I think the important thing here is to
point out that the reason that building you own
distro is a not the best choice (and why the one you need that Derek found is listed at $600). It's not the amount of
power available that is the question in making a distro. It's getting control over that power. To make this correctly you need to have an appropriate over
current device (aka
breaker) properly installed for each 20A
outlet. This is a pretty big legal liability and to do it right even the parts are going to cost you a few hundred bucks. Even if you did want to save the money and
build it yourself then your are liable for anything that goes wrong with the distro, and the
theatre company would probably be liable for letting you do it. Even in technically simple projects small mistakes often lead to burnt out plugs and that can very easily lead to fire. The best choice here is definitely to buy the right thing. It'll have a manufacture's warranty and more importantly a UL listing. It is more power than you sound like you need now, but it's an affordable way to be prepared for future expansion.
No matter what you choose to do, double check the breaker on that service. Ranges use that
plug for standardization, but very few ranges use anywhere near that much power. The building SHOULD be wired and breakered for you to use all of the power that the outlet is rated for, but that is not necessarily a guarantee. Make sure that it's a 50A breaker, as far as the wiring it would take a professional to open up the cabinet and double check that the
wire is of an appropriate
gauge. This might be a high quality install and you don't have to worry about that. If not, maybe you can talk to an electrician and have them come take a peak for you. Inspecting the wiring shouldn't take very long, you could probably find an electrician to do it for a small ad in your program or even just free. Also if you know who did the install they might be able to tell you.
EDIT: It looks like a 40A breaker would work because that's all the
Peavey unit is designed to draw. Not sure if they make those or not though.
It may sound like I'm blowing the complexity of this way out of the water. It's not a complex thing to do, but it does involve a whole ton of liability which is much worse for you and the theatre company.
As a side note I love that the first few
safety warnings in the
manual are:
1. Read these instructions.
2. Keep these instructions.
3. Heed all warnings.
4. Follow all instructions.