    Default Funky Cable in the pit.

    There is a cable coming right out from under our stage at my school, right into the pit. At first I thought it could be Socapex, we do have a dimmers that go to a "unknown location". My school was built in 55, so everyone thought it was just from and old system. After more research, ive finally found a product number for the connector! Amphenol MS3106B28-21S. Now, my question is, is for the dimmers, like a socapex or is it from an old system? We have a Strand CD-80SV for our dimmers. If it is for the dimmers I'd love to finally use this! My other question is if it is for the dimmers.. where could I get something like a socapex breakout for this?

  2. #2


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    I also just looked at the link above that came up on socapex... it could be a 37 pin socapex... It says amphenol at the bottom and 28-21s at the top. Pins are labeled with uppercase and lowercase letters.

  3. #3
    Chase  Premium Member 


    chausman's Avatar
    Join Date
    Jul 2010
    Location
    Spokane, WA
    Occupation
    HS Student
    Posts
    2,757
    Thanks
    235
    Thanked 96 Times in 86 Posts

    Blog Entries
    6

    Default Re: Funky Cable in the pit.

    Do you have pictures? We like pictures...
    Oh...Pretty Colors!!!
    Chase H.
    "If I relax, let up on the gas, I would probably die" - Gordon Ramsay

  4. #4
     Premium Member 


    Edrick's Avatar
    Join Date
    Mar 2007
    Location
    Boston, MA
    Occupation
    Pro
    Posts
    1,194
    Thanks
    1
    Thanked 19 Times in 13 Posts

    Default

    I fifth the request for photos.
    Inspire Create Perform | E.S Entertainment | Venue Management
    Edrick Smith | Boston, MA

  5. #5


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    haha ok I'll grab one tomorrow.

  6. #6
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,948
    Thanks
    81
    Thanked 205 Times in 147 Posts

    Default

    Quote Originally Posted by Windrider View Post
    I also just looked at the link above that came up on socapex... it could be a 37 pin socapex... It says amphenol at the bottom and 28-21s at the top. Pins are labeled with uppercase and lowercase letters.
    Datasheet says 37-pin. Don't have the link handy but a quick Googke search on that model found it.
    Mike Nicolai
    Milwaukee, WI

  7. #7
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,208
    Thanks
    33
    Thanked 182 Times in 163 Posts

    Default Re: Funky Cable in the pit.

    37 pin Veam connector, popular in the 1980's. 18 circuits, one ground. 10+ amp pins. 1kw per circuit. Often coupled on the end of 16/37 SDN type cable that used nylon insulated conductors in a heavy rubber jacket. Had a bunch of the stuff back in the 80's myself. BML out of NJ was making it popular in the north-east US. Used as truss feeders for 8 fixture bars. Each 8 fixture bar would also have one non-dim (total 9) and would then jump to the next bar on a double hang, thus 18 circuits total.

    Don't think anything like this would be allowed today. (#16 wire and only one ground for 18 circuits.)

    SDN16-37 SDN Small Diameter Multi-Conductor

    Remember them looking like this Syntax Male Panel 37 Pin (Male frame mount. But green with silver pins.)
    Last edited by JD; March 20th, 2012 at 08:38 PM.
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  8. #8

    porkchop's Avatar
    Join Date
    Feb 2008
    Location
    What city are we in again?
    Occupation
    Employee
    Posts
    931
    Thanks
    9
    Thanked 31 Times in 30 Posts

    Default Re: Funky Cable in the pit.

    If it's 37 wire that sounds like a Pyle cable to me. You probably COULD make it usable, but if it's 16 AWG like the datasheet I found on the matter says it should be you're not going to be able to use it for much and you'd have to do some work on both ends to get enough grounding which would probably mean buying component parts and soldering them yourself, which although do able I don't recommend (soldering 37 pin connectors is no fun). You're best bet is to see if you can remove the cable and sell if for scrap and use the money to buy more modern equipment.

    EDIT: I reread the the OP's 2nd post and on this datasheet if you search for 28-21 it'll bring up a 37pin 16AWG connector so my assumptions seem to be correct.

