    Hi all,

    So I've started adding movers to my LX, and have the issue of getting non-dim AC to them. My current way of doing so is with an extension cable in a regular outlet at stage level, tie-wrapped to a conduit that runs up to batten level, tie-wrapped to the slack portion of the dimmer power feed (I have motorized winches for my LX), and then left loose at the end of the batten near the dimmers. I then run another extension from batten-end to fixture when necessary.

    To date, I have only used the movers for small perfomances where not many other fixtures were used and the total show ran less than an hour.

    I am worried that running a standard extension cord near my fresnels at full power for 2 hours would be hazardous. Are my worries valid? If so, what is the appropraite cable to use?

    Thanks.

  2. #2
     Premium Member 


    gafftapegreenia's Avatar
    Join Date
    Sep 2005
    Location
    Atlanta GA
    Occupation
    Assoc. Technical Director
    Posts
    3,304
    Thanks
    219
    Thanked 112 Times in 100 Posts

    Blog Entries
    1

    Default Re: Running standard AC extension cable near LX

    If you are using standard hardware store "orange cord" it is likely 14/3 or 16/3 SJTW. Normal "extension cord", be it black, orange, green, yellow, red or what have you uses a thin thermoplastic jacket that is not acceptable for stage use. You should be using type 12/3 SOOW. You could use 14/3 or 16/3 SOOW, depending on the wattage of the movers, but I would stick to the standard of 12/3 SOOW.

    Any cable, even SOOW, should be run in a way that it avoids touching a lighting instrument. SJTW will melt, whereas SOOW will have a much shorter lifespan.

    I see you are in Montreal. I'm not sure of your fire codes but I'm not certain if my fire marshal would approve of "portable" cable being installed in a more permanent manner with tie-wraps.

    Another option, depending on your dimmer rack, is to swap out some dimmer modules for a relay or constant on modules. You could then a power a mover from any existing circuit in the house that you choose.
    One must first know and understand the rules of theatre before one can break them.

  3. #3
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,956
    Thanks
    83
    Thanked 207 Times in 148 Posts

    Default Re: Running standard AC extension cable near LX

    First I'd look into what gaff suggested -- whether or not your modules are swappable. If you can give a dimmer rack model name to us, we can tell you if they are.

    The second thing you should do is make some adapters for your existing cable inventory. If you simply don't have any 12/3 SO-type cable, you'll want some, but if you have a bunch and it has stage pin or twist-lock connectors, then make or buy adapters between those and 5-15 connectors (aka "Edison" aka "household"). You need not buy lots of new cable if you have a few 50' stage pin cables laying around. You can adapt from 5-15 on the front end of the extension (near the receptacle), then adapt out of it on the back end (near the fixture), and repurpose a cable you already own on an as-needed basis.

    If you swap modules so that you have constant non-dim power from your existing receptacles, you'll also probably need adapters out of that and into 5-15 to connect to your fixtures.

    I'm making a few assumptions here, so it'd help if you gave us more info on what your dimmer racks are and what your existing cable inventory looks like along with which style of connectors you use on your lighting fixtures.
    Mike Nicolai
    Milwaukee, WI

  4. #4
     Premium Member 
    sk8rsdad's Avatar
    Join Date
    Aug 2008
    Location
    Ottawa
    Occupation
    Hobbyist
    Posts
    1,118
    Thanks
    30
    Thanked 109 Times in 96 Posts

    Default Re: Running standard AC extension cable near LX

    Your AHJ would be the final authority on this but assuming they adhere to the CEC, the use of SO or other extra-hard duty cable would be required in a theatre. SJ cable may be permitted by the local AHJ.

    Depending on your dimmer rack, it may be possible to replace a dimmer module with a relay. That would be your best option.

