Results 1 to 39 of 39
The safety of outlet taps in entertainment lighting is being discussed in the ControlBooth Lighting and Electrics forum; When I started my current job in June of last year, I was surprised to find out that a lot ...

  1. #1


    Join Date
    Jun 2009
    Location
    Really far outside DC
    Occupation
    Lighting Designer
    Posts
    83
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Default The safety of outlet taps in entertainment lighting

    When I started my current job in June of last year, I was surprised to find out that a lot of our "two-fers" were actually edison outlet taps (the entire space is edison). I reluctantly accepted this fact for the present but resolved to solve it in the future. Over the course of the season, I used some of my dead time in between productions to fashion "real" V-style twofers from surplus plugs and cable. I'm now proud to say that the taps are entirely gone.

    But I got to thinking, as I was spending all this time making two-fers, that I couldn't entirely blame my predecessors for thinking outlet taps were a good choice; after all...

    1. They are UL-listed (I believe) and rated at 15 amps, which isn't a FULL dimmer load, but enough for three source fours or similar instruments, which is about the limit I'd put on a dimmer anyway. Besides, it's not wrong to use, say, 14-gauge cable with a 20 amp dimmer, because in a professional environment it's assumed you know what you're doing and won't overload it.

    2. They are cheap, costing only about as much as a single edison plug (on a two-fer there are three plugs, two of which are the typically more expensive female, plus a few feet of cable, which also costs).

    3. You don't have to spend any time to make them, and finally...

    4. They are professionally manufactured and have no flexible parts. Why is it that we would consider a two-fer made by hand perfectly safe and preferable, and not a solid block of plastic with no wires to come loose? I can think of so many failure points of a self-made two-fer; after all, they aren't even made in such a way that uses the male plug in a manufacturer-intended way.

    I've seen two-fers made in horrible ways, with no strain relief because someone tried to use 12-gauge SO and it wouldn't fit, so they just took off a few inches of rubber and replaced it with e-tape, then clamped the strain relief down on the inner conductors. What would you reccommend then, these jury-rigged devices or an outlet tap?



    Trust me, I'm firmly of the belief that what goes in your grid should not be the same thing used to power your toaster oven, but I'm looking for solid justification for this belief. Thoughts?

  2. #2
    Senior Team  Premium Member 
    Footer's Avatar
    Join Date
    Nov 2005
    Location
    Saratoga Springs, NY
    Occupation
    Production Coordinator
    Posts
    7,596
    Thanks
    2
    Thanked 535 Times in 429 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    I hope you did not throw away the power cubes.

    Home made two-fers are actually illegal to use. I know everyone does it, but it is against the NEC to make multiple connections inside a connector except when a connector is designed for that use (socapex breakouts for example). This is the reason why professionally made twofers have the split in a molded lump in the middle of the cable.



    Now, the other issue is the 15amp rating. Everything down stream of a breaker should be rated for the maximum rating of that circuit. So, you have a 20amp breaker, you can not connect 16 gauge cable because its to rated to handle 20 amps of power. You are right that you should not use triple taps with a lighting system. Instead, you should buy properly made molded two-fers.

    All is not lost however, many places sell just the cable part, you provide your own ends. I have am buying another 15 of these at the end of this season to fix the rest of my stock.
    2-fer, Molded, 36", Blunt Ends



    18 bucks is cheap for piece of mind.
    Kyle Van Sandt
    Production Coordinator
    The Egg
    Van Sandt Designs

    "Pull rope, push box, push button, get a banana."

  3. #3
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,946
    Thanks
    81
    Thanked 202 Times in 146 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    There's not much room for error should the voltage drop, as it often does in long cable runs and through dimmer packs. This is especially in a theatre where a user might unknowingly have 750w lamps floating around.

    While I agree that there is some expectation that users are deemed competent, but most professional theatres know better and are easily able to use the right equipment, while schools and small community theatres are the ones that are often guilty of using these. In schools and small community theatres, I've seen these outlet taps -- two, three, four plugged into each other at a time. A school theatre filled with these taps could very quickly make a probably safe situation extremely dangerous.

