ETC Sensor rack troubleshooting is being discussed in the ControlBooth Lighting and Electrics forum; hey guys so im having a problem with a 24 ch etc sensor rack i have one channel that is ...

  1. #1


    Join Date
    Mar 2010
    Location
    los angeles
    Occupation
    President/Owner
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Smiley ETC Sensor rack troubleshooting

    hey guys so im having a problem with a 24 ch etc sensor rack i have one channel that is on or off only no dimming at all. i have swapped out dimmer cards and main brain but still have problem with just one channel any suggestions ? i have take all cards and brain out cleaned it and now i have no idea what to do thanks

  2. #2


    Join Date
    Oct 2008
    Location
    Iowa USA
    Occupation
    Designer/Programmer/Systems Tech
    Posts
    454
    Thanks
    10
    Thanked 8 Times in 7 Posts

    Default re: ETC Sensor rack troubleshooting

    Check the dimming curve on both your console and your rack. I would first check your console, and if you tell us what console you are using we can walk you trough it.
    Either way you will want to change it back to a linear curve.
    - Will Brown
    Flickr - wbrownLD
    Portfolio - http://wbrown.squarespace.com

  3. #3


    Join Date
    Jan 2008
    Occupation
    Employee
    Posts
    140
    Thanks
    0
    Thanked 12 Times in 10 Posts

    Default re: ETC Sensor rack troubleshooting

    Is it a MPE or a CEM control module? (MPE has 3 dials for address, CEM has LCD display)

    If it's an MPE, then it's more than likely coming from the control console with that profile.

    If it's a CEM, you can go in and check the settings.
    SETUP
    DIMMER
    (scroll to the dimmer number with the up/down arrow keys)
    ENTER (moves to the bottom row of the LCD)
    (Use L/R arrows to MODE)
    You can have several choices here, but you want it to be "NORMAL" using the up/down arrows - more than likely it's in "SWITCHED"
    ENTER
    EXIT
    EXIT

  4. #4
     Premium Member 
    starksk's Avatar
    Join Date
    Mar 2009
    Location
    Madison, WI
    Occupation
    Technical Support Specialist
    Posts
    435
    Thanks
    49
    Thanked 81 Times in 65 Posts

    Default re: ETC Sensor rack troubleshooting

    Quote Originally Posted by oak1now View Post
    hey guys so im having a problem with a 24 ch etc sensor rack i have one channel that is on or off only no dimming at all. i have swapped out dimmer cards and main brain but still have problem with just one channel any suggestions ? i have take all cards and brain out cleaned it and now i have no idea what to do thanks
    Quote Originally Posted by jxgriffi View Post
    Is it a MPE or a CEM control module? (MPE has 3 dials for address, CEM has LCD display)

    If it's an MPE, then it's more than likely coming from the control console with that profile.

    If it's a CEM, you can go in and check the settings.
    ...
    To add to jxgriffi's advice, it could also be a CEM+ (LCD display with +,-, <, and Check Mark buttons).
    In that case, you would also want to check to make sure the correct firing mode is selected. You can do that by pressing the + key until you see [Dimmers] and then press the check mark. Scroll using the + or - keys until you see [Set Firing Mode] and press the check mark. Choose the range of dimmers you want to affect (if they should be all the same, I like to just select every dimmer to avoid missing that pesky one later on). There you can select the [Normal] firing mode and press the check mark.

    Alternately, there could be some other factors causing this issue. When you swapped modules around, did the problem stay with that one circuit or did it move with the module?

    Also what kind of console are you using? Could it be that there is a profile defined on that console that is telling the dimmer be on or off and not dimmed?

    If you set the level at the rack, does that circuit dim?

    Also, if you get stuck, please feel free to call us at 800-688-4116. We will be happy to talk through these troubleshooting steps (and more) with you.
    Kirk Starks
    Technical Support Specialist
    ETC, Inc.

  5. #5


    Join Date
    Mar 2010
    Location
    los angeles
    Occupation
    President/Owner
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default re: ETC Sensor rack troubleshooting

    i have an old brain the mpe so its just the 3 dials and when i swaped out cards it stays on the same port and doesnt go with the card. Same thing when i swaped out the mpe. I am using a lep 624 which i dont think it can be the problem but you guys let me know thanks

  6. #6


    Join Date
    Feb 2010
    Location
    Atlanta
    Occupation
    Owner/Proprietor
    Posts
    163
    Thanks
    10
    Thanked 7 Times in 7 Posts

    Default re: ETC Sensor rack troubleshooting

    Does the affected circuit dim when told to by the MPE directly?