    SIDE NOTE: On the same data sheet they have an 85 pin connector. Wouldn't that be fun to solder?
    Last edited by porkchop; March 20th, 2012 at 10:22 PM.
    Brett Smith
    Touring Stagehand
    Computer Guru
    Avid Shoe Wearer

  9. #9
    CBmod  Premium Member 

    Join Date
    Jul 2005
    Location
    Sydney, Australia
    Occupation
    Consultant
    Posts
    3,332
    Thanks
    34
    Thanked 124 Times in 108 Posts

    Default Re: Funky Cable in the pit.

    I've used that connector extensively, though not for mains voltages.
    37 pin is the size of choice for a 12 channel audio core, and 85 pins works well for 24 (or theoetically 28) channels.

    Soldering them is not an issue, you solder the contacts individually and then insert them into the connector body.

  10. #10

    venuetech's Avatar
    Join Date
    Apr 2008
    Location
    AK, north pacific
    Occupation
    kat
    Posts
    682
    Thanks
    16
    Thanked 26 Times in 24 Posts

    Default Re: Funky Cable in the pit.

    off the top of my head I would just say that it is unlikely to be part of the lighting system. What makes you think it is part of the lighting system?
    Your unterminated dimmers are likely on the grid in a pull box waiting for the acoustical shell that was high on the priority but got cut out of the project just before the dimmer rack was installed.
    I have borrowed such unused (future use) dimmers in the past.. at least till they get around to installing a shell.
    Last edited by venuetech; March 21st, 2012 at 01:49 AM.
    Tom K.

  11. #11

    tdeater's Avatar
    Join Date
    Jun 2009
    Location
    Fremont, MI
    Occupation
    Technical
    Posts
    62
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: Funky Cable in the pit.

    I have a bunch of those scattered about my theater as audio snake connections. If it is in the pit, that seems probable to me. Do you have an audio patch bay around anywhere, or maybe a matching connector in the booth around where the sound board sits? It is possible if you have un-terminated dimmers, they are just extras. When I was in school, the sensor rack that was installed had 6 unused circuits in it, but they where populated with dimmers instead of blanks. It was located in a room right off stage left, so some cabling out of the rack gave me some more useable circuits to play with on stage.

  12. #12


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    Funky Cable in the pit.-img_20120321_083834.jpg
    Here's a picture. There are no others in our whole stage area. I'm almost sure it isn't sound, the only built in sound equipment we have it a PA system and it only has XLR inputs. I noticed some of you said I might be able to use my other dimmers by running cables directly into the dimmer rack.. how would I do that with my CD-80SV? Another weird thing is that the unknown dimmers are 1,2,37,38,39,44,47,48. We have a 24 module rack with dual 2.4kW dimmers.

  13. #13
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,208
    Thanks
    33
    Thanked 182 Times in 163 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Windrider View Post
    Click image for larger version. 

Name:	IMG_20120321_083834.jpg 
Views:	274 
Size:	1.15 MB 
ID:	6690
    Here's a picture. There are no others in our whole stage area. I'm almost sure it isn't sound, the only built in sound equipment we have it a PA system and it only has XLR inputs. I noticed some of you said I might be able to use my other dimmers by running cables directly into the dimmer rack.. how would I do that with my CD-80SV? Another weird thing is that the unknown dimmers are 1,2,37,38,39,44,47,48. We have a 24 module rack with dual 2.4kW dimmers.
    Although the pinout looks the same, the shell is a reverse of the Veam series. On those, the key is on the male and the slot is on the female along with the locking ring. Bit of an odd connector (although Amphenol connectors are well known) so all bets are off. Are there any markings on the cable? Is it a long cable, or is this a tail coming from a box that is less than six feet away?
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  14. #14


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    It has multiple wires coming out of it... going directly under the stage.. maybe I could track it in our basement.

  15. #15
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,208
    Thanks
    33
    Thanked 182 Times in 163 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Windrider View Post
    It has multiple wires coming out of it... going directly under the stage.. maybe I could track it in our basement.
    Ooooh! Interesting twist of the plot line! Follow those wires! (Could be something from an old organ install.)
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  16. #16
    Van
    Van is offline
    CBmod  Premium Member 
    Van's Avatar
    Join Date
    Jul 2006
    Location
    Portland, Or.
    Occupation
    technical director
    Posts
    5,005
    Thanks
    110
    Thanked 292 Times in 250 Posts

    Blog Entries
    12

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by JD View Post
    Ooooh! Interesting twist of the plot line! Follow those wires! (Could be something from an old organ install.)
    You beat me to it! I was just begining to think it might be an organ connector. I remember using Veam but it was always in a production R&R setting never in a permanent install.
    Van J. McQueen
    Technical Director
    Artists Repertory Theatre
    "The only Dumb Question is the one you don't ask."

  17. #17


    Join Date
    May 2009
    Location
    Cedar Rapids, Iowa
    Occupation
    Bldg Maintenance
    Posts
    311
    Thanks
    6
    Thanked 13 Times in 12 Posts

    Default

    Our rebuilt 1927 organ is using multipin for data. Might be something to look into.
    Did someone call for more photons?

    T Robb
    Member, NFPA Electrical Section
    Maintenance & Technician, Community Theatre

  18. #18

    porkchop's Avatar
    Join Date
    Feb 2008
    Location
    What city are we in again?
    Occupation
    Employee
    Posts
    931
    Thanks
    9
    Thanked 31 Times in 30 Posts

    Default Re: Funky Cable in the pit.

    I've seen them used for lighting but only with an external neutral so you have have 24 hots, 12 grounds, and 1 solid support core. Not the best idea I've ever heard, but the show I saw this on was built in 99 with equipment that wasn't exactly brand new.
    Brett Smith
    Touring Stagehand
    Computer Guru
    Avid Shoe Wearer

  19. #19


    Join Date
    Mar 2004
    Occupation
    Other
    Posts
    459
    Thanks
    8
    Thanked 30 Times in 24 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Windrider View Post
    Click image for larger version. 

Name:	IMG_20120321_083834.jpg 
Views:	274 
Size:	1.15 MB 
ID:	6690
    Here's a picture. There are no others in our whole stage area. I'm almost sure it isn't sound, the only built in sound equipment we have it a PA system and it only has XLR inputs. I noticed some of you said I might be able to use my other dimmers by running cables directly into the dimmer rack.. how would I do that with my CD-80SV? Another weird thing is that the unknown dimmers are 1,2,37,38,39,44,47,48. We have a 24 module rack with dual 2.4kW dimmers.
    You may want to drop in to your town's building department and ask to see the blueprints for your school auditorium. I did that and it answered lots of questions I had concerning how things were originally set up. I'm sure that your school didn't have XLR connectors in 1955. Your sound system probably consisted of push-and-twist connectors in the stage floor that were connected to an amp, reel to reel tape player and a record player back stage. The blueprint may also answer your "mystery dimmer" question. You might find a long lost wall pocket, floor pocket, or footlights you didn't know you had. Who knows, the original plans may even solve your cable question.

    You could also try contacting a retired music or AV teacher to see if they can help you.

  20. #20
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Default

    Off the top of my head I cant remember how many pins it has but ive got an old house light control box that has a connector pretty similar to that. Don't think it had that
    Many pins but I'll try to find a picture.



    Doesn't show how many pins but it's pretty similar in size and it's pretty close, so it could be something like that too

    Sent from my iPod touch using Tapatalk
    Last edited by josh88; March 23rd, 2012 at 01:45 PM.
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  21. #21


    Join Date
    Jan 2012
    Location
    Houston, TX
    Occupation
    Facility Manager
    Posts
    63
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Default Re: Funky Cable in the pit.

    Does your pit have a lift? Our original pit lift controller had a very similar connector. A later renovation changed it to a much more robust connector with fewer pins.

  22. #22


    Join Date
    Mar 2008
    Location
    Tacoma, WA
    Occupation
    Broadcast Engineer
    Posts
    863
    Thanks
    0
    Thanked 63 Times in 60 Posts

    Default Re: Funky Cable in the pit.

    That connector isn't rated for enough current for it to be the dimmer outputs. But, it certainly could have been used for an analog control lighting console for a previous dimming system. The building is old enough to have gone through several generations of dimming systems.

  23. #23
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Default Re: Funky Cable in the pit.

    Now that I've looked at the connector on my house lights box I think I'm right. It's labeled "Amphenol" as well. So I'm thinking it had to tie into some system like the box I posted above. Here's mine with the male end.

    Click image for larger version. 

Name:	photo(1).JPG 
Views:	610 
Size:	237.6 KB 
ID:	6708
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  24. #24


    Join Date
    Mar 2012
    Location
    BELOIT, WI
    Occupation
    Paid Volunteer
    Posts
    54
    Thanks
    3
    Thanked 0 Times in 0 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Windrider View Post
    It has multiple wires coming out of it... going directly under the stage.. maybe I could track it in our basement.
    Find it yet?

    I'm guessing it's from an analogue dimmer system, as a on stage/ near stage connection for hang/focus. The local private college has a similar lighting system in an old church turned concert hall. Will get pics 2 compare against.

  25. #25

    venuetech's Avatar
    Join Date
    Apr 2008
    Location
    AK, north pacific
    Occupation
    kat
    Posts
    682
    Thanks
    16
    Thanked 26 Times in 24 Posts

    Default Re: Funky Cable in the pit.

    do the " multiple wires " have any sort of printing on them and how many is multiple?

    photo of the printing on the wire?
    Tom K.

  26. #26

    venuetech's Avatar
    Join Date
    Apr 2008
    Location
    AK, north pacific
    Occupation
    kat
    Posts
    682
    Thanks
    16
    Thanked 26 Times in 24 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Windrider View Post
    Another weird thing is that the unknown dimmers are 1,2,37,38,39,44,47,48. We have a 24 module rack with dual 2.4kW dimmers.
    start guessing. for example where in the theatre is dimmer #2&3? perhaps on the catwalk closest to the booth. then #1&2 may be in the booth

    where are
    45,46?
    35,36?
    50?
    43?
    Tom K.

  27. #27


    Join Date
    Mar 2012
    Location
    BELOIT, WI
    Occupation
    Paid Volunteer
    Posts
    54
    Thanks
    3
    Thanked 0 Times in 0 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by venuetech View Post
    do the " multiple wires " have any sort of printing on them and how many is multiple?

    photo of the printing on the wire?
    the wire looks like 'bell wire' each dimmer has its own cable. each dimmer pack is 12 1.2k dimmers, each dimmer has its own 2 conductor 18awg cable, 2 dimmer pack means 24 cables between dimmer packs and 2 scene preset board. An additional 6 cables go between dimmer pack A and a wall mount fader module. The only way to change which fader controls which dimmer is to move the fader cable to the dimmer you want to control. Risky business considering the age of the equipment, and how touchy the fader module already is.

    I don't have 24/7 access to get pics. Hopefully will have a few minutes tomorrow morn to swing by.

  28. #28


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by FMEng View Post
    That connector isn't rated for enough current for it to be the dimmer outputs. But, it certainly could have been used for an analog control lighting console for a previous dimming system. The building is old enough to have gone through several generations of dimming systems.
    Thats what I thought after i looked into 37 pin socapex and my tech teacher told me she thought the wires had the wrong gauge...

    Quote Originally Posted by marmer View Post
    Does your pit have a lift? Our original pit lift controller had a very similar connector. A later renovation changed it to a much more robust connector with fewer pins.
    Nope nothing fancy like that haha.

    Quote Originally Posted by DrPinto View Post
    You may want to drop in to your town's building department and ask to see the blueprints for your school auditorium. I did that and it answered lots of questions I had concerning how things were originally set up. I'm sure that your school didn't have XLR connectors in 1955. Your sound system probably consisted of push-and-twist connectors in the stage floor that were connected to an amp, reel to reel tape player and a record player back stage. The blueprint may also answer your "mystery dimmer" question. You might find a long lost wall pocket, floor pocket, or footlights you didn't know you had. Who knows, the original plans may even solve your cable question.

    You could also try contacting a retired music or AV teacher to see if they can help you.
    The drama techer suggested that and told a assistant principal had them. its spring break so i have to wait till next week. I shall unlock the secrets of the school like our rumoured hallway across the top of the gym!!!

    Quote Originally Posted by Clarkwg3 View Post
    Find it yet?

    I'm guessing it's from an analogue dimmer system, as a on stage/ near stage connection for hang/focus. The local private college has a similar lighting system in an old church turned concert hall. Will get pics 2 compare against.
    Havent been able to get in the basement yet... its spring break so i have to wait till next week.

    Quote Originally Posted by venuetech View Post
    do the " multiple wires " have any sort of printing on them and how many is multiple?


    photo of the printing on the wire?
    I'll get a picture next week.

  29. #29


    Join Date
    May 2011
    Location
    Rhode Island
    Occupation
    Displaced General-purpose Tech
    Posts
    149
    Thanks
    5
    Thanked 2 Times in 2 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by DrPinto View Post
    You may want to drop in to your town's building department and ask to see the blueprints for your school auditorium. I did that and it answered lots of questions I had concerning how things were originally set up.
    I hate to drag this thread off-topic, but will the building department really just give out blueprints like that? I've been wanting blueprints of our theater for the longest time.
    I may or may not have flown your lunch.

    "Wow, that's a lot of buttons. Do you know what they ALL do?"
    "No, I've just been guessing and getting lucky."

  30. #30


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Lambda View Post
    I hate to drag this thread off-topic, but will the building department really just give out blueprints like that? I've been wanting blueprints of our theater for the longest time.
    I'm just hoping my assistant principal will have them.

  31. #31


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,912
    Thanks
    146
    Thanked 123 Times in 115 Posts

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by Lambda View Post
    I hate to drag this thread off-topic, but will the building department really just give out blueprints like that? I've been wanting blueprints of our theater for the longest time.
    You may have to prove your identity and pay for a copy, but probably.
    Philip LaDue
    9 year member.

  32. #32
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Default

    I'm telling ya it's got the same amphenal label as my house light box, I think it's for an old system like that for control I'd put good money on it


    Sent from my iPod touch using Tapatalk
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  33. #33
     Premium Member 



    Join Date
    Jun 2005
    Location
    Malden MA
    Occupation
    Volunteer
    Posts
    292
    Thanks
    2
    Thanked 12 Times in 12 Posts

    Default Re: Funky Cable in the pit.

    Amphenol is a company that makes (among other things) connectors. Their round ones are very common in the industrial and military world.
    /mike

  34. #34
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Default

    I'm aware, but the theatre I pulled that box from had a pit connection and a backstage connection for it which is why I think it may have been a similar system


    Sent from my iPod touch using Tapatalk
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  35. #35


    Join Date
    Nov 2011
    Location
    Youngstown, Ohio
    Occupation
    Lighting, Sound, A/V, rigger, stage hand, and operator...low budget operation.
    Posts
    8
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default

    I did work in a church that had a connector almost identical to that for an audio snake...its no where near 60 years ild though, so I doubt your connector is for the same thing. Very similar looking though.

    Sent from my BlackBerry Runtime for Android Apps using Tapatalk

  36. #36


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,912
    Thanks
    146
    Thanked 123 Times in 115 Posts

    Default Re: Funky Cable in the pit.

    Amphenol has been making connectors like that for at least 60 years.
    Philip LaDue
    9 year member.

  37. #37

    Aman121's Avatar
    Join Date
    Feb 2012
    Location
    Pittsburgh
    Occupation
    HS Student
    Posts
    315
    Thanks
    16
    Thanked 13 Times in 12 Posts

    Default Re: Funky Cable in the pit.

    If it has multiple wires going to different places, that might rule out lighting control, as youd think that all wires would head to the rack or back to the booth. I wonder if it was for a custom sound system back in the day. There would be a large number of wires exiting the amp rack to go to the different frequency drivers, so this may explain the wires heading off in different directions. It also could be for an organ as mentioned before, I know our theatre had the organ amps under the stage.
    Last edited by Aman121; March 26th, 2012 at 04:54 PM. Reason: Spell Fail

  38. #38


    Join Date
    Nov 2011
    Location
    Long Island-The Hamptons
    Occupation
    HS Student
    Posts
    42
    Thanks
    13
    Thanked 0 Times in 0 Posts

    Default Re: Funky Cable in the pit.

    Any updates on where the cable went?

  39. #39


    Join Date
    Dec 2011
    Location
    Alberta
    Occupation
    HS Student
    Posts
    15
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Thread Starter

    Default Re: Funky Cable in the pit.

    Quote Originally Posted by macwhiz View Post
    Any updates on where the cable went?
    Nope, it still spring break... I won't be in until monday.

  40. #40

    Aman121's Avatar
    Join Date
    Feb 2012
    Location
    Pittsburgh
    Occupation
    HS Student
    Posts
    315
    Thanks
    16
    Thanked 13 Times in 12 Posts

    Default Re: Funky Cable in the pit.

    Any updates yet? Sorry, this is interesting!