    I can't figure this out, though I'm running on very little sleep this week so that may be it, which is why I'm bringing this here. I've got a spot of houselights that are dead. It's one strip of seating, 3 pars and that's consitant with one dimmer the way things are set up. I've determined which dimmer it is, but according to the rack (ETC)that dimmer isn't getting signal. I've swapped out modules (after LOTO) without any success, I've patched it to another channel to make sure, but it clearly isn't that that particular dimmer is bad. I've got no other problems and the rack doesn't show any issues.

    Why would they be like this? I can't imagine that I lost all three of those lamps and they just need to be replaced, though they've been out for awhile and I'm just now getting to that on my list so I guess it could be that they need changing, but I wouldn't think I'd lose all three at the same time. I feel like it's something to do with the fact that it's showing no signal when it should be receiving one. Any ideas?
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  2. #2


    Join Date
    Aug 2012
    Location
    In Washington
    Occupation
    HS Student
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: House Light Dimming Issue

    have you tried changing the light bulbs?

  3. #3


    Join Date
    Oct 2009
    Location
    Doesnt matter
    Posts
    2,199
    Thanks
    103
    Thanked 88 Times in 82 Posts

    Default

    What rack and processor are you using. We had issues of the cem3+ module forgetting part of its patch.

  4. #4
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Thread Starter

    Default Re: House Light Dimming Issue

    Quote Originally Posted by jsusfrk100 View Post
    have you tried changing the light bulbs?
    No, that is why I said it's still possible it could be that, however given the rate at which my lights fail I don't think that's the problem the way it's affecting all three on the dimmer. Because they are over the seats I haven't had time and Maintenance hasn't checked either so it's still on the list.

    Quote Originally Posted by DuckJordan View Post
    What rack and processor are you using. We had issues of the cem3+ module forgetting part of its patch.
    ETC 96 with a classic CEM.
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  5. #5


    Join Date
    Oct 2009
    Location
    Doesnt matter
    Posts
    2,199
    Thanks
    103
    Thanked 88 Times in 82 Posts

    Default

    Check that your center patch is still good, your dmx number should line up with module number in chart, not sure if there is a screen since I've only worked with cem2s and up.

  6. #6
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Thread Starter

    Default Re: House Light Dimming Issue

    Quote Originally Posted by DuckJordan View Post
    Check that your center patch is still good, your dmx number should line up with module number in chart, not sure if there is a screen since I've only worked with cem2s and up.
    I only have a vague idea of what you mean. I will note that the other dimmer in the module ALSO shows that it's not getting signal though the lights on that dimmer are just fine and are obviously gettting signal despite the what the light on the module indicates.
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  7. #7


    Join Date
    Oct 2009
    Location
    Doesnt matter
    Posts
    2,199
    Thanks
    103
    Thanked 88 Times in 82 Posts

    Default Re: House Light Dimming Issue

    excuse my phone typo's,

    Check the CEM patch. find out what slot that dimmer is in, and make sure the corresponding number is attached to a DMX address in the CEM processor. I' not sure if they have a screen on the original CEM's but if they do it should be fairly simple to find that info. otherwise a call to ETC tech support will help. I have a feeling its in the CEM system and not the rack itself.

  8. #8
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,458
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: House Light Dimming Issue

    So both green "Signal" LEDs aren't lit on the D20AF module? On any module you stick in that slot? I'd call ETC at 1.800.688.4116 during non-emergency hours. Sounds like a backplane or edge connector issue in the rack. But if not too difficult, change at least one of the three lamps in question to rule that out.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  9. #9
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Thread Starter

    Default Re: House Light Dimming Issue

    Quote Originally Posted by derekleffew View Post
    So both green "Signal" LEDs aren't lit on the D20AF module? On any module you stick in that slot? I'd call ETC at 1.800.688.4116 during non-emergency hours. Sounds like a backplane or edge connector issue in the rack. But if not too difficult, change at least one of the three lamps in question to rule that out.
    That's right. Neither LED is lit, though one of the slots works just fine. I'll poke around with it on monday and looks like maybe I'll have to give them a call.
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  10. #10


    Join Date
    Feb 2010
    Location
    Atlanta
    Occupation
    Owner/Proprietor
    Posts
    163
    Thanks
    10
    Thanked 7 Times in 7 Posts

    Default Re: House Light Dimming Issue

    Definitely change at least one of the lamps to rule that out. I once spent three hours troubleshooting a circuit problem that turned out to be lamps. The users just didn't notice them going out until the whole row was out.

    On the CEM front, you can use the dimmer key on the CEM to force the dimmer in question on. Its Dimmer # at 100 Enter. It will bypass the console and send direct control from the rack. If the signal light doesn't come on when you do that, there is a problem with that ribbon cable or firing card. Also, remember to clear the rack command when you are done (Dimmer # at Clr Enter), otherwise the console will not be able to control the circuit until you do. The screen should say "Not Set" if you did it right.

    Something just came to mind as I was typing this: Is there an error message saying that slot or dimmer has overheated? The rack won't let that circuit come up until you clear out that error. Hold down the Clr button until the LCD screen says System OK. Then try to bring up the circuit in question.
    Chris Whittle
    Owner-Relight Lighting Repair
    Programmer, repairer, installer, and generally a nice guy.