    Also, these taps are intended for a 15A environment on 5-15 connectors, where overloading the taps is synonymous with overloading the circuit breaker. In residences, this is not a problem when most circuits are 15A, but in schools and commercial buildings almost all circuits are 20A. Likewise, almost all theatrical circuits are 20A. That means you can overload these taps without knowing it. In that regard, there is a problem with 5-15 parallel blade connectors being able to plug into 5-20 receptacles.
    Last edited by MNicolai; April 24th, 2010 at 03:56 AM.
    Mike Nicolai
    Milwaukee, WI

  4. #4
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,199
    Thanks
    32
    Thanked 182 Times in 163 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    On the bright side, most of these do have a 15 amp push button breaker, limiting them to 15 amps.

    Now for the downside-

    Constant loads are a funny thing. (As in three S4's on for an hour.) What should work sometimes burns up anyway. Most of these strips are very cheap inside. Most using a marginal gauge thin metal strip to supply all of the outlets.

    Although I wouldn't think twice about using one to plug my computer and printer in, I would never use one in the stage environment. (imho)
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  5. #5
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by Footer View Post
    ... Everything down stream of a breaker should be rated for the maximum rating of that circuit. ...
    If that were true, 5-15 devices would NEVER be permitted on a circuit with a 20A OPD. Not to mention plugging in the SourceFour having 16g wire from the plug to the socket.

    Quote Originally Posted by MNicolai View Post
    ... There's not much room for error should the voltage drop, as it often does in long cable runs and through dimmer packs. ...
    It doesn't work that way. As voltage decreases, so does the wattage:

    watts/WATTS = (volts/VOLTS)^1.6
    (not 'squared' as you would get with a fixed resistance)
    For the record, I have nothing against using good quality cube taps in lieu of Edison twofers. Except for the fact that they're often too short, requiring jumpers. And some AHJs, especially in exhibit halls and convention centers, won't allow them. Their house, their rules.
    Last edited by derekleffew; April 25th, 2010 at 02:26 PM. Reason: BBcode quote
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  6. #6
    len
    len is offline


    Join Date
    Oct 2004
    Location
    Chicagoland
    Occupation
    President/Owner
    Posts
    2,317
    Thanks
    29
    Thanked 76 Times in 69 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    We use cube taps all the time. But 99% of the time the load on them is an LED fixture, which draws 35 - 50 watts, so no big deal.

    Chances are, if you're using conventional fixtures and edison cube taps, you're using shoebox dimmers (at least in my case it's true), which means most of the time it's one fixture per circuit anyway, so cube taps or two-fers would be useless.

    The problem I run into with good cube taps is that they're good and they tend to disappear.
    http://www.chicagolightingdesign.com
    "I don't feel it's healthy to keep your faults bottled up inside me." - Bucky Katt

  7. #7
    Senior Team  Premium Member 
    Footer's Avatar
    Join Date
    Nov 2005
    Location
    Saratoga Springs, NY
    Occupation
    Production Coordinator
    Posts
    7,596
    Thanks
    2
    Thanked 535 Times in 429 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post
    If that were true, 5-15 devices would NEVER be permitted on a circuit with a 20A OPD. Not to mention plugging in the SourceFour having 16g wire from the plug to the socket.

    The 15amp connector debate is one we have gone around and around on. There is also a difference between a cable with a known load on the end and a cable that could have any load on the end.
    Kyle Van Sandt
    Production Coordinator
    The Egg
    Van Sandt Designs

    "Pull rope, push box, push button, get a banana."

  8. #8
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,946
    Thanks
    81
    Thanked 202 Times in 146 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Derek, you raise a good point. My logic is faulty in that it suggests if voltage drops, current will be inversely proportional to it, eventually approaching infinity. That assumes constant brightness (and power), which is not the case. If that was true, you'd never be able to dim lights because as the dimmers reduced voltage, current would increase. The actual power draw relates purely to voltage and the hot resistance of the filament.

