Old February 13th, 2009, 02:07 PM

 
Join Date: May 2008
Posts: 488
Thanks: 14
Thanked 9 Times in 9 Posts
Default How Big a Generator?

Okay so we are trying to figure out how big (power wise) of a generator we need for an outdoor charity event. The event is about 2 months away, but we need to spec the genny now. Unfortunately, the genny will be powering all of the staging as well as regular power needs for concessions, radios, tvs, ect. We also don't have the final specs for the staging and won't for at least a month. From the specs I have we will have 5-10kW of MLs, a sound system for a large outdoor event, and some video from a projector. The 'other' not technical stuff will probably need 10kW to be safe.

How big of a generator do we need? Do we need some kind of seperate (intermediate) breaker between the genny and the 'other' stuff so if they put something bad or overload it we don't lose the power to staging?

Note: We will have someone there qualified to do the hookup, so that's not an issue.
Reply With Quote
Old February 13th, 2009, 03:02 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,535
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: How Big a Generator?

Isn't this a question better posed to your generator rental vendor?

See also:
Aggreko: Rental Generators, Heating & Cooling, and Oil-Free Air
Power Generators for Rent, Emergency Generator on Rent, Generator Rentals
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
Old February 13th, 2009, 04:27 PM
hsaunier's Avatar

 
Join Date: Jan 2008
Location: Northwest Ohio
Posts: 105
Thanks: 9
Thanked 6 Times in 6 Posts
Default Re: How Big a Generator?

Most often 2 seperate genies are used. One for light and the other for audio. Put all the conscession stuff on the light genie. Short of that make sure a very, very, good earth ground has been placed (deep). Many times the audio gear does not like lights operating on the same source, dimmers will make an obvious buzzing.
__________________
Hugh Saunier, Technical Director

Niswonger PAC of NW Ohio
10700 SR 118
Van Wert, Ohio 45891

tech@npacvw.org

419-238-6722

www.npacvw.org
Reply With Quote
Old February 13th, 2009, 06:04 PM

 
Join Date: May 2008
Posts: 488
Thanks: 14
Thanked 9 Times in 9 Posts
Default Re: How Big a Generator?

While I agree that asking the generator supplier would be a good idea, they aren't quite so helpful when we're trying to get them to either donate the use of the equiptment or give us a huge discount. We pretty much have to go in saying this is what we need. I'm trying to figure out how much extra we need (I read in FOH magazine that you want 2x what you think you will need). As I sain in the Sound forums-- we DON'T know what the sound setup will be yet.
Reply With Quote
Old February 14th, 2009, 01:02 PM
CBmod
 Premium Member 
 
Join Date: Jul 2005
Location: Sydney, Australia
Posts: 1,799
Thanks: 13
Thanked 37 Times in 33 Posts
Default Re: How Big a Generator?

Getting a genny that's too big can bite you as it will be idling and probably won't maintain it's frequency as well as it would under load. Expect also that your voltages will be a lil hot.

So issue no 1 is that you spec generator sizes in kVA not kW. They are not the same. kW = kVA * Power factor. You could assume a 0.8 power factor, most people use that sort of a number for rough guesses. Actual PF will vary dependent on your load characteristics. The closer to 1 the more efficient...

Are any of your concessions (right so showing my flag now - I take concessions to be stalls, food vans etc?) using urns, toasters, microwaves, hot water units or any such power hogs? How far away will they be from the genny? Do you have means to distribute the power that will work and meet relevant codes?

The trcik if you do use a single genny for lights and sound if you can is to distribute your loads such that audio is one one phase and the lights are mostly on the other two.

Now to slighlty conytradict the last statement, balancing loads on generators is far more important than load balancing for a mains install because the demand by other devices on three phase tends to even out and a few amps is neither here nor there in the couple of hundred (or double that in the US?) amps at the nearest stepdown transformer... Get it wrong on a generator and the thing will not be a happy camper.

Re intermediate breaker question, you'll need a power distribution system rated to your needs and code compliant and all that fun stuff...
Reply With Quote
Old February 14th, 2009, 03:53 PM
len len is offline
 Premium Member 

 
Join Date: Oct 2004
Location: Chicagoland
Posts: 1,397
Thanks: 8
Thanked 32 Times in 28 Posts
Default Re: How Big a Generator?

If you know the rough demands of everything and where approximately it will be within the venue (area), I'd pass this along to a couple of rental companies and ask for their input. They may see some things that you maybe didn't think of. IN my experience, rental vendors like to help, because they're trying to get you as a long term customer and they also don't want their equipment abused. Allowing them some input as opposed to saying (I need a genny with this output on this date. How much?) will build you some good will for the future as well.
__________________
http://www.chicagolightingdesign.com
"I don't feel it's healthy to keep your faults bottled up inside me." - Bucky Katt
Reply With Quote
Old February 14th, 2009, 04:12 PM
lieperjp's Avatar
 Premium Member 

 
Join Date: Mar 2008
Location: Jackson, WI and New Ulm, MN
Posts: 1,132
Thanks: 42
Thanked 20 Times in 17 Posts
Default Re: How Big a Generator?

Quote:
Originally Posted by Chris15 View Post
Are any of your concessions (right so showing my flag now - I take concessions to be stalls, food vans etc?) using urns, toasters, microwaves, hot water units or any such power hogs? How far away will they be from the genny? Do you have means to distribute the power that will work and meet relevant codes?
Chris brings up an excellent point. What are you using for Concessions? Don't forget food warmers like Nescos, refrigerators, nacho cheese warmers or popcorn machines. If you are getting a common concessions truck/trailer (i.e. small), most have a limit of 15 amps for food service and another 5-10 amps for lights. Of course, that doesn't stop you from bringing in your own electricity.

Also, to save money on this, definitely check with your local Pepsi or Coke distributor, (or adult beverage center) as they usually do free rentals on trailers if you buy their product and sell it exclusively. These even come with soda fountains, however all other equipment must be furnished by you.
__________________
I'm somewhere...
Reply With Quote
Old February 15th, 2009, 05:28 AM
 Premium Member 

 
Join Date: Sep 2007
Location: perth W Australia
Posts: 511
Thanks: 13
Thanked 16 Times in 14 Posts
Default Re: How Big a Generator?

The concessions are your friend, they will keep a base load on the genny, your sound load can go from virtually nothing to full draw over seconds and badly load the generator, moving lights are good on generators as they are a constant load, dimmers can be a nightmare, with changing loads and wave chopping and high neutral currents, they need serious attention.As a general rule if you have dimmers on a genny, load it up with everything you can find to ameliorate the problems.
__________________
David Ashton
All Things Theatre
Perth,Australia

"for every complex problem there is a solution which is neat, simple,and wrong"
H. L. Menken
Reply With Quote
Reply

Tags
big, generator

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How does AC have a hot and a neutral? Dustincoc Lighting 16 May 15th, 2008 02:09 AM
That DMX has a mind of its own. MircleWorker Lighting 22 November 11th, 2006 07:23 PM
Generator Power JP12687 Lighting 7 October 25th, 2005 12:44 PM