Protective CAM-lok covers is being discussed in the ControlBooth Lighting and Electrics forum; Here's the problem. For our outdoor 100a-3phase service panel, the CAM's out of the bottom of the panel are exposed, ...

  1. #1
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,956
    Thanks
    83
    Thanked 207 Times in 148 Posts

    Default Protective CAM-lok covers

    Here's the problem. For our outdoor 100a-3phase service panel, the CAM's out of the bottom of the panel are exposed, obviously so that you can plug feeder cable in without having to open the panel up. HOWEVER, it is housed within another panel, that also has an open bottom. We're looking for solutions to protect the female CAM's on the panel from the weather when snow builds up in the winter. Any ideas?
    Mike Nicolai
    Milwaukee, WI

  2. #2
    Van
    Van is offline
    CBmod  Premium Member 
    Van's Avatar
    Join Date
    Jul 2006
    Location
    Portland, Or.
    Occupation
    technical director
    Posts
    5,005
    Thanks
    110
    Thanked 293 Times in 251 Posts

    Blog Entries
    12

    Default Re: Protective CAM-lok covers

    Three solutions come to mind.
    First, Crutch tips, Yes the little rubber things that you can pick up at any drug store or medical supply house, they go on the end of canes to provide traction/protection. They are the perfect size to slide over an exposed male end of a camlock, they also fit neatly into the recess of a female end. When working on Men Of Honor, I bought out several drug stores entire indventory to cap off the spare plugs on spider boxes, lunch boxes etc. This solution is going to set you back around ten dollars.

    Second, Much more expensive, buy some male cam locks, fill the back end < where the cable goes > with epoxy, then use the as plugs, this will provide a water tight / corrosion tight seal. As mentioned, however, this is a much more expensive solution at a couple hundred dollars.

    Third, Install a new panel with NEC approved Wet condition, safety caps on the plugs. This shouldn't be more than a couple thousand dollars.
    Van J. McQueen
    Technical Director
    Artists Repertory Theatre
    "The only Dumb Question is the one you don't ask."

  3. The Following User Says Thank You to Van For This Useful Post:

    MNicolai (July 17th, 2008)

  4. #3


    Join Date
    Mar 2007
    Location
    Houston, Tx
    Occupation
    President/Owner
    Posts
    1,284
    Thanks
    3
    Thanked 45 Times in 44 Posts

    Default Re: Protective CAM-lok covers

    Is there enought room to shove the connectors inside the outer box? If not here is exactly what your looking for

    http://www.crouse-hinds.com/moldedpr...d/j_powerx.pdf

    Look on page 8 (E1016 series is standard cam lock) and what you need are the protective caps.

    FYI this is a really good catalog to have on hand and Here is where i get all of my cam cables from
    J Custom Supply, Inc.
    They have better prices than any one else. And they will sell you everything from raw connectors to cables premade.

  5. The Following User Says Thank You to TimMiller For This Useful Post:

    MNicolai (July 17th, 2008)

  6. #4
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,956
    Thanks
    83
    Thanked 207 Times in 148 Posts

    Thread Starter

    Default Re: Protective CAM-lok covers

    Thanks a lot, guys!

    This same box gave us a bit of frustration today. All 10 cams were held in place using grommets as washers, and they were so small that 3 of the cams broke loose and were only held on by the flexibar straps. Thanks to that I spent two and a half hours weaseling my arm in a funky angle to replace each of the washers, which was followed by moving the straps away from the screws. Previously some of the straps were nearly touching the screws, which would've caused entire phases to directly ground out. I have no idea how in the past six years since the facility opened, nobody became fried by that panel.
    Mike Nicolai
    Milwaukee, WI

  7. #5
    Van
    Van is offline
    CBmod  Premium Member 
    Van's Avatar
    Join Date
    Jul 2006
    Location
    Portland, Or.
    Occupation
    technical director
    Posts
    5,005
    Thanks
    110
    Thanked 293 Times in 251 Posts

    Blog Entries
    12

    Default Re: Protective CAM-lok covers

    Quote Originally Posted by MNicolai View Post
    Thanks a lot, guys!

    This same box gave us a bit of frustration today. All 10 cams were held in place using grommets as washers, and they were so small that 3 of the cams broke loose and were only held on by the flexibar straps. Thanks to that I spent two and a half hours weaseling my arm in a funky angle to replace each of the washers, which was followed by moving the straps away from the screws. Previously some of the straps were nearly touching the screws, which would've caused entire phases to directly ground out. I have no idea how in the past six years since the facility opened, nobody became fried by that panel.

    Please tell me you disconnected the panel prior to sticking your arm in there.......
    Van J. McQueen
    Technical Director
    Artists Repertory Theatre
    "The only Dumb Question is the one you don't ask."

  8. #6
     Premium Member 


    MNicolai's Avatar
    Join Date
    Mar 2008
    Location
    Milwaukee Metro Area
    Posts
    1,956
    Thanks
    83
    Thanked 207 Times in 148 Posts

    Thread Starter

    Default Re: Protective CAM-lok covers

    Quote Originally Posted by Van View Post
    Please tell me you disconnected the panel prior to sticking your arm in there.......
    If I hadn't, I wouldn't be here right now.

    Before I even started I went in with a multimeter to verify nothing was live in the panel, including the feed to it. After turning the power back on, but before closing up shop, I took the multimeter again to verify no current was being carried through the panel, that between phases it correctly read 208VAC, individually 120VAC, and that the panel itself grounded properly.
    Mike Nicolai
    Milwaukee, WI

  9. #7
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,516
    Thanks
    256
    Thanked 963 Times in 786 Posts

    Blog Entries
    4

    Default Re: Protective CAM-lok covers

    Attaboy, MNicolai!

    I saw an interesting Camlok output panel today. A 400A Switch with two sets of outputs, each containing 1x Blk, Red, Blu Females, 2x Wht Males & Females, 1x Grn Male & Female. So a total of NINE receptacles per each row, all with metal spring-loaded covers, 18 total. Very safe, but a bit of a pain as I had to open almost every cover to find the color and gender I needed. I'm guessing the designer/builder never wanted anyone to ever have to use gender-changers. And I always like Grn on the left. Taught a couple of people the correct order to plug in today. And explained, again, unless you can see both ends of the cable, treat it as live.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  10. #8
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,247
    Thanks
    34
    Thanked 186 Times in 167 Posts

    Default Re: Protective CAM-lok covers

    Ah! And even sometimes when you think you see both ends of the cable, it's still live because it was actually two cables!

    Anyway, there is an old saying in Pyro- "Always treat explosives like they are about to go off, because someday they just might!" I find the same rule works pretty well with power. Even when you are absolutely sure something is powered down, don't become "part" of the circuit!

    And then there's this one- The biggest zap I ever got was from a com cable that wasn't connected to anything! It had been strung aerial over to a follow spot platform at an outside gig. There was a storm in the air, but no lightning. I learned a new term that day- "air voltage gradient."
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"