    My point remains pretty much the same, though. It's less than .625 amps for a margin of safety assuming ideal conditions. Also, if these cube taps are close to the lighting fixtures, they will have to stand up to not only being pushed to their rated current draw, which will produce heat in the device, but also have to additionally withstand the high ambient temperatures of nearby lighting fixtures.

    JD, I don't know which cube taps you buy, but I don't think I've ever seen a cube tap with a push-to-reset breaker. Any that do have that feature will have additional problems in tripping at less than 15A. Unlike ETC dimmers, most circuit breakers are not rated for 100% loading -- if left at a slightly lower current draw for a long enough amount of time, it's likely they'll trip the 15A breakers, again, because there isn't enough leftover margin for error.

    I'd prefer saving cube taps for low-current applications. While they certainly can be useful, I'd always want to have more room for error. Here is something that is sort of an odd twist, though:

    Assuming ideal conditions:
    (575w * 3 fixtures) / 120v = 14.375A
    (750w * 2 fixtures) / 120v = 12.5A

    You would actually be better off plugging two 750w loads into the taps instead of three 575w loads. This gives you enough overhead that you'll not be as likely to prematurely trip a 15A breaker.
    Last edited by MNicolai; April 24th, 2010 at 05:16 AM.
    Mike Nicolai
    Milwaukee, WI

  9. #9
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,199
    Thanks
    32
    Thanked 182 Times in 163 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by MNicolai View Post
    JD, I don't know which cube taps you buy, but I don't think I've ever seen a cube tap with a push-to-reset breaker. Any that do have that feature will have additional problems in tripping at less than 15A. Unlike ETC dimmers, most circuit breakers are not rated for 100% loading -- if left at a slightly lower current draw for a long enough amount of time, it's likely they'll trip the 15A breakers, again, because there isn't enough leftover margin for error.
    The word "Cube" did not get added until later in the thread. My first take was the standard Edison strip, usually containing six outlets. Cubes, on the other hand, I have no problem with. (Usually with 250w movers and such)

    Regarding Amps/volts and long runs, there is one exception which is an electronic ballast. These will increase current draw as the voltage drops by way of their switch mode supply operation. Also, many spots (like some super troupers) will have a tap switch that will alter the current draw dependent on the voltage. Still, when referring to non-discharge stage lights, current & brightness drop as the voltage goes down.

    (Of course, anyone plugging a Super Trouper into a cube tap.... Well, enough said ! )
    Last edited by JD; April 24th, 2010 at 09:18 AM. Reason: I just can't type this morning !!
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  10. #10


    Join Date
    Mar 2008
    Location
    Winter Haven, FL
    Occupation
    all things technical
    Posts
    432
    Thanks
    23
    Thanked 49 Times in 38 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Footer, I have two of those molded 2fers that you pictured, one of them took out the Solid State Relay in one of my dimmers. When I determined that it was shorted internally, I used a razor knife and cut open the out vulcanized rubber jacket. Inside I found a plastic housing in two parts, that clamshell around three of the metal connection sleeves with a set screw on each end. The wires from the two output cables were twisted together and pushed into the sleeve and the screw was tightened down on the wire, with neither a ferrule or tinning. End result was that the wires had pulled out of the sleeve and shorted. The two I have were given to me as a gift, so I don't know if they may have been a cheaper version of a better brand, or the good stuff that escaped quality control. I Repaired the whole thing with ferrules and tightened everything down, replaced the outercover with with silicone adhesive.
    I am still a little "gunshy" about using the one that has not failed, with the anticipation that it may have been assembled in the same careless manner. No real conclusions drawn, just a mild warning.