  5. #5

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,185
    Thanks
    46
    Thanked 91 Times in 71 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by MNicolai View Post
    The second thing you should do is make some adapters for your existing cable inventory. If you simply don't have any 12/3 SO-type cable, you'll want some, but if you have a bunch and it has stage pin or twist-lock connectors, then make or buy adapters between those and 5-15 connectors (aka "Edison" aka "household"). You need not buy lots of new cable if you have a few 50' stage pin cables laying around. You can adapt from 5-15 on the front end of the extension (near the receptacle), then adapt out of it on the back end (near the fixture), and not need to buy tons of new cable.
    Agree, swapping modules is probably the best option, but if that doesn't work, I'd propose a slight amendment to Mike's solution. Assuming you do have the spare stage pin/twist lock cable lying around, instead of simply building adapters for each end, I would actually recommend putting different connectors on the ends of the cable. For one, this will be cheaper because you only need to buy one of each gender, instead of two of each to build adapters. Secondly, having different types of power running through cables with the same connectors can get dicey. When using 208V power alongside dimmer circuits, it's standard practice to have all the 208V cabled with twist lock connectors, and the dimmers cabled with stage pin, to avoid accidentally plugging in the wrong one. While mixing up non-dim and dimmable 120V power isn't nearly as big of a deal, it still might be good practice to keep the connectors separate so that someone doesn't accidentally plug a mover into a dimmer, or a conventional into the ML non-dim circuit.
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  6. #6


    Join Date
    Oct 2009
    Location
    Chicago / Boulder, Co
    Occupation
    Undergrad
    Posts
    141
    Thanks
    5
    Thanked 2 Times in 2 Posts

    Default Re: Running standard AC extension cable near LX

    A lot of people have recommended using constant power or relay modules if his rack is allowing. We actually have had serious problems with this. We are using an old D192 rack and built some non-dim modules by bypassing the SCR on the tray. We have had 3 of the MLs we powered off that configuration have power supply issues. One was a ETC Revolution and two were HES Studio Colors 575. The best we can figure is the banks of dimmers were causing power spikes upstream of the dimmer tray. Something to think about.
    Alex Rausch
    Student
    BFA; Lighting Design
    "Do not play with things unless you know how not to die while doing it. Its not hard to do right."

  7. #7
    CBmod  Premium Member 
    Grog12's Avatar
    Join Date
    Nov 2006
    Location
    Denver, CO
    Occupation
    Ballet Technical Director/Lighting Designer
    Posts
    2,583
    Thanks
    71
    Thanked 88 Times in 79 Posts

    Blog Entries
    3

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by skienblack View Post
    A lot of people have recommended using constant power or relay modules if his rack is allowing. We actually have had serious problems with this. We are using an old D192 rack and built some non-dim modules by bypassing the SCR on the tray. We have had 3 of the MLs we powered off that configuration have power supply issues. One was a ETC Revolution and two were HES Studio Colors 575. The best we can figure is the banks of dimmers were causing power spikes upstream of the dimmer tray. Something to think about.
    I would think that the problem here actually lies in the fact that you built your own non-dim modules. If you'd purchased non-dim modules for your rack and had the same issue then there might be something to it.

    Quote Originally Posted by rochem View Post
    . When using 208V power alongside dimmer circuits, it's standard practice to have all the 208V cabled with twist lock connectors, and the dimmers cabled with stage pin, to avoid accidentally plugging in the wrong one. .
    On 120v twistlock the ground is reversed from 208v twistlock. You'd have a hard time plugging one into the other.
    6 P's to live by: Piss Poor Planning Prevents Positive Performance
    4 P's for LD's Producers Prefer Pretty Photographs.
    Nothing like being focused and desperate to make me remember how something works. ~Steve B
    It's not bullying--it's educating via the time-honored traditions of intimidation and humiliation. ~Derek

  8. #8

    porkchop's Avatar
    Join Date
    Feb 2008
    Location
    What city are we in again?
    Occupation
    Employee
    Posts
    933
    Thanks
    9
    Thanked 31 Times in 30 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by skienblack View Post
    A lot of people have recommended using constant power or relay modules if his rack is allowing. We actually have had serious problems with this. We are using an old D192 rack and built some non-dim modules by bypassing the SCR on the tray. We have had 3 of the MLs we powered off that configuration have power supply issues. One was a ETC Revolution and two were HES Studio Colors 575. The best we can figure is the banks of dimmers were causing power spikes upstream of the dimmer tray. Something to think about.
    The difference is that some dimmer racks have specific modules that are made to provide constant power. ETC's R15AF and R20AF modules for examples. I don't know anything really about D192 racks, but if you built non-dim modules I have a feeling they weren't designed by the manufacture to provide on/off non-dim power.
    Brett Smith
    Touring Stagehand
    Computer Guru
    Avid Shoe Wearer

