Ive googled, and KGBed it. And I havent found any answers. But I Know yall have to know!
| What's the difference? SO vs. SJO is being discussed in the ControlBooth Lighting and Electrics forum; between SOOW, SJOOW, SO, and SJ cable? Ive googled, and KGBed it. And I havent found any answers. But I ... |

between SOOW, SJOOW, SO, and SJ cable?
Ive googled, and KGBed it. And I havent found any answers. But I Know yall have to know!

Perhaps the wiki entry: Cable Types, S, SO, SOOW, SJ can illuminate.

Quickie answer is SO and SJ are the older and no longer manufactured versions, where as SOOW and SJOOW are the new current types, with improvements in the jacket design for resistance to chemicals, etc...
SOOW is heavy duty, with a thicker jacket, SJOOW is light duty with a thinner jacket.
For theatrical use, SOOW is the version allowed for on-stage use, below 12 ft. above deck level ? (12 or 20, cannot remember) and in lengths over 20ft. Thus typical multi-cables with male and female breakouts and fan outs can use SJOOW as long as the breakout is no longer then 20 ft.. I believe 2-fers are now SOOW as they need to be molded, as per recent UL listing requirements, thus no more 2-fers made with 12/3 SJOOW into a male 2p&G male plug.
SB
Steve B.
"Read it again, before pressing Send"

I'm not sure about the 2-fer thing as we just got 72 brand spanking new 2-fers from LEX Products made out of SJTOW and terminated inside of the 2P&G male connector. I'll be really angry to find out that these brand new 2-fers which we just got delievered last Thrusday are not up to code...
Last edited by Sony; August 6th, 2010 at 01:54 PM.
Trevor Bates
Designer/Stagehand
Boston, MA

SO cable is designed to be coiled and recoiled repeatedly
SJ is Tray Cable and not designed to be coiled and recoiled
W o o f e r H o u n d
http://wooferhound.home.mindspring.com
http://iatse900.home.mindspring.com

This is incorrect. Lex Products' Two-fer Junior, even when of the molded "Y"-style, use 12/3 SJTOW-A cable, and have a UL Listing.
See also this post, and particularly its attachment.


gafftapegreenia (August 7th, 2010)

Thanks Derek,
This was (to me) a recent change - I believe UL driven not NEC, about being molded and I couldn't get info. at the time I needed to do a proposal for replacement 2-fers, as to whether they allowed SJOOW for the molded portion, but it makes sense as they had allowed it for a non-molded.
SB
Steve B.
"Read it again, before pressing Send"


OK. What you are telling us Steve, is that 2-fers made with 2 pieces of 12/3 SJOOW cable, in a V design, using 2 pieces of cable into the male connector, is still allowed by the NEC. With a length limit of 36", if memory serves ?.
Is it UL listed if purchased new as a pre-assembled unit/device ?, which is a different issue and possibly why one of my suppliers would not sell me (and no longer carries pre-made) V style, but instead is only carrying pre-assembled as molded Y type ?. And is why they carry kits that assemble in a V design, which would be OK as they are not doing the assembly and thus don't care if the user assembles a device not UL listed ?.
As per MRB's comment "There is no exception for height off the deck, length if its a male to female cord, or anything else." Could someone more knowledgeable about the NEC answer/confirm these questions:
- Maximum length allowed for 12/3 SJOOW ?, which I thought was 20 ft in breakout only, not allowed as any single cable length usage ?.
- Maximum 2-fer length of 36 inches when using SJOOW, and/or is it 36" for ANY 2-fer or any construction ?.
- SJOOW only allowed a certain minimum height off stage floor ?, and if so, how does that affect breakouts below that height ?.
Going crazy in Brooklyn here.....
SB
Steve B.
"Read it again, before pressing Send"