  11. #11


    Join Date
    Mar 2004
    Location
    Brooklyn, NY
    Occupation
    Lighting Director / Head Elec.
    Posts
    2,406
    Thanks
    61
    Thanked 150 Times in 128 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by Footer View Post

    Home made two-fers are actually illegal to use. I know everyone does it, but it is against the NEC to make multiple connections inside a connector except when a connector is designed for that use (socapex breakouts for example). This is the reason why professionally made twofers have the split in a molded lump in the middle of the cable.
    .
    Perhaps Steve Terry could clarify/confirm this, as I thought that there was an allowance in the NEC for 2-fers 18" or less in length to use the male connector as the connecting point for 2 SJ 12/3 cables.

    Reason I ask as I purchased a whole lot of new 2-fers all made by TMB with splice in the male and would be surprised if they were all illegal.

    SB
    Steve B.
    "Read it again, before pressing Send"

  12. #12


    Join Date
    Jun 2009
    Location
    Really far outside DC
    Occupation
    Lighting Designer
    Posts
    83
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Thread Starter

    Default Re: The safety of outlet taps in entertainment lighting

    I remember reading in another thread that V-style twofers were explicitly allowed by the NEC. I don't think they're illegal. But then again I don't think cube taps and the like are explicitly disallowed either.

    For the record I was talking about cube taps, but I didn't want to say cube taps because not all of them are cubes, per se; but I'm talking about a small plastic device with one male plug and three female receptacles.

  13. #13
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    Of these, the only one I approve of is the orange one, and someone makes them in black.

    Coding Horror: Road Warrior Revisited

    JD was, of course, talking about a power strip/MOS/Waber strip.
    Last edited by derekleffew; April 24th, 2010 at 11:30 AM.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  14. #14


    Join Date
    Mar 2004
    Location
    Brooklyn, NY
    Occupation
    Lighting Director / Head Elec.
    Posts
    2,406
    Thanks
    61
    Thanked 150 Times in 128 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by SteveB View Post
    Perhaps Steve Terry could clarify/confirm this, as I thought that there was an allowance in the NEC for 2-fers 18" or less in length to use the male connector as the connecting point for 2 SJ 12/3 cables.

    Reason I ask as I purchased a whole lot of new 2-fers all made by TMB with splice in the male and would be surprised if they were all illegal.

    SB
    Steve had this to say in a prior CB post:

    " Twofers are a recognized construction in the theatre, as evidenced by section 520.69, which allows reduced diameter Junior Hard Service cord for twofers specifically so that two cables can enter the male connector. In this case, article 520 modifies Chapters 1 through 4 of the code for the theatre, a Special Occupancy."

    And as comment on the OP, one thing that bothered me was the assumption that just because all the outlets were Edison, that they were 15 amp, noting that there are 20 amp versions. If the system was installed professionally and to code, these should have been 20 amp duplex, if the dimmers have 20 amp breakers and all wiring was appropriately sized.

    Thus care must be taken in the use of connectors, cabling and cube taps downstream of the load breaker, as 15 amp devices are generally not allowed by NEC, for use on stage lighting equipment, when used on a stage or space that meets the definitions of section 520.

    Just a thought.
    Last edited by SteveB; April 24th, 2010 at 12:03 PM.
    Steve B.
    "Read it again, before pressing Send"

  15. #15

    shiben's Avatar
    Join Date
    Jun 2009
    Location
    Chicago, IL
    Occupation
    Lighting Designer, Electrician, Student
    Posts
    3,090
    Thanks
    58
    Thanked 111 Times in 99 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by SteveB View Post
    And as comment on the OP, one thing that bothered me was the assumption that just because all the outlets were Edison, that they were 15 amp, noting that there are 20 amp versions. If the system was installed professionally and to code, these should have been 20 amp duplex, if the dimmers have 20 amp breakers and all wiring was appropriately sized.
    20A Edison style connectors dont have 2 parallel blades, however, one is perpendicular to the other.

    As for the 2fer illegality debate, I really hope that they are, just about ever house in town has bought or made them in a v style.
    ---
    Shiben
    Now shipping with industry standard 3-pin DMX.

  16. #16


    Join Date
    Mar 2004
    Location
    Brooklyn, NY
    Occupation
    Lighting Director / Head Elec.
    Posts
    2,406
    Thanks
    61
    Thanked 150 Times in 128 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by shiben View Post
    20A Edison style connectors dont have 2 parallel blades, however, one is perpendicular to the other.

