
Old April 30th, 2009, 12:08 AM

 
Join Date: Feb 2009
Location: SW Ontario, Canada
Posts: 189
Thanks: 0
Thanked 4 Times in 4 Posts
Default Re: Temp electrical service at amphitheater

Quote:
so I figure I can bolt a wire on a stake and use it for local earth ground…I don’t know if this would matter or not.
When it comes to bonds and grounding it is necessary to deal with the authorities, especially when using more than one service as source.

I am glad to hear that you have already now decided to deal with an electrician. I'm not sure about the local authorities where you are doing your show but I know that the Ontario Electrical Safety Authority can be very, may I say militant on issues of that nature.

There are lots of things you can do, but you'll get in lots of trouble if you do it without a proper permit AND inspection, with the inspectors permission on that particular setup in advance.
Reply With Quote
Old May 5th, 2009, 02:57 PM
gafftaper's Avatar
Senior Team
 Premium Member 
 
Join Date: Jan 2006
Location: Seattle, Washington
Posts: 6,652
Thanks: 46
Thanked 231 Times in 191 Posts
Blog Entries: 6
Default Re: Temp electrical service at amphitheater

Caution is always a good thing when dealing with electricty. However, if you get the assistance of a certified professional electrician, using the spider box will be safe and reliable. It's done all the time in the industry for applications just like your own.
__________________
Community College Technical Director
Reply With Quote
Old May 17th, 2009, 10:08 PM
TimmyP1955's Avatar

 
Join Date: Oct 2006
Location: Indianapolis
Posts: 229
Thanks: 0
Thanked 6 Times in 6 Posts
Send a message via AIM to TimmyP1955
Default Re: Temp electrical service at amphitheater

Quote:
Originally Posted by taneglaus View Post
But as I thought about it, I wouldn’t have any problem with running a 100’ 12g extension cord and pulling 20 amps through it…this setup is about the same thing just much more power. In effect I'm using a high power extension cord with a power strip that has circuit breakers on each circuit.
You'll get a lot of voltage drop. I once had to run my PA on a single 100' run of 10 gauge. I had a 5V drop with the system at idle. According to manufacturers specs on the gear, I was drawing less than 10 amps.
Reply With Quote
Reply

Tags
amphitheater, electrical, service, temp

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lamp Questions ship Lighting 57 August 4th, 2009 09:14 AM
Cable and plug types for stage jumpers ship Lighting 39 June 10th, 2009 02:29 AM
Lamps derekleffew Collaborative Articles 0 October 9th, 2007 01:59 PM
Cable Repair ship Lighting 15 February 22nd, 2004 04:51 AM