    Is it still used in the industry? I just never seen someone using it so far. Is it because the news machines don't need it? If you are still using it... then when?

    Thanks

  2. #2


    Join Date
    Jun 2008
    Location
    Cincinnati, Ohio
    Occupation
    Freelance
    Posts
    286
    Thanks
    3
    Thanked 6 Times in 6 Posts

    Default Re: The DMX termination plug

    I still like to use them. Some people feel that the risk of corrupt information coming back up the line is very slim and dont feel it is necessary to use them. While the chance is slim the one time you dont use them is the time that something will happen and you may spend 20 mins trouble shooting instead of programing. Although some manufactures do have built in terminators so that is not necessary to use them (most boards have them).
    if its not broken, take it apart find out why it isnt broken and put it back together

  3. #3
    CBmod  Premium Member 
    DaveySimps's Avatar
    Join Date
    Feb 2007
    Location
    Marine City, MI
    Occupation
    Performing Arts Center Manager
    Posts
    2,523
    Thanks
    15
    Thanked 85 Times in 83 Posts

    Default Re: The DMX termination plug

    I still use them in all of my rigs. I also see them reguarly in touring productions with new gear.

    ~Dave

  4. #4


    Join Date
    Feb 2007
    Location
    Canada
    Occupation
    President/Owner
    Posts
    441
    Thanks
    0
    Thanked 25 Times in 23 Posts

    Default Re: The DMX termination plug

    I always use them, the problems are most likely to occur at the end of a long termination and/or when you are approaching the 32 unit load. This is when the DMX signal is approaching its minimum signal parameters.

    This is also why using an optically isolated DMX splitter improves the "reliability" of the command link - because it includes line drivers on the output you have the ability to drive another 32 units on each output.

  5. #5
     Premium Member 


    Kelite's Avatar
    Join Date
    Sep 2005
    Location
    Fort Wayne IN, USA
    Occupation
    Manager/Administrator
    Posts
    1,701
    Thanks
    40
    Thanked 80 Times in 72 Posts

    Blog Entries
    1

    Default Re: The DMX termination plug

    Quote Originally Posted by McCready00 View Post
    Is it still used in the industry? I just never seen someone using it so far. Is it because the news machines don't need it? If you are still using it... then when?

    Thanks

    When responding to Right Arm or Smart Color tech calls, a large percentage of DMX related misbehavior is traced to DMX termination (or lack of, in this case). Moving lights and color scroller PSU's rely upon a clean DMX signal though the entire run, and the longer the DMX run the more chance of reflection, as Church has pointed out.

    DMX termination is very similar to car insurance. Sometimes you'll need the insurance when away from the system, and someone adds/subtracts/substitutes fixtures within your run. It seems rare that these changes are mentioned to the designer/TD/ME until a problem occurs...


    This is a very valid observation, McCready00. I would stick with a DMX terminator at the end of each run.
    Keith Kankovsky
    Apollo Design Technology
    US distributor of Spotlight and Multiform fixtures. Earth-friendly gobos, gel, and other gear at www.apollodesign.net
    *PrintScenic Full Color & B/W gobos for LED profiles
    Laus Deo

  6. #6
    CBmod icewolf08's Avatar
    Join Date
    Jan 2007
    Location
    Salt Lake City, UT
    Occupation
    Master Electrician
    Posts
    3,782
    Thanks
    25
    Thanked 264 Times in 221 Posts

    Default Re: The DMX termination plug

    You should always terminate your DMX lines as it is the proper way to run a DMX distribution system. I have seen plenty of unterminated DMX systems work fine, but at the same time you may not know if some internal motor is a fixtures is sitting there twitching because of reflected data. A terminator costs $5 and 5 minutes to build, so keep them in stock and use them, better safe than sorry.
    Alex Weisman
    Master Electrician - Pioneer Theatre Company
    IceWolf Photography


    Soup or art?

    "...allow me to explain about the theatre business.
    The natural condition is one of insurmountable obstacles on the road to imminent disaster!
    ...Strangely enough, it all turns out well."

    Love CB? Upgrade to premium today!

  7. #7


    Join Date
    Feb 2007
    Location
    Salt Lake Ciity, UT
    Occupation
    Employee
    Posts
    33
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: The DMX termination plug

    I agree - DMX was developed to be a very robust data buss based on EIA 485. But that buss was designed to be terminated with a 120 ohm resistor. It's a simple to add a terminator to each DMX buss to prevent the possibility of reflected data screwing up any fixtures.

    Rick

  8. #8


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,912
    Thanks
    146
    Thanked 123 Times in 115 Posts

    Default Re: The DMX termination plug

    Quote Originally Posted by icewolf08 View Post
    A terminator costs $5
    You're paying too much for parts!
    Philip LaDue
    9 year member.

  9. #9

    zuixro's Avatar
    Join Date
    Aug 2008
    Location
    Spartanburg, SC
    Occupation
    Undergrad
    Posts
    369
    Thanks
    2
    Thanked 5 Times in 3 Posts

    Default Re: The DMX termination plug

    Quote Originally Posted by avkid View Post
    You're paying too much for parts!
    Yeah, Mouser has the connectors for $2.68. The resistor is just a few cents.
    Nick Whitworth
    Sophmore - USC Upstate, Communications Major w/ Emphasis in Theatre

  10. #10
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The DMX termination plug

    See the Glossary entry: http://www.controlbooth.com/forums/g...ight=terminate.
    Quote Originally Posted by Wolf View Post
    ... Although some manufactures do have built in terminators so that is not necessary to use them (most boards have them).
    This is an absolutely UNTRUE statement. By definition, the control console or DMX source cannot terminate the line. Some dimmer racks and devices have a termination switch. I (and others) have yet to be shown a moving light or LED fixture that has "auto-termination" or "self-termination." I cannot recall ever seeing a fixture with a termination switch.

    McCready00, you might find this poll useful: http://www.controlbooth.com/forums/l...ight=terminate. "DO as we say, not as we do."

    Quote Originally Posted by Kelite View Post
    When responding to Right Arm or Smart Color tech calls, a large percentage of DMX related misbehavior is traced to DMX termination (or lack of, in this case).
    Kelite, your manuals need some revision. In previously researching this topic, I found that the RightArm manual does have a one-line remark (with an error!), but could not find any mention of 5-pin termination in the SmartColor manual. See this post: http://www.controlbooth.com/forums/w...tml#post103731.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  11. #11


    Join Date
    Jul 2008
    Occupation
    Employee
    Posts
    49
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: The DMX termination plug

    Quote Originally Posted by derekleffew View Post
    I (and others) have yet to be shown a moving light or LED fixture that has "auto-termination" or "self-termination." I cannot recall ever seeing a fixture with a termination switch.
    Actually, current models of the Source Four Revolution are self-terminating. There's a switch built into the female XLR that connects a termination resistor when nothing is plugged in. Here's a link to the manual. Page 4 is where that feature is described. Apparently they've been that way since at least the beginning of 2007.

  12. #12
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The DMX termination plug

    Thank you for the correction, Malabaristo. Are you aware of any other fixtures having this feature?
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  13. #13
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The DMX termination plug

    EDI Scrimmer Sticks (portable dimmers) have a terminate switch on them. That's the only thing I've seen with one.


  14. #14


    Join Date
    Jul 2008
    Occupation
    Employee
    Posts
    49
    Thanks
    0
    Thanked 1 Time in 1 Post

    Default Re: The DMX termination plug

    Quote Originally Posted by derekleffew View Post
    Thank you for the correction, Malabaristo. Are you aware of any other fixtures having this feature?
    Nope, that's the only one I've seen. Of course, ETC products are what I'm most familiar with, so that shouldn't be terribly surprising. As simple as it is, though, I'm sort of surprised it hasn't been a more popular feature. Especially since lack of termination is so frequently the cause of DMX problems.

  15. #15
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,591
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: The DMX termination plug

    Quote Originally Posted by Malabaristo View Post
    Nope, that's the only one I've seen. Of course, ETC products are what I'm most familiar with, so that shouldn't be terribly surprising. As simple as it is, though, I'm sort of surprised it hasn't been a more popular feature. Especially since lack of termination is so frequently the cause of DMX problems.
    Seems like a really cheap and easy feature for manufacturers to install.


  16. #16


    Join Date
    Jul 2008
    Occupation
    Ld
    Posts
    81
    Thanks
    6
    Thanked 2 Times in 2 Posts

    Default Re: The DMX termination plug

    For how cheap they are, I do no see why you would not use one. If anything it gives you a piece of mind.

  17. #17
     Premium Member 


    STEVETERRY's Avatar
    Join Date
    Aug 2007
    Location
    New York
    Occupation
    Manager/Administrator
    Posts
    1,051
    Thanks
    8
    Thanked 188 Times in 98 Posts

    Default Re: The DMX termination plug

    Quote Originally Posted by Malabaristo View Post
    Actually, current models of the Source Four Revolution are self-terminating. There's a switch built into the female XLR that connects a termination resistor when nothing is plugged in. Here's a link to the manual. Page 4 is where that feature is described. Apparently they've been that way since at least the beginning of 2007.
    This is correct. I forgot that we implemented this in 2007. Moral of this story: never ask the VP of R&D about product details.

    :-)

  18. #18

    porkchop's Avatar
    Join Date
    Feb 2008
    Location
    What city are we in again?
    Occupation
    Employee
    Posts
    931
    Thanks
    9
    Thanked 31 Times in 30 Posts

    Default Re: The DMX termination plug

    The tour I'm on doesn't even have a single terminator in stock. This drives me nuts if you ask me you should terminate every dmx run. Like we've illustrated they are cheap and often the misbehavior can be seem by people not looking for it. I have seen High End techno's that need to be terminated always, but I can't say that I've noticed any thing not working right with our current unterminated rig.
    Brett Smith
    Touring Stagehand
    Computer Guru
    Avid Shoe Wearer

  19. #19
    JD
    JD is offline

    JD's Avatar
    Join Date
    Jan 2005
    Occupation
    President/Owner
    Posts
    2,199
    Thanks
    32
    Thanked 182 Times in 163 Posts

    Default Re: The DMX termination plug

    Anybody that has looked at the signal with & without on a scope will opt to terminate!
    John Dziel
    DAE Concert Lighting
    founded 1971
    Intelligent Lighting Solutions
    "Oh, that switch also fed the Hotel ?"

  20. #20


    Join Date
    Mar 2007
    Location
    Washington State
    Occupation
    Manager/Administrator
    Posts
    8
    Thanks
    1
    Thanked 0 Times in 0 Posts

    Default Re: The DMX termination plug

    I can detect a noticeable difference when I take my terms off my units; my technobeams will occasionally bounce around as if receiving occasional incorrect settings. It's foolish not to use terminators if you are running anything more than a few feet from a splitter or console.

    I'm not familiar with any movers (I haven't used the Revolution) that have self-termination, but many dimmer systems have either a switch or they auto-terminate. I seem to recall that some of Wybron's color scroller power supplies self-terminate, but that might just be referring to the scroller data lines, not the actual DMX. I'm not sure.

  21. #21
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,455
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: The DMX termination plug

    Quote Originally Posted by Malabaristo View Post
    Nope, that's the only one I've seen. Of course, ETC products are what I'm most familiar with, so that shouldn't be terribly surprising. As simple as it is, though, I'm sort of surprised it hasn't been a more popular feature. Especially since lack of termination is so frequently the cause of DMX problems.
    For anyone interested in building one's own DMX devices, here is the Neutrik spec sheet on the connector in question, as used on the ETC Revolution: Neutrik - Industrial - A Series - NC5FAV-SW.



    The SmartPack uses this connector also, as evidenced in this statement:
    DMX may be daisy-chained from one panel to another utilizing the XLR connectors on the front of
    the unit. When daisy-chaining DMX, utilizing only the XLR connectors, the DMX-Thru connector is
    self terminated when no connection is made.

    from this document: http://www.etcconnect.com/docs/docs_...SetupGuide.pdf.
    Last edited by derekleffew; December 1st, 2011 at 11:12 AM. Reason: updated Neutrik link
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  22. #22


    Join Date
    Mar 2007
    Location
    Houston, Tx
    Occupation
    President/Owner
    Posts
    1,281
    Thanks
    3
    Thanked 45 Times in 44 Posts

    Default Re: The DMX termination plug

    personally i would prefer pushing a termination button or plugging in a terminator over relying on a fixture to self terminate. I would fear that something would eventually get corroded and the fixture would decide to terminate or not terminate when it should and with my luck i would have a fixture in the middle of the run decide to terminate itself on top of the fixture at the end being terminated and cause the entire data run to freak out due to there being two terminators on the line. If it can go wrong it eventually will. I still cant get over the time i had a data cable coming off of the first fixture decide to quit during the second song in a show. It had been working fine for the previous 2 days of programming.