    Jot down the rotary switch setting before you try this, so you can get back to proper operation after:

    Set the rotary switches to 830 and press [Reset]
    After you set the rotary switches to 830 and press [Reset] the MPE repeatedly fades each dimmer channel level up and down in numerical order. You set the speed with the last rotary switch on the right (higher setting = faster cycle).
    This fading continues until you end the test by setting the rotary switches back to their original position and pressing [Reset].

    Try that and watch the light on the affected circuit, does it dim up and down? That will tell you if it is an issue with the control console or with the configuration in the MPE.

    If it is a custom configuration, you would need someone at the factory, or a field service tech, to reprogram the MPE. Are all of your dimmer modules d20s? Are all of the loads incandescant? Is this a new problem, or one that has been like this for a while?

  7. #7
    CBmod  Premium Member 
    Grog12's Avatar
    Join Date
    Nov 2006
    Location
    Denver, CO
    Occupation
    Ballet Technical Director/Lighting Designer
    Posts
    2,580
    Thanks
    71
    Thanked 88 Times in 79 Posts

    Blog Entries
    3

    Default re: ETC Sensor rack troubleshooting

    oak1now when you say its not dimming does the light just pop on when you start to bring it up? Is it at 1% or at 100% that it just pops on?

    I never assume anything when dealing with new posters so please don't take this quesiton the wrong way: What kind of light is hooked up to the dimmer?

    Have you hooked another console up to the system to rule out the Leprecon?

    Are you outputting AMX or DMX from the board to the dimmers...if AMX do you have a converter in line?

    Is this a new problem or something that you've always dealt with?

    Pulling out the CEM/MPE of the rack isn't something to be taken lightly. There could also very well be a patch at the dimmers that is causing the module to be non-dim.

    What kind of of dimmer module is it?

    http://www.leprecon.com/productfiles...D612manual.pdf The manual to your console.
    6 P's to live by: Piss Poor Planning Prevents Positive Performance
    4 P's for LD's Producers Prefer Pretty Photographs.
    Nothing like being focused and desperate to make me remember how something works. ~Steve B
    It's not bullying--it's educating via the time-honored traditions of intimidation and humiliation. ~Derek

  8. #8


    Join Date
    Mar 2010
    Location
    los angeles
    Occupation
    President/Owner
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default re: ETC Sensor rack troubleshooting

    the 2 channels are pretty much on/off bring it up to 1% and it goes to 100%
    i have used other consoles from a m1 to hog ipc and hog3 and have had the same issue. I am using dmx. I bought the dimmer used and have always had that problem. I haven't had time to the test but as soon as i do i will post on the outcome thanks

  9. #9
     Premium Member 
    starksk's Avatar
    Join Date
    Mar 2009
    Location
    Madison, WI
    Occupation
    Technical Support Specialist
    Posts
    435
    Thanks
    49
    Thanked 81 Times in 65 Posts

    Default re: ETC Sensor rack troubleshooting

    Welcome back oak1now,

    A few questions:
    Which 2 circuits are affected by this issue?
    Are they in the same module?
    What type of module(s) are they?
    How is power connected to this rack? (Three phase or single(bi)-phase?)
    If you run diagnostic test 820, do these circuits dim?

    To run diagnostic test 820:
    Set the rotary switches to address 820.
    Press [Reset]
    All lights should fade from 0 to 100 percent and back
    To exit, set the rotary switches back to the proper starting address and press [Reset].
    Kirk Starks
    Technical Support Specialist
    ETC, Inc.

  10. #10


    Join Date
    Mar 2010
    Location
    los angeles
    Occupation
    President/Owner
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default re: ETC Sensor rack troubleshooting

    i was able to fix my 12ch dimmers but i just had to do the same thing on a new 24 channel etc sensor rack w/ a emp brain. its channels 11-12 only did the test pattern of 830 and also 820 and the same thing happen after it reaches 1% it goes to full any suggestions ???

  11. #11
     Premium Member 
    starksk's Avatar
    Join Date
    Mar 2009
    Location
    Madison, WI
    Occupation
    Technical Support Specialist
    Posts
    435
    Thanks
    49
    Thanked 81 Times in 65 Posts

    Default Re: ETC Sensor rack troubleshooting

    Howdy oak1now,

    It sounds like you have narrowed it down to just a pair of circuits. It could be an issue in the rack or just with that specific module. With the power to the rack off, swap the module that dims circuits 11 & 12 with a known working module. Then, power the rack back on and repeat tests 820 and 830 to see if the problem moved with the module or stays in the slot.

    If it moves with the module, then it is most likely the power cube of the module has failed. If it stays with the slot, please give us (ETC) a call at 800-688-4116.
    Kirk Starks
    Technical Support Specialist
    ETC, Inc.