  9. #9


    Join Date
    Oct 2009
    Location
    Chicago / Boulder, Co
    Occupation
    Undergrad
    Posts
    141
    Thanks
    5
    Thanked 2 Times in 2 Posts

    Default Re: Running standard AC extension cable near LX

    I would agree that it was an inherent flaw in our design besides the fact that it merely takes the power from the bus bar through the breaker and into the choke. We built these because we could not find any constant power or relay modules for the D192.
    Alex Rausch
    Student
    BFA; Lighting Design
    "Do not play with things unless you know how not to die while doing it. Its not hard to do right."

  10. #10
    BGW
    BGW is offline


    Join Date
    Oct 2011
    Location
    Boulder, Colorado/Bozeman, MT atm
    Occupation
    Undergrad
    Posts
    119
    Thanks
    29
    Thanked 6 Times in 6 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by skienblack View Post
    I would agree that it was an inherent flaw in our design besides the fact that it merely takes the power from the bus bar through the breaker and into the choke. We built these because we could not find any constant power or relay modules for the D192.
    You shouldn't have the choke connected if the SSR is bypassed. I'll bet that's your problem. D192 racks are cool, I wish we had one.

  11. #11

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,185
    Thanks
    46
    Thanked 91 Times in 71 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by Grog12 View Post
    On 120v twistlock the ground is reversed from 208v twistlock. You'd have a hard time plugging one into the other.
    That's exactly my point. The whole principle behind the design of the L5-20 and L6-20 connectors is to ensure that you can't accidentally plug something into the wrong source. This same principle could be applied to the OP's situation in order to help ensure that only conventionals get plugged into dimmed circuits.
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  12. #12
    CBmod  Premium Member 
    Grog12's Avatar
    Join Date
    Nov 2006
    Location
    Denver, CO
    Occupation
    Ballet Technical Director/Lighting Designer
    Posts
    2,583
    Thanks
    71
    Thanked 88 Times in 79 Posts

    Blog Entries
    3

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by rochem View Post
    That's exactly my point. The whole principle behind the design of the L5-20 and L6-20 connectors is to ensure that you can't accidentally plug something into the wrong source. This same principle could be applied to the OP's situation in order to help ensure that only conventionals get plugged into dimmed circuits.
    True. My immediate thought though upon reading your OP was that there are still many twist lock houses in the world.
    6 P's to live by: Piss Poor Planning Prevents Positive Performance
    4 P's for LD's Producers Prefer Pretty Photographs.
    Nothing like being focused and desperate to make me remember how something works. ~Steve B
    It's not bullying--it's educating via the time-honored traditions of intimidation and humiliation. ~Derek

  13. The Following User Says Thank You to Grog12 For This Useful Post:

    DuckJordan (March 20th, 2012)

  14. #13


    Join Date
    Jan 2011
    Location
    Phoenix
    Occupation
    Undergrad
    Posts
    358
    Thanks
    9
    Thanked 15 Times in 13 Posts

    Default Re: Running standard AC extension cable near LX

    Agreed. If you're trying to essentially use the dimmer as a 20A breaker, you shouldn't have the choke connected.

  15. #14
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,515
    Thanks
    256
    Thanked 963 Times in 786 Posts

    Blog Entries
    4

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by skienblack View Post
    ...We built these because we could not find any constant power or relay modules for the D192.
    It might be noted that the non-dim option from the factory for the Colortran Dimension 192 dimmers was a small PCB card with a slider switch that sat on top of the SSR. It didn't actually bypass the SSR; instead turned it into an Off/ON-but-chopped-waveform device when control signal crossed the 50% threshold.

    Quote Originally Posted by FlashBang View Post
    ... I am worried that running a standard extension cord near my fresnels at full power for 2 hours would be hazardous. Are my worries valid? If so, what is the appropriate cable to use?
    What exactly is the concern? As stated already, the heat of conventional fixtures is a issue with any cable used near them, whether or not it contains dimmed or un-dimmed power. I'd be more concerned with dressing the data cable away from the fixtures.
    Last edited by derekleffew; March 19th, 2012 at 09:05 PM.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  16. #15
     Premium Member 


    gafftapegreenia's Avatar
    Join Date
    Sep 2005
    Location
    Atlanta GA
    Occupation
    Assoc. Technical Director
    Posts
    3,304
    Thanks
    219
    Thanked 112 Times in 100 Posts

    Blog Entries
    1

    Default Re: Running standard AC extension cable near LX

    It sounds like OP is running Edison cords to use 120 volt power on his movers. 208 isn't a worry here.

