    Hey Guys,


    Just a quick question. If i had a 400 Amp 3 phase service, i can technically t-tap the output of that and go in to 2 x 250Amp 3 phase distros and everything should be fine. Is that a correct assumption. Thanks for the help in advance!

  2. #2


    Join Date
    Jul 2008
    Location
    East Coast
    Occupation
    Undergrad
    Posts
    656
    Thanks
    33
    Thanked 28 Times in 19 Posts

    Default

    2 x 250 = 500
    500 > 400

    I would assume no, but someone else will be along shortly...
    ~Scott

  3. #3
     Premium Member 


    Edrick's Avatar
    Join Date
    Mar 2007
    Location
    Boston, MA
    Occupation
    Pro
    Posts
    1,194
    Thanks
    1
    Thanked 19 Times in 13 Posts

    Default

    You can do it it's commonly done but you'll still be limited to the breaker rating.
    Inspire Create Perform | E.S Entertainment | Venue Management
    Edrick Smith | Boston, MA

  4. #4


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,918
    Thanks
    146
    Thanked 124 Times in 116 Posts

    Default Re: distros

    As long as the disconnect is fused or has a breaker go for it.
    Philip LaDue
    9 year member.

  5. #5


    Join Date
    Oct 2008
    Location
    Iowa USA
    Occupation
    Designer/Programmer/Systems Tech
    Posts
    454
    Thanks
    10
    Thanked 8 Times in 7 Posts

    Default Re: distros

    You are still limited to the 400amps, but you can break it out as many times as you want.
    - Will Brown
    Flickr - wbrownLD
    Portfolio - http://wbrown.squarespace.com

  6. #6


    Join Date
    Dec 2006
    Location
    Lititz, PA
    Occupation
    Pro
    Posts
    138
    Thanks
    13
    Thanked 10 Times in 8 Posts

    Default Re: distros

    Quote Originally Posted by avkid View Post
    As long as the disconnect is fused or has a breaker go for it.
    And make sure all your cable is 4/0

  7. #7
     Premium Member 


    STEVETERRY's Avatar
    Join Date
    Aug 2007
    Location
    New York
    Occupation
    Manager/Administrator
    Posts
    1,060
    Thanks
    8
    Thanked 191 Times in 101 Posts

    Default Re: distros

    Quote Originally Posted by LD4tw View Post
    Hey Guys,


    Just a quick question. If i had a 400 Amp 3 phase service, i can technically t-tap the output of that and go in to 2 x 250Amp 3 phase distros and everything should be fine. Is that a correct assumption. Thanks for the help in advance!
    Yes, you can do that under the "tap rule" of NEC section 520.53(H)(3) and (4). If you are using conductors rated at less than 400A between the 400A service and the 250A distros, you are limited to length and routing by these sections:

    (3) Supply Conductors Not Over 3.0 m (10 ft) Long. Where supply conductors do not exceed 3.0 m (10 ft) in length between supply and switchboard or supply and a subsequent overcurrent device, the supply conductors shall be permitted to be reduced in size where all of the following conditions are met:

    (1) The ampacity of the supply conductors shall be at least one-quarter of the current rating of the supply overcurrent protective device.

    (2) The supply conductors shall terminate in a single overcurrent protective device that will limit the load to the ampacity of the supply conductors. This single overcurrent device shall be permitted to supply additional overcurrent devices on its load side.

    (3) The supply conductors shall not penetrate walls, floors, or ceilings or be run through doors or traffic areas. The supply conductors shall be adequately protected from physical damage.

    (4) The supply conductors shall be suitably terminated in an approved manner.

    (5) Conductors shall be continuous without splices or connectors.

    (6) Conductors shall not be bundled.

    (7) Conductors shall be supported above the floor in an approved manner.

    (4) Supply Conductors Not Over 6.0 m (20 ft) Long. Where supply conductors do not exceed 6.0 m (20 ft) in length between supply and switchboard or supply and a subsequent overcurrent protection device, the supply conductors shall be permitted to be reduced in size where all of the following conditions are met:

    (1) The ampacity of the supply conductors shall be at least one-half of the current rating of the supply overcurrent protective device.

    (2) The supply conductors shall terminate in a single overcurrent protective device that limits the load to the ampacity of the supply conductors. This single overcurrent device shall be permitted to supply additional overcurrent devices on its load side.

    (3) The supply conductors shall not penetrate walls, floors, or ceilings or be run through doors or traffic areas. The supply conductors shall be adequately protected from physical damage.

    (4) The supply conductors shall be suitably terminated in an approved manner.

    (5) The supply conductors shall be supported in an approved manner at least 2.1 m (7 ft) above the floor except at terminations.

    (6) The supply conductors shall not be bundled.

    (7) Tap conductors shall be in unbroken lengths.

    ST