| CD80SV CC modules needed is being discussed in the ControlBooth Lighting and Electrics forum; Good Morning All I have a venue that wants to put some ETC LED S4 on 3 of their stage ... |

Jack Hochberg
ETCP Electrician
Service Tech Barbizon FLA

Ive been looking for some as well. Strand was unsure if they had any...

Jack Hochberg
ETCP Electrician
Service Tech Barbizon FLA



Exercise some caution here. The choke helps to manage the SCCR rating of the module by providing a partial inrush resistance [in rough terms] to a large short circuit current draw and helping to protect the rest of the power feed. IE, a large enough short could damage components in the module or cause a main feed to trip. Likely? Not really, but then no one really expects a large, low-resistance short-circuit until it happens. You really should put a large, and appropriately class-rated fuse in the module to replace the choke.
WARNING: None of what I have told you to do is covered under the UL or ETL listings for the product. Modification of the product and a failure sometime later with put all liability on the facility and the person doing to modification.
It's a shame someone hasn't yet made a listed module for the tons of these racks that are out there.
One more very important point...there is a real and distinct advantage to using relay modules to power LED fixtures. You make a large investment per LED fixture and you want it to last a long time. A relay module allows you to shut off power to the fixture thereby reducing time on the power supply and allowing it to run for much more time down the road. Protect your investment in LEDs....use relays.
Have fun,
David
Last edited by DavidNorth; September 4th, 2012 at 03:53 PM.
David North
ETC


Yeah. Somebody should.
If only there was a company who was in the business of making modules you can put into dimmer racks...
Mike Nicolai
Milwaukee, WI



Yes, you can remove it, but the technical reason behind my earlier statement still stands. The choke does more than merely create a voltage drop when faced with a sudden change in current [risetime for a forward-phase control dimmer]. The secondary benefit to having a choke in series is a creating a less than sudden current draw through the breaker, bus bars and feed thereby provding another series point of dimmer component, rack and feed protection in the case of a short circuit.
Can you get by with remodeling or modifying your dimmer modules. Probably, but I, for one, do not wish to be in the responsibility chain for any problems arising from information given in this forum. Note that any product modification, especially when it comes to power-handling products, does assume some responsibility and liability.
David
David North
ETC