    OP is obviously smart enough to know that his movers need constant AC and that dimmers at full isn't appropriate.

    Also I thought I'd once read something about how a cable over a few feet had to have the same connector on both end by code.
    One must first know and understand the rules of theatre before one can break them.

  17. #16
    CBmod  Premium Member 
    Grog12's Avatar
    Join Date
    Nov 2006
    Location
    Denver, CO
    Occupation
    Ballet Technical Director/Lighting Designer
    Posts
    2,583
    Thanks
    71
    Thanked 88 Times in 79 Posts

    Blog Entries
    3

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by gafftapegreenia View Post
    It sounds like OP is running Edison cords to use 120 volt power on his movers. 208 isn't a worry here.
    .
    Yeah Rochem and I arent suggesting 208v in sense of the OP lewdly as a similie.
    6 P's to live by: Piss Poor Planning Prevents Positive Performance
    4 P's for LD's Producers Prefer Pretty Photographs.
    Nothing like being focused and desperate to make me remember how something works. ~Steve B
    It's not bullying--it's educating via the time-honored traditions of intimidation and humiliation. ~Derek

  18. #17

    porkchop's Avatar
    Join Date
    Feb 2008
    Location
    What city are we in again?
    Occupation
    Employee
    Posts
    933
    Thanks
    9
    Thanked 31 Times in 30 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by gafftapegreenia View Post
    Also I thought I'd once read something about how a cable over a few feet had to have the same connector on both end by code.
    I don't believe it's code, but it sure is much better when your adapters are small. I hate it when I run a 50 foot cable just to find out it's not what I wanted. One show I was on had some 100' female-to-female DMX cables that the head elec wouldn't let me change and they used to drive me nuts.
    Brett Smith
    Touring Stagehand
    Computer Guru
    Avid Shoe Wearer

  19. #18


    Join Date
    Dec 2010
    Location
    Montréal
    Occupation
    Auditorium Supervisor / Technician
    Posts
    76
    Thanks
    11
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Running standard AC extension cable near LX

    Thanks for all the great replies!

    I'm have an L86 rack with EM264 modules. My dimmer circuits are all twist-lock connectors. I don't currently have spare twist-lock cables to slap an adapapter on. 208 V is indeed not an issue. And, finally, I don't have my cables laying up against the side of the fixtures - they are tied/taped to the batten, but still experience a good amount of heat when the surrounding fixtures are on.

    Also a very good point was the DMX cable. It too is taped to the batten, but does come relatively close to the fresnel I have hanging next to the mover. How close is too close, in your opinion? What kind of measures can I take to protect my data cable?

    I will at least purchase appropriate cable to withstand the heat - but the module-swap seems like the more logical approach (especially since some of my dimmers are shot anyway - I'm about to look into repair/replacing them). If I take this approach will I be able to share the power off that circuit between movers if they don't have power thru (ie. a powerbar type splitter)?

    Thanks again!

  20. #19

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,185
    Thanks
    46
    Thanked 91 Times in 71 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by FlashBang View Post
    Also a very good point was the DMX cable. It too is taped to the batten, but does come relatively close to the fresnel I have hanging next to the mover. How close is too close, in your opinion? What kind of measures can I take to protect my data cable?