    .
    Only on the males. The female receptacles have both configurations to allow use of 15 amp male plugs.
    Steve B.
    "Read it again, before pressing Send"

  17. #17
    mrb
    mrb is offline


    Join Date
    Dec 2008
    Occupation
    President/Owner
    Posts
    377
    Thanks
    0
    Thanked 15 Times in 15 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    couple quick notes:
    15 amp edisons have the same current carrying capacity as a 20 amp edison. The metal inside is the same, the keying exists to keep you from plugging something that requires a 20 amp circuit into a 15 amp circuit.

    The issue with the V style twofers is the listing of the plug. I dont think youre going to find an edison plug listed for multiple cords in the strain relief, and two conductors in the terminals.

    NEC allows 15 amp receptacles on a 20 amp circuit, unless it is a single receptacle (a duplex is ok).

  18. #18
    The Royal Renaissance Man  Premium Member 


    Arez's Avatar
    Join Date
    Jul 2005
    Location
    Wisconsin
    Posts
    1,009
    Thanks
    35
    Thanked 44 Times in 37 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by mrb View Post
    The issue with the V style twofers is the listing of the plug. I dont think youre going to find an edison plug listed for multiple cords in the strain relief, and two conductors in the terminals.
    If anyone knows of a company that makes one, I'd be very interested.

  19. #19
    CBmod cdub260's Avatar
    Join Date
    Aug 2008
    Location
    Southern California
    Occupation
    Stage Electrician
    Posts
    1,243
    Thanks
    12
    Thanked 66 Times in 50 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by Arez View Post
    If anyone knows of a company that makes one, I'd be very interested.
    Off hand, I'd say there probably isn't one. That said, there is an alternative if you absolutely have to make your own twofers. Heatshrink breakout boots will allow you to safely cover your splices and since they are adhesive lined, they also act as a strain relief for you splice. As with all things electrical, only qualified individuals should be making their own twofers.

    However, I personally would not choose to use these breakout boots for standard twofers. Why? They're expensive. Once you factor in the cost of the wire, you're probably only saving $2.00 or so per twofer. Factor in what your employer pays for your time in making the twofers and it's probably a wash or cheaper to just by the pre-made assemblies. I use breakout boots quite often as I have to make a lot of custom cable assemblies. And they work very well for my needs. As an example, for last year's Pageant of the Masters I needed a 30 ft. cable with breakout points every 10 ft. I could have done this with three ten ft. cables and two twofers, but I had to be able to set it up and break it down in less than a minute on a nightly basis for nearly two months straight. For this application, two breakout boots, 30 ft. of cable, and a few connectors were an ideal solution. I still have the cable should I ever need it again. For a more conventional cable run, one that would stay in place for the run of a show, I would never go to this much effort, as my time could be better spent on other projects.
    C.W. Keller
    Master Electrician
    Pageant of the Masters
    Laguna Beach, CA



    Always remember: Pillage first, then burn.

  20. #20
    The Royal Renaissance Man  Premium Member 


    Arez's Avatar
    Join Date
    Jul 2005
    Location
    Wisconsin
    Posts
    1,009
    Thanks
    35
    Thanked 44 Times in 37 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by cdub260 View Post
    Off hand, I'd say there probably isn't one. That said, there is an alternative if you absolutely have to make your own twofers.
    It was more of a curiosity (I was trying to find some for a stubborn company a while ago), I prefer them to be molded, and I don't make or use homemade ones. Thanks for the link on the boots though, I knew they were out there but never put much into finding them. Certainly not really worth it for making a straight up twofer, I would ahve to agree with you.
    Last edited by Arez; April 25th, 2010 at 03:27 AM.