--6.0 m (20') max length for SJ (junior hard service or hard usage) and derivatives in breakout assemblies. Must be protected from physical damage by being supported over its entire length by a pipe, truss, tower, scaffold, or other substantial support structure. There is no minimum height off the ground specified. Must connect a single multi-pole connector containing two or more circuits and multiple 2-pole, 3-wire connectors. Must be protected by an overcurrent protective device of not over 20A. Section 520.68(A)(4)
--1.0 m (3.3') max length for SJ and derivatives in adapters and twofers. No length limit on twofers using SO or derivatives. Section 520.69(C)
All other applications require extra hard usage (SO and derivatives). Section 520.68(A)(1).
ST
Last edited by STEVETERRY; August 7th, 2010 at 06:21 PM.
SteveB (August 7th, 2010)

So.... Are sleeved twofers (fiberglass or plastic) NEC compliant? Have they ever been?
Also, a slightly related question. If one builds a M 60amp to 3 F 20amp adaptor, each 20amp leg needs to be protected. Is there a preferred off-the-shelf product that would be appropriate?
Given appropriate branch circuit protection, is there any way such a 'break-out' could be SJOOW?
Sean R. McCarthy


With regard to sleeved twofers, I would reckon no since three wires in a sleeve is not a cord type listed in article 400.
For 60 amp to three 20 amp, yes each 20 amp leg would need to be protected. You can obtain female 20 amp bates that have a fuse inside. This would provide protection and (i think) the short length of 12awg before the fuse would be ok under tap rules. This is not an ideal solution though as you have to take apart the female bates to replace the fuse. Most everyone these days is using a distro with 60 amp in and three 20 amp circuits out. These are available in both lunchbox and flat designs.
Yes your (properly fused) 60 to three 20 adapter could be constructed of SJOOW.

See this post, last point.
Not exactly the same thing, but same concept: PowerFLEX™ Cable Assemblies: Stage Pin 100 Amp to 60 Amp Splitter | Lex Products. Note the conspicuous lack of mention of UL on the pdf.
mrb , I've used the female 2P&G connectors with a 20A cartidge fuse inside them, but can't find who made them and if they are still available. Got a link? One didn't need to take apart the connector to change the fuse, just open a little "door" on the side of the connector.
Sean , here is a sort-of off the shelf product. This post confirms it can be ordered with stagepin receptacles.
PowerHOUSE Portable Distribution Boxes: 60 Amp Motion Picture Brick | Lex Products
As long as each leg is limited to 3.3' (1m), no problem.
Last edited by derekleffew; August 7th, 2010 at 12:29 PM.

group 5 makes a fused 20 amp female Group5 20Amp Female Inline: all colors & terminations | Marinco
Mole makes one too
derekleffew (August 7th, 2010)


1. Sleeve twofers are non compliant because the only allowed use of this construction is for tails on high-temperature luminaires as covered in section 520.68(A)(3). Junior hard service (hard usage) cord was specifically allowed in section 520.69 to prevent the use of this type of non-compliant construction in twofers.
2. I don't think a 60A to 20A "adaptor" is actually an adapter as defined by 520.69, because it fails the "no reduction in current rating" rule of 520.69(A). It is actually a power distribution device covered by section 520.62. Therefore, any pendant cable involved in this device must be extra hard usage (SO), not hard usage (SJ).
In addition, I do not agree that any tap rule applies to a short length of flexible cord in the "adapter" you describe. . There are no tap rules that I know of for portable cord other than single-conductor feeders in sections 520.53(H)(3) and 520.53(H)(4). The overcurrent protective device must therefore be at the head end of the reduced-ampacity cord so that the ampacity of the cord and the rating of the overcurrent device are coordinated. This suggests a construction available from Lex, Union, and others, where the 20A overcurrent protective devices are contained in an enclosure, along with panel-mount connectors.
ST
Last edited by STEVETERRY; August 7th, 2010 at 06:23 PM.

thanks for clearing that up

Does this mean that every Stagepin to Edison (NEMA 5-15) Adapter, FED is also NOT code compliant,
except those using a T-slot 15/20A Edison female (NEMA 5-20)?
![]()


derekleffew (August 7th, 2010)

