Im having a lighting problem. i have a grand ma. one day i came in and turned on the board and just about every light in my rig was going nuts. All the faders were down. I hadnt even done anything yet. I have 14 vl3000's, 4 vl3500's a bunch of pars and likos, and 26 color blast 12's. But like i said i turned on the board and you could hear the vl's strobing, the color blasts were changing colors and flickering, and pars and likos were blinking. This lasts for about ten minutes, then it stops. i also have a ghosting problem with one set of color blasts. its a set of four. They are on a pds-150 power supply. They will not stop flickering