  21. #21
     Premium Member 


    STEVETERRY's Avatar
    Join Date
    Aug 2007
    Location
    New York
    Occupation
    Manager/Administrator
    Posts
    1,051
    Thanks
    8
    Thanked 188 Times in 98 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by SteveB View Post
    Perhaps Steve Terry could clarify/confirm this, as I thought that there was an allowance in the NEC for 2-fers 18" or less in length to use the male connector as the connecting point for 2 SJ 12/3 cables.

    Reason I ask as I purchased a whole lot of new 2-fers all made by TMB with splice in the male and would be surprised if they were all illegal.

    SB
    The whole reason the NEC allows SJO on twofers is that its smaller diameter will allow two cables into a male connector. The TMB connector (and there may be others) has an enlarged strain relief hold in the cover to accommodate two pieces of 12/3 SJO.

    "V" twofers are considered by the NEC to be industry-specific safe practice when properly constructed. 36" is the max length for SJO in this application.

    For more details, see this post:

    http://www.controlbooth.com/forums/l...tml#post168140

    ST
    Last edited by STEVETERRY; April 25th, 2010 at 10:35 AM.

  22. The Following User Says Thank You to STEVETERRY For This Useful Post:

    gafftapegreenia (June 16th, 2011)

  23. #22

    Soxred93's Avatar
    Join Date
    Aug 2009
    Location
    USA
    Occupation
    HS Student
    Posts
    186
    Thanks
    2
    Thanked 3 Times in 3 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    I've seen some theatres use these: Y-splitter Liberator Power Extension - 121-2594 - SmartHomeUSA.com They're only 15 amps, but you avoid the problem of illegality and homemade problems with these things. At $4.55, you can't beat the price.
    If I ate a tub of cookie dough ice cream every time something in my high school theatre went wrong... I'd be dead by now of a sugar overdose.

  24. #23
     Premium Member 


    STEVETERRY's Avatar
    Join Date
    Aug 2007
    Location
    New York
    Occupation
    Manager/Administrator
    Posts
    1,051
    Thanks
    8
    Thanked 188 Times in 98 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by Footer View Post
    The 15amp connector debate is one we have gone around and around on. There is also a difference between a cable with a known load on the end and a cable that could have any load on the end.
    NEC section 520.9 allows a branch circuit of any rating, but requires that the receptacle rating not be smaller than that of the branch circuit overcurrent protective device.

    That would require a 20A receptacle on a 20A circuit. If this were an edison-plug installation, that would be a 20A t-slot receptacle. Section 520.67 allows us to plug a 15A parallel blade connector into a 20A t-slot receptacle protected by a 20A overcurrent protective device.

    ST

  25. #24
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    I should have remembered that it's Lex Products who make the cube tap in black:

    Lex Tri-Tap Adapter Cube Tap Black 50201B - Lex Products (Electrical)

    Quote Originally Posted by STEVETERRY View Post
    NEC section 520.9 allows a branch circuit of any rating, but requires that the receptacle rating not be smaller than that of the branch circuit overcurrent protective device.

    That would require a 20A receptacle on a 20A circuit. If this were an edison-plug installation, that would be a 20A t-slot receptacle. Section 520.67 allows us to plug a 15A parallel blade connector into a 20A t-slot receptacle protected by a 20A overcurrent protective device.
    Still slightly unclear here. (My NFPA online reader doesn't seem to be working.) Does 520.9 refer only to permanent wiring, or encompass portable cable as well? Does receptable include cord-mounted female connectors as well as flush-mounted ones? Can the E-String only be used on 15A circuits?

    PowerFLEX Cable Assemblies: E-String (3) NEMA 5-15 Receptacles Black | Lex Products

    Furthering the confusion, is the 15A T-Slot female connector (with "20A. 125V" clearly stamped on its face!):

    PowerPARTS Wiring Devices: Lex-Loc Edison 15 Amp Female Connector | Lex Products


    Am I the only one who thinks the NEMA 5-20P

    Hammond Mfg. - 15 & 20 Amp Rack Mount - With Ammeter - Outlet Strips (1583 & 1589 Series)
    (and resulting debate) is tiresome? Every time I've encountered one in the field, it's been supplied with a 5-15 to 5-20 adapter; or is cut off and replaced with a 5-15P.