    I will at least purchase appropriate cable to withstand the heat - but the module-swap seems like the more logical approach (especially since some of my dimmers are shot anyway - I'm about to look into repair/replacing them). If I take this approach will I be able to share the power off that circuit between movers if they don't have power thru (ie. a powerbar type splitter)?
    Assuming your fixtures are hung on a batten, and the cable is run along that batten, you will be fine. This is how most every theatre works, and it's not a problem. This is true for your power as well as data cable. Assuming you swap modules, you need to keep in mind that you will actually swap TWO dimmers for every one module you swap - so, if you want dimmer 37 to be a non-dim module, dimmer 38 will also be a non-dim module. This is important if you're short on raceway circuits, as you're losing two dimmers instead of just one. However, ML power can be two-fered just like dimmed power can - ideally, you would have every ML on its own circuit so that you could power cycle individual fixtures if required, but that's not crucial in this instance. If you end up going with running cable up to the pipe instead of swapping modules, you do need to go out and buy real 12/3 SOOW cable, instead of using your extension cords.
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  21. #20


    Join Date
    Dec 2010
    Location
    Montréal
    Occupation
    Auditorium Supervisor / Technician
    Posts
    76
    Thanks
    11
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Running standard AC extension cable near LX

    I'm not TOO stressed with my raceway circuits, but its always easier when you don't really have to worry about running out of circuits. What kind of system would a professional house put in place to provide non-dim power if they were unable to re-assign current rack modules? Would they install a new rack capable of both dim an non-dim? Would they have an electrician install electrical outlets somewhere on their grid?

    If I continue to run extensions from the stage up, the only portion of cable which experiences high-temperature use is the portion along the batten.

    Would it be practically safe to use regular duty cable for the portion of the run between the outlet on the stage and the end of the batten, and then heavy duty cable along the batten itself? Would a fire marshall or AHJ have a problem with me doing this?

    Continued thanks..
    Last edited by FlashBang; March 21st, 2012 at 02:47 PM.

  22. #21
     Premium Member 


    gafftapegreenia's Avatar
    Join Date
    Sep 2005
    Location
    Atlanta GA
    Occupation
    Assoc. Technical Director
    Posts
    3,304
    Thanks
    219
    Thanked 112 Times in 100 Posts

    Blog Entries
    1

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by FlashBang View Post
    I'm not TOO stressed with my raceway circuits, but its always easier when you don't really have to worry about running out of circuits. What kind of system would a professional house put in place to provide non-dim power if they were unable to re-assign current rack modules? Would they install a new rack capable of both dim an non-dim? Would they have an electrician install electrical outlets somewhere on their grid?

    If I continue to run extensions from the stage up, the only portion of cable which experiences high-temperature use is the portion along the batten.

    Would it be practically safe to use regular duty cable for the portion of the run between the outlet on the stage and the end of the batten, and then heavy duty cable along the batten itself? Would a fire marshall or AHJ have a problem with me doing this?

    Continued thanks..
    Depends how much money a "professional" theatre had, the last time they upgraded, and how much power they had available. Its really D) All of the above.

    Again, I don't know Canadian code, but in the US, only type SOOW cable is to be used on stage with a few exceptions for type SJOOW (Break outs/ins and two-fers). If your extension cord is any type of SJT its NOT acceptable no matter where it is, batten or not. (Yes people use SJT, but this is controlbooth.com and we advocate proper practices)

    Stages constitute an extra hard usage environment with high temps only being one factor.
    One must first know and understand the rules of theatre before one can break them.

  23. #22

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,185
    Thanks
    46
    Thanked 91 Times in 71 Posts

    Default Re: Running standard AC extension cable near LX

    Quote Originally Posted by FlashBang View Post
    I'm not TOO stressed with my raceway circuits, but its always easier when you don't really have to worry about running out of circuits. What kind of system would a professional house put in place to provide non-dim power if they were unable to re-assign current rack modules? Would they install a new rack capable of both dim an non-dim? Would they have an electrician install electrical outlets somewhere on their grid?
    For a non-installed solution, a professional house would probably buy a 120V Power Distro rack, park it offstage or on a midrail, then run cables from that to each electric. Something like the fourth product down on this page from Motion Labs might be appropriate for a smaller solution. For an installed solution, any of those you listed would be a possibility. As has been pointed out, in the US, you must only use SOOW cable on stage. Therefore, regardless of the fact that your cable won't be near any hot lights, the run up to the batten still needs to be SOOW. I unfortunately know nothing about Canadian electrical codes, so I can't help you there.
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  24. #23


    Join Date
    Dec 2010
    Location
    Montréal
    Occupation
    Auditorium Supervisor / Technician
    Posts
    76
    Thanks
    11
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Running standard AC extension cable near LX

    Alright! And with that I believe it is "case closed".

    Thanks for the help, all!