Does anybody know what general firecode is towards the length of time in between "Fireproofing" Stage curtains. Our school has been open 8 years and the curtains have not been proofed. I feel like I heard someone say it's 5years but I'm not entirely sure.

We also don't fireproof our sets because we don't have the money, and I'm basically our Drama Club's Tech Director. Should I be on my Director's tail about these things?
__________________
Ben Green
High School Stage Technician
Lighting Designer
Reply With Quote
Sponsored Links
  #2 (permalink)  
Old July 7th, 2008, 08:18 PM
lieperjp's Avatar
English Education Major
CB Supporter 

Technical Director
 
Join Date: Mar 2008
Location: Jackson, WI and New Ulm, MN
Posts: 577
Thanks: 34
Thanked 6 Times in 6 Posts
Default Re: Firecode

Quote:
Originally Posted by midgetgreen11 View Post
Does anybody know what general firecode is towards the length of time in between "Fireproofing" Stage curtains. Our school has been open 8 years and the curtains have not been proofed. I feel like I heard someone say it's 5years but I'm not entirely sure.

We also don't fireproof our sets because we don't have the money, and I'm basically our Drama Club's Tech Director. Should I be on my Director's tail about these things?
My church just recently purchased stage curtains, and the fire proofing is rated for 5 years. I don't know if it varies at all, though.

This is just an example. It may be different on your curtains.
__________________
Sophomore, Martin Luther College

"If food is the prose of the party, then lights are its poetry."
-Movie Joe Black

If you are learning as much as I am please consider donating to keep this wonderful website running!!!

Last edited by lieperjp; July 7th, 2008 at 09:26 PM..
Reply With Quote
  #3 (permalink)  
Old July 7th, 2008, 09:14 PM
Footer's Avatar
Senior Team

Technical Director
 
Join Date: Nov 2005
Location: Atlanta, GA
Posts: 2,619
Thanks: 1
Thanked 84 Times in 81 Posts
Default Re: Firecode

Look on the tag on the soft good, call that company and ask them. As far as what you need to "fireproof", most places just require backpainting everything, and in some instances require actual fireproof solution to be applied to all surfaces, usually though you have to be using pyro to get to that level.

BUT. YOU MUST CONTACT YOUR LOCAL FIREMARSHAL, RULES ARE DIFFERENT ACCROSS THE ENTIRE COUNTRY, DO NOT TAKE ANY ADVICE HERE FOR LAW, YOU MUST CONTACT YOUR LOCAL FIREMARSHAL.

Some places require a fire marshal inspection before every show opens, some don't. Just depends on the area and what type of suppression is available at the theatre.
Reply With Quote
  #4 (permalink)  
Old July 8th, 2008, 06:44 AM

Techie
 
Join Date: Feb 2008
Location: Ashland - Oregon
Posts: 76
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Firecode

Be careful when fireproofing a set, especially if you paint your stage. During my school's remount of Little Shop of Horrors we fireproofed the set because we had to move it, just in case, y'know. Anyways, now there are certain parts of the stage we can't paint over because of the substance we used on the set.
__________________
High School Lights Technician
Reply With Quote
  #5 (permalink)  
Old July 8th, 2008, 11:18 AM

Techie
 
Join Date: Oct 2007
Location: Greenville, SC
Posts: 56
Thanks: 2
Thanked 4 Times in 2 Posts
Default Re: Firecode

NFPA 701: Standard Methods of Fire Tests for Flame Propagation of Textiles and Films, is the federal standard, however your local Fire Department may have more strict rules, so definitely check with them. As for the length of the flame proofing, check with the original goods manufacturer. The goods may be inherently flame resistant so they may bee good for the life of the goods. If they are treated, such as some of mine, the substance that treated the goods would be what you need to check on. For example the stuff we used, Fire Block, is good indefinitely or 3 washes, and as I don't own a washer that can fit 672 sq.ft. of material I should never have to worry about re-treating them.
__________________
Scott Benson
Technical Director
The Peace Center
Reply With Quote
Sponsored Links
  #6 (permalink)  
Old July 15th, 2008, 06:22 PM

Techie
 
Join Date: Aug 2007
Location: Iowa
Posts: 118
Thanks: 1
Thanked 4 Times in 4 Posts
Default Re: Firecode

I'm 90% sure national code says soft good should be fireproofed every 5 years. I'm not aware of a code that requires fireproofing for sets and painted surfaces.
However, national code (NFPA 72) also gives local authority (your fire marshal or city inspector) the right to make any local rules he wants, so you MUST!!!! check with him/her. Beyond CODE concerns there is a manufacturer's tag that tells you how long the original fireproofing is good for, but that doesn't mean that subsequent fireproofing used the same materials or is good for as long. Records of each subsequent treatment should be maintained, including the life expectancy of the treatment.
Reply With Quote
  #7 (permalink)  
Old July 15th, 2008, 07:01 PM
museav's Avatar

Assistant TD
 
Join Date: Jul 2007
Location: Marietta, GA
Posts: 410
Thanks: 2
Thanked 26 Times in 26 Posts
Default Re: Firecode

Just to emphasize the checking with local officials, it is usually their interpretation of the code, not yours, that really matters, so best to get their interpretation.
__________________
Brad Weber
audio, audiovisual and acoustical consultant
www.museav.com
Reply With Quote
  #8 (permalink)  
Old July 15th, 2008, 08:29 PM
derekleffew's Avatar
Senior Team
CB Supporter 

Technical Director
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,014
Thanks: 76
Thanked 158 Times in 130 Posts
Default Re: Firecode

This document from RoseBrand may be helpful.

I have seen a Fire Marshal conduct a "match test" as follows: Cut a one inch square swatch of material from a seam or other unnoticed location. Hold a lit paper match to it for ten seconds. Once the flame is removed, the material must self-extinguish and not be able to sustain the flame on its own.
__________________
Better questions produce better answers!
Reply With Quote
  #9 (permalink)  
Old July 16th, 2008, 11:34 AM

Techie
 
Join Date: Jan 2008
Location: Rhode Island
Posts: 198
Thanks: 6
Thanked 1 Time in 1 Post
Send a message via AIM to midgetgreen11
Default Re: Firecode

I figured it out by looking at the tag on our 4 travelers. They are inherently flame proof. The weird thing is that our main drape is a split-drape that opens sideways, and it has like this plastic material on the back of it.

Would this be our fire curtain, because we do not have one that drops? Shouldn't a fire curtain be something that drops automatically?
__________________
Ben Green
High School Stage Technician
Lighting Designer
Reply With Quote
  #10 (permalink)  
Old July 16th, 2008, 01:39 PM

Technical Director
 
Join Date: Mar 2008
Location: CA
Posts: 503
Thanks: 0
Thanked 4 Times in 4 Posts
Default Re: Firecode

Ben - no, that wouldn't be a fire curtain. I think you need to have a talk with your TD or the head of your department as you should have one (a real one) in place legally. We had to have ours tested twice a year by the FM when I was back at the college. At the theater where I work now, it's pretty much up to us when we want to have it tested.
__________________
Char5lie

Check out our shows at: sctlivetheatre.org
Reply With Quote
Reply

Tags
firecode

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


All times are UTC -4. The time now is 04:02 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0
Powered by NuWiki v1.3 RC1 Copyright ©2006-2007, NuHit, LLC
Advertisement System V2.5 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54