    I have a SR48 dimmer rack fed by a 200A disconnect.

    W=VA
    W=120*200
    W=24,000

    Assuming a 750 HPL Source 4:

    24,000/750=32 instruments

    Is this correct?
    ~Scott

  2. #2
     Premium Member 
    sk8rsdad's Avatar
    Join Date
    Aug 2008
    Location
    Ottawa
    Occupation
    Hobbyist
    Posts
    1,119
    Thanks
    30
    Thanked 109 Times in 96 Posts

    Default Re: Double Check My Math?

    Is the 200A disconnect single-phase or three-phase? It's the difference between 24kW and 72kW. Is the 200A derated or faceplate?


    Incidentally, it's P=VI (neglecting power factor)
    where:
    P = power (W)
    V = voltage (V)
    I = current (A)

  3. #3

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,185
    Thanks
    46
    Thanked 91 Times in 71 Posts

    Default Re: Double Check My Math?

    Not quite. Chances are your 200A disconnect is actually three phase - so without complicating it too much, you actually get 200A * 3 phases = 600A of power to work with. So:

    W=120(200*3)
    W=120*600
    W=72,000

    72,000/750=96

    Hey, that number looks familiar!

    Hope that helps.
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  4. #4
     Premium Member 


    epimetheus's Avatar
    Join Date
    Apr 2009
    Location
    Houston, TX
    Occupation
    Electrical Engineer
    Posts
    748
    Thanks
    28
    Thanked 37 Times in 33 Posts

    Default Re: Double Check My Math?

    No, there's more to it then that.

    First, single phase or 3 phase installation?

    If it's 3 phase (208Y/120), then you have 200A per leg, or 200A*208V*sqrt(3)=72kVA. This could also be looked at as 200A*120V*3=72kVA. (208V=120V*sqrt(3)) Assuming W=VA, 72kW/750W=96 fixtures.

    If it's single phase (240/120), then you still have 200A per leg, but you only have 2 legs. This would be 200A*120V*2=48kVA. Assuming W=VA, 48kW/750W=64 fixtures.

    Dang-nabbit, beat several times over.

  5. #5

    Dionysus's Avatar
    Join Date
    Feb 2009
    Location
    SW Ontario, Canada
    Occupation
    Freelance
    Posts
    466
    Thanks
    21
    Thanked 12 Times in 12 Posts

    Default Re: Double Check My Math?

    Quote Originally Posted by epimetheus View Post
    No, there's more to it then that.

    First, single phase or 3 phase installation?

    If it's 3 phase (208Y/120), then you have 200A per leg, or 200A*208V*sqrt(3)=72kVA. This could also be looked at as 200A*120V*3=72kVA. (208V=120V*sqrt(3)) Assuming W=VA, 72kW/750W=96 fixtures.

    If it's single phase (240/120), then you still have 200A per leg, but you only have 2 legs. This would be 200A*120V*2=48kVA. Assuming W=VA, 48kW/750W=64 fixtures.

    Dang-nabbit, beat several times over.
    Dang-nabbit you beat me to it!
    By the way you may notice that things work out to 12, 48, 64, 96, etc. (circuits/fixtures), this is not be accident! Things are worked out to come easily to these easy to work with.

  6. #6
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,249
    Thanks
    34
    Thanked 186 Times in 167 Posts

    Default Re: Double Check My Math?

    Quote Originally Posted by ScottT View Post
    W=VA
    Although we all know what you were trying to say, watch out putting V and A together like that as VA is yet another term.
    see:
    Watts the difference?
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  7. #7


    Join Date
    Jul 2008
    Location
    East Coast
    Occupation
    Undergrad
    Posts
    656
    Thanks
    33
    Thanked 28 Times in 19 Posts

    Thread Starter

    Default Re: Double Check My Math?

    Quote Originally Posted by rochem View Post
    Not quite. Chances are your 200A disconnect is actually three phase - so without complicating it too much, you actually get 200A * 3 phases = 600A of power to work with. So:

    W=120(200*3)
    W=120*600
    W=72,000

    72,000/750=96

    Hey, that number looks familiar!

    Hope that helps.
    Excellent. I had asked my hum-head friend about this problem a few weeks ago and we assumed that it was 200 A total...

    The bad thing is that, the person who held my position before me had a Sensor Portable Pack installed on the catwalks because she assumed (incorrectly, like I did!) that our power was so severely limited. Anyone want to buy an empty Sensor Portable Pack?


    Quote Originally Posted by JD View Post
    Although we all know what you were trying to say, watch out putting V and A together like that as VA is yet another term.
    see:
    Watts the difference?
    Yeah, yeah, yeah. Right as always JD



    Thanks for all the help guys!
    ~Scott