    Does anyone know of a 20A NEMA 5-20 cube tap? Or one with a 15A male and T-Slot females? I don't think I've ever seen one.
    Last edited by derekleffew; April 26th, 2010 at 01:31 PM.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  26. #25


    Join Date
    May 2008
    Occupation
    College Student/ Lighting Tech
    Posts
    923
    Thanks
    33
    Thanked 14 Times in 13 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Most rental companies I've encountered use edison, and will provide adapters to whatever you need (if using it with an existing system). When you ask for 2-fers or 3-fers they send out tritaps (of the black or orange variety depending)... I'm inclined to say if they feel it is safe, it probably is. The idea is anyone setting up this gear knows what they are doing. I'm also going to venture a guess that the heavy duty orange (or black) moulded tritaps would stand up to 20A without issue (not recommending, but I don't forsee any issues other than with the fire marshal). Now I kinda want to find a bad one and do some surgery...

  27. #26


    Join Date
    Mar 2004
    Location
    Brooklyn, NY
    Occupation
    Lighting Director / Head Elec.
    Posts
    2,406
    Thanks
    61
    Thanked 150 Times in 128 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post

    Am I the only one who thinks the NEMA 5-20P

    (and resulting debate) is tiresome? Every time I've encountered one in the field, it's been supplied with a 5-15 to 5-20 adapter; or is cut off and replaced with a 5-15P.
    Agree completely. No need for ANOTHER connector type, especially as it's the most widely used in the US and Canada. They could have kept the old 15a configuration and simply started building to 20a rating and be done with it. If you have a 15 amp circuit with over current protection at that rating - who cares ?. If you be dumb enough to load to 20 (like my sound man is doing), the breaker trips.

    Right now you can have a duplex receptacle that accepts both 15 and 20 amp devices. You have no idea what the circuit rating is unless you look at the breaker. My sound guy uses cheap HD 15 amp connectors, pulls 20 on his monitor rig, the receptacle, wiring and breaker on the Sensor relay are all 20, so he fries the connector. Now I have to swap the duplex receptacle that has the single fried male prong sticking out of it.

    Rant over.

    SB
    Last edited by derekleffew; April 26th, 2010 at 01:32 PM. Reason: BBcode
    Steve B.
    "Read it again, before pressing Send"

  28. #27
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by photoatdv View Post
    Most rental companies I've encountered use edison, ... I'm inclined to say if they feel it is safe, it probably is. The idea is anyone setting up this gear knows what they are doing. ...
    Bad assumption. I know of one lighting company that uses 2P&Gs on their movers, and run them at 208V! Not illegal (as the 2P&G is rated for 125 and 250V), but a very bad practice nonetheless, in my opinion.

    Yes, there have been times when I've sent 208V through an Edison, but never felt good about doing it.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  29. #28
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post
    Of these, the only one I approve of is the orange one, and someone makes them in black.
    Why do you not approve of using the clear one?
    Seems to me it's essentially the same thing as the orange one. All molded plastic. 3 way. Only difference I see is the shape. Do you not like the way the three plugs are lined up and jammed together so tightly?


  30. #29


    Join Date
    Sep 2009
    Location
    Chicago, IL
    Occupation
    HS Student
    Posts
    276
    Thanks
    17
    Thanked 6 Times in 6 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by gafftaper View Post
    Why do you not approve of using the clear one?
    Seems to me it's essentially the same thing as the orange one. All molded plastic. 3 way. Only difference I see is the shape. Do you not like the way the three plugs are lined up and jammed together so tightly?
    To me the clear tap looks to close to the white tap, and only small plugs would fit. Whereas the orange one is very different from the others and will fit large plugs.

  31. #30
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The safety of outlet taps in entertainment lighting

    The clear flat one is different from the white ones because it's molded plastic vs snapped together plastic. It's therefore more durable. You can drop it from the grid and still use it. The white ones will shatter.

    I was thinking the clear flat one is actually safer than the orange because three professional size Edison plugs wont fit. This means someone can't come along and plug in three fixtures into one 15 amp tap (which is potentially pushing your luck safety wise).


  32. #31
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The safety of outlet taps in entertainment lighting

    It's completely a hijack... but yYou've got to love the socapex cube tap:

    Everyone should have one just because it's just so big and cool!


  33. #32

    zuixro's Avatar
    Join Date
    Aug 2008
    Location
    Spartanburg, SC
    Occupation
    Undergrad
    Posts
    369
    Thanks
    2
    Thanked 5 Times in 3 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by gafftaper View Post
    It's completely a hijack... but yYou've got to love the socapex cube tap:

    Everyone should have one just because it's just so big and cool!
    Anyone else see that and think "Hefty Hefty Hefty!"
    Nick Whitworth
    Sophmore - USC Upstate, Communications Major w/ Emphasis in Theatre

  34. #33


    Join Date
    Mar 2004
    Location
    Brooklyn, NY
    Occupation
    Lighting Director / Head Elec.
    Posts
    2,406
    Thanks
    61
    Thanked 150 Times in 128 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post

    Yes, there have been times when I've sent 208V through an Edison, but never felt good about doing it.
    To tie into an past thread, I'd bet Tesla wanted to send 208 through an Edison.

    And I'd like to send 208 through my sound man !.
    Steve B.
    "Read it again, before pressing Send"

  35. #34
     Premium Member 


    JChenault's Avatar
    Join Date
    Jan 2009
    Location
    seattle, wa USA
    Occupation
    Lighting designer and Software Engineer
    Posts
    778
    Thanks
    20
    Thanked 63 Times in 55 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post
    Yes, there have been times when I've sent 208V through an Edison, but never felt good about doing it.
    Derek
    Just curious - why do you not feel good about sending 208 through an edison. Are you afraid that the insulation will not handle 2068 volts?

    Just trying to understand if this is an emotional response, or an emotional one?
    John Chenault
    Co-Creator of Plexus - a software only solution for controlling Conventional and Moving Lights

  36. #35
    Senior Team  Premium Member 
    Footer's Avatar
    Join Date
    Nov 2005
    Location
    Saratoga Springs, NY
    Occupation
    Production Coordinator
    Posts
    7,596
    Thanks
    2
    Thanked 535 Times in 429 Posts

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by gafftaper View Post
    It's completely a hijack... but yYou've got to love the socapex cube tap:

    Everyone should have one just because it's just so big and cool!
    Those things are pretty useful, especially when dealer with par bars/six bangers. They are expensive as hell though for what they are.
    Kyle Van Sandt
    Production Coordinator
    The Egg
    Van Sandt Designs

    "Pull rope, push box, push button, get a banana."

  37. #36
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by JChenault View Post
    Derek
    Just curious - why do you not feel good about sending 208 through an edison. Are you afraid that the insulation will not handle 2068 volts?

    Just trying to understand if this is an emotional response, or an emotional one?
    No; more worried that someone will see an Edison connector and (reasonably?) assume that it carries 120V.


    As to the Socapex twofer block--stupidest thing ever. Yes, let's add MORE parts, cable, connectors than necessary: that'll make troubleshooting really challenging! Gimme a regular "parbar tufer" any day.

    VEAM TWOFER - UsedLighting.com
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  38. #37
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The safety of outlet taps in entertainment lighting

    Yeah but you've got to admit it's the king of cube taps!


  39. #38
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The safety of outlet taps in entertainment lighting

    No, I don't; in that it meets none of the requisite characteristics of a cube tap.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  40. #39
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The safety of outlet taps in entertainment lighting

    Quote Originally Posted by derekleffew View Post
    No, I don't; in that it meets none of the requisite characteristics of a cube tap.
    To quote the Church Lady "how convenient"... You wrote the definition!

    (it's only because of my deep respect for the wiki that I didn't rewrite the definition and post the Lux Cube tap as part of it.)