Hello. So im looking into buying some new cable and I was wandering what exactly "Extra Hard Service Cord" was the other option I see is "Junior Hard Service Cable" Im looking on production advantage, I will buy form a local supplier but was just doing some ball park pricing. Does "Extra Hard" refer to the physical cable? Any insight is appreciated.
Im looking at 12/3 just by the way
----
I may have just answered my own question is it that "Junior" is 300v while "Hard" is 600v?
Last edited by Wolf; August 19th, 2010 at 11:40 PM.
if its not broken, take it apart find out why it isnt broken and put it back together

Going by the wire coding, type S, SO, SOW and SOOW cable is Extra Hard Service Cable.
Could have an "E" in it right after the "S" also, I would tend to avoid it as plastic cable tends to melt should it touch by accident a lighting fixture in causing a short, fixture(s) going out during a show fed by it, and the destruction of that length of cable.
Also, I normally avoid... forget if CE for compliance or in general Euro cable even if SOOW. Extra Hard Service cord is suposted to have an extra amount of outer jacket insulation to the conductors. Seen many many instances especially on the larger 8/5 sizes where the twisting of the cable was not proper and that Euro style applied as if sprayed on outer jacket to the cable, was much less in thickness than it should be. This to the extent of mis-cast that you can see thru the outer jacket to what inner conductor is showing thru. In addition to this, Euro compliant cable is harder to strip and easier in an outer jacket cut to go all the way thru to the condctor.
Euro cable is applied to the twisted conductors, normal classic SO cable has an outer jacke that's pulled thru the inner conductors and has jute or other materials as filler in use to keep the cable round. Cheaper to do the Euro cable and more common these days given this. If SOOW Euro, it's at least better than SEOOW Euro compliant cable but not by much. Over ten years of some of the stuff in my inventory... sure a lot of it has lasted... just a question of being harder to properly install the plugs on, and in the case of the plastic version of the thick rubberized cable, just takes one mistake.
(Long story about surface area in contact with the heat and what happens to rubberized material verses plastic when it touches the heat. Both SE and S are rated for the same temperature, end result though, if it's burning and loosing it's dielectric strength to that surface area touching a fixture - but still round in only a small surface contact, that's a lot different than melting and the conductors also burning their way into the heat source before they short to the fixture or each other.)
SJ type cable has similar types of Euro verses domestic making, this in addition to SJT type grade that's mostly the same as SJE type cable for all intensive purposes. SJ type cable by code (and others are better on it than I,) is rated for strapping to a truss and or pipe for support. Other than that, not for cable drops or floor use, and it assumes not a class 1A theater I believe the term is, where it has to be type S / Extra Hard Service.
After that, while type S - best as SOOW is much heavier, you can consider it's service life double that of type SJOOW cabe no matter what the circumstance. Figure that into the overall cost of buying it.

Search for the specifics, but as stated in other threads junior service cable is VERY limited in use on stage. To summarize those threads, and combine with Ship, unless you are running shorter than about 3' go with extra hard service. Heck, I use it in short lengths as well as its easier to just stock one type.
I'm thinking that junior is also only rated to 300V whereas extra hard is rated to 600V. Shouldn't be an issue for you (I hope), but I wanted to throw it out there.
Did someone call for more photons?
T Robb
Member, NFPA Electrical Section
Maintenance & Technician, Community Theatre


A few clarifications
1. Extra Hard Usage (Hard Service) cable is 600V, designed to withstand physical abuse, and is required in almost all applictions in the theatre (see below for more). This cable is type S, SO, and derivatives.
2. Hard Usage (Junior Hard Service) cable is 300V, and only allowed in theatres for specific applications (see below). This cable is type SJ, SJO, and derivatives.
3. The only allowable uses of Hard Usage (Junior Hard Service) cable in theatres and other venues covered by NEC Article 520:
--Twofers and adapters not over 1m (3.3') in length.
--Breakout assemblies not over 20' in length supported over their entire length by a pipe, truss, tower, or other substantial support structure.
ST