I have a SR48 dimmer rack fed by a 200A disconnect.
W=VA
W=120*200
W=24,000
Assuming a 750 HPL Source 4:
24,000/750=32 instruments
Is this correct?
| Double Check My Math? is being discussed in the ControlBooth Lighting and Electrics forum; I have a SR48 dimmer rack fed by a 200A disconnect . W=VA W=120*200 W=24,000 Assuming a 750 HPL Source ... |

I have a SR48 dimmer rack fed by a 200A disconnect.
W=VA
W=120*200
W=24,000
Assuming a 750 HPL Source 4:
24,000/750=32 instruments
Is this correct?
~Scott

Is the 200A disconnect single-phase or three-phase? It's the difference between 24kW and 72kW. Is the 200A derated or faceplate?
Incidentally, it's P=VI (neglecting power factor)
where:
P = power (W)
V = voltage (V)
I = current (A)

Not quite. Chances are your 200A disconnect is actually three phase - so without complicating it too much, you actually get 200A * 3 phases = 600A of power to work with. So:
W=120(200*3)
W=120*600
W=72,000
72,000/750=96
Hey, that number looks familiar!
Hope that helps.
Michael
"Why be gentle, it's rental!"
[I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]


No, there's more to it then that.
First, single phase or 3 phase installation?
If it's 3 phase (208Y/120), then you have 200A per leg, or 200A*208V*sqrt(3)=72kVA. This could also be looked at as 200A*120V*3=72kVA. (208V=120V*sqrt(3)) Assuming W=VA, 72kW/750W=96 fixtures.
If it's single phase (240/120), then you still have 200A per leg, but you only have 2 legs. This would be 200A*120V*2=48kVA. Assuming W=VA, 48kW/750W=64 fixtures.
Dang-nabbit, beat several times over.

Dang-nabbit you beat me to it!
By the way you may notice that things work out to 12, 48, 64, 96, etc. (circuits/fixtures), this is not be accident! Things are worked out to come easily to these easy to work with.
Although we all know what you were trying to say, watch out putting V and A together like that as VA is yet another term.
see:
Watts the difference?
John Dziel
DAE Concert Lighting
founded 1971
Intelligent Lighting Solutions
"Oh, that switch also fed the Hotel ?"

Excellent. I had asked my hum-head friend about this problem a few weeks ago and we assumed that it was 200 A total...
The bad thing is that, the person who held my position before me had a Sensor Portable Pack installed on the catwalks because she assumed (incorrectly, like I did!) that our power was so severely limited. Anyone want to buy an empty Sensor Portable Pack?
Yeah, yeah, yeah. Right as always JD
Thanks for all the help guys!
~Scott