  11. #11


    Join Date
    Jan 2010
    Location
    Ft Lauderdale FL
    Occupation
    Technician
    Posts
    111
    Thanks
    10
    Thanked 16 Times in 14 Posts

    Default Re: House Light Dimming Issue

    Good Morning Josh

    Try SETTING the dimmer from the CEM
    press the blue DIMMER button, select the dimmer number, AT , (a level like) 50 , ENTER
    check for the SIGNAL light.
    then press AT, CLEAR, ENTER to " NOT SET " that dimmer
    if someone had SET these dimmers & set them to 00 ( AT, 0, ENTER ) the CEM will not listen to the outside world

    the blue ABOUT option is a safe way to see if there is an issue.
    option 1-dimmer, then punch in the dimmer #, ENTER, & right arrow til you get to LEVEL
    if there is a letter after the number, like S , then the dimmer is SET.
    You can always RESET the CEM if you think it a setting


    Good Luck
    Jack Hochberg
    ETCP Electrician
    Service Tech Barbizon FLA

  12. #12
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Thread Starter

    Default

    Yeah I had already tried the above earlier. Overriding at the rack still didn't turn on the signal or the lights. I tried that while I was swapping dimmer modules. And I haven't had any error messages.


    Sent from my iPod touch using Tapatalk
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  13. #13
    Chase  Premium Member 


    chausman's Avatar
    Join Date
    Jul 2010
    Location
    Spokane, WA
    Occupation
    HS Student
    Posts
    2,757
    Thanks
    235
    Thanked 96 Times in 86 Posts

    Blog Entries
    6

    Default Re: House Light Dimming Issue

    Can you put at least one of the non-functional fixtures on a separate channel/circuit/dimmer?

    When you swapped modules, the "new" module had the same symptoms, correct?

    Quote Originally Posted by jhochb View Post
    You can always RESET the CEM if you think it a setting

    That sounds like something I'd want as a very VERY last resort. And not something to try until you knew EXACTLY what was going happen, and was prepared for it.
    Oh...Pretty Colors!!!
    Chase H.
    "If I relax, let up on the gas, I would probably die" - Gordon Ramsay

  14. #14


    Join Date
    Feb 2010
    Location
    Atlanta
    Occupation
    Owner/Proprietor
    Posts
    163
    Thanks
    10
    Thanked 7 Times in 7 Posts

    Default Re: House Light Dimming Issue

    Quote Originally Posted by chausman View Post
    That sounds like something I'd want as a very VERY last resort. And not something to try until you knew EXACTLY what was going happen, and was prepared for it.
    I think he means reboot the rack, not reset the rack. Rebooting will clear any CEM override messages.
    Chris Whittle
    Owner-Relight Lighting Repair
    Programmer, repairer, installer, and generally a nice guy.

  15. #15
     Premium Member 
    josh88's Avatar
    Join Date
    Jan 2010
    Location
    Providence, Rhode Island
    Occupation
    TD, instructor, jack of all trades
    Posts
    931
    Thanks
    25
    Thanked 47 Times in 46 Posts

    Thread Starter

    Default Re: House Light Dimming Issue

    Quote Originally Posted by chausman View Post
    Can you put at least one of the non-functional fixtures on a separate channel/circuit/dimmer?

    When you swapped modules, the "new" module had the same symptoms, correct?
    The new known working module swapped into that slot still had the same issues as the "old" module. and patching those separately from everything else didn't change anything either. I'm planning on calling ETC on monday probably when I get into work just for good measure.
    Josh Smith
    TD/Instructor:Saint Andrew's School/All Children's Theatre- Rhode Island.
    http://mywaytonormal.blogspot.com/

  16. #16


    Join Date
    Jul 2008
    Location
    East Coast
    Occupation
    Undergrad
    Posts
    656
    Thanks
    33
    Thanked 28 Times in 19 Posts

    Default Re: House Light Dimming Issue

    Quote Originally Posted by derekleffew View Post
    Sounds like a backplane or edge connector issue in the rack. But if not too difficult, change at least one of the three lamps in question to rule that out.
    Agreed. Had this issue a few weeks ago when we installed our backup CEM (it got configured as SR24 instead of SP24). This caused all sorts of issues that we originally though were due to the soft patch being wrong but ended up being because the CEM thought it was working with an installed rack, when in reality it is a portable rack. You haven't replaced your CEM recently, have you?
    ~Scott

  17. #17


    Join Date
    May 2009
    Location
    Cedar Rapids, Iowa
    Occupation
    Bldg Maintenance
    Posts
    311
    Thanks
    6
    Thanked 13 Times in 12 Posts

    Default

    Re: Dead Lamps.
    I just had three lobby lamps (MR11 if it matters) die in two days, and they also run off a dimmer rack. It is possible to lose an unusual number of lamps in a short period.
    Did someone call for more photons?

    T Robb
    Member, NFPA Electrical Section
    Maintenance & Technician, Community Theatre

  18. #18
    zmb
    zmb is offline


    Join Date
    Mar 2010
    Location
    Redmond, WA
    Occupation
    High School Student
    Posts
    1,039
    Thanks
    27
    Thanked 27 Times in 24 Posts

    Default Re: House Light Dimming Issue

    Quote Originally Posted by tjrobb View Post
    Re: Dead Lamps.
    I just had three lobby lamps (MR11 if it matters) die in two days, and they also run off a dimmer rack. It is possible to lose an unusual number of lamps in a short period.
    How long have those lamps be installed and were they from the same package? If the lamps are the 12V and have the voltage reducer, maybe something went bad in that?

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •