I hear a lot that you shouldn't run nonlinear loads on the same breaker as a more sensitive load due to the harmonics. How does it help to put the nonlinear load on a different circuit? If you trace backwards through the breakers, it goes to the same bus bar.
Reply With Quote
Old August 25th, 2009, 12:54 PM

 
Join Date: Dec 2006
Location: Maryland
Posts: 333
Thanks: 9
Thanked 21 Times in 20 Posts
Default Re: Keeping Power Separate

In an ideal world, the non-linear loads would be on a different transformer...

It's true that when mixing loads on the same panel, some of the harmonics will get to the other loads. But, they will be at a much lower level compared to being at the end of the same wire with the non-linear load.

-Fred
Reply With Quote
Old August 25th, 2009, 02:33 PM
Cashwalker's Avatar

 
Join Date: Apr 2009
Posts: 31
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Keeping Power Separate

I think it's more practical that at least the different types of loads be on different phases, even if the neutrals all end up on the same buss bar.

When I run a Battle of the Bands, I go as far as running the lights from one panel, the mixing equipment from another, and the band equipment from a third panel.
__________________
Rob Cashman
TD LD SD TP
The Minstrel Players
Northport, NY
Reply With Quote
Old August 26th, 2009, 03:03 AM
TimmyP1955's Avatar

 
Join Date: Oct 2006
Location: Indianapolis
Posts: 229
Thanks: 0
Thanked 6 Times in 6 Posts
Send a message via AIM to TimmyP1955
Default Re: Keeping Power Separate

Quote:
Originally Posted by Cashwalker View Post
I think it's more practical that at least the different types of loads be on different phases, even if the neutrals all end up on the same buss bar.

When I run a Battle of the Bands, I go as far as running the lights from one panel, the mixing equipment from another, and the band equipment from a third panel.
That can cause some nasty "mic bites" owing to voltage differences between the PA ground and the backline ground. Of course if either the PA or the backline are not grounded properly this won't happen, but you then have bigger potential problems on your hands.
Reply With Quote
Old August 26th, 2009, 12:15 PM

 
Join Date: Mar 2009
Location: Gonarch's Lair
Posts: 85
Thanks: 3
Thanked 2 Times in 2 Posts
Default Re: Keeping Power Separate

What's so special about the breakers that they attenuate harmonics?
Reply With Quote
Old August 26th, 2009, 03:26 PM

 
Join Date: Feb 2009
Location: SW Ontario, Canada
Posts: 189
Thanks: 0
Thanked 4 Times in 4 Posts
Default Re: Keeping Power Separate

Nothing. Breakers do not attenuate harmonics.

The best solution is to run non-linear loads off of a separate transformer. In a lot of larger installs there is a separate transformer for Audio, and a separate transformer for lighting. These go to individual panels that distrubute to their loads.
The Audio panel often has receptacles all over the venue, and because of such they must be clearly labelled.

It is commonplace to run audio all off of a common phase in temporary situations. This minimizes the effect of the harmonics since the audio gear is all "common".
Reply With Quote
Old August 26th, 2009, 04:39 PM

 
Join Date: Dec 2006
Location: Maryland
Posts: 333
Thanks: 9
Thanked 21 Times in 20 Posts
Default Re: Keeping Power Separate

Quote:
Originally Posted by headcrab View Post
What's so special about the breakers that they attenuate harmonics?
Nothing. But, long pieces of wire will. So, getting as much wire between the the noise source and the sensitive load is what is desired. (If you can't be on different transformers, or at least different phases.)

-Fred
Reply With Quote
The Following User Says Thank You to fredthe For This Useful Post:
headcrab (August 26th, 2009)
Reply

Tags
keeping, power, separate

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Your opinions of Cordless Drill-Drivers ship Scenery 84 January 29th, 2009 12:49 AM
New Booth Foxinabox10 Get Organized! 64 November 11th, 2008 11:35 PM
Homemade Electric on/off box TupeloTechie Lighting 21 January 24th, 2007 02:03 AM
Dimming mercury lamps... mixsa Lighting 1 October 13th, 2005 01:19 AM


All times are UTC -4. The time now is 10:29 PM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.1 
Advertisement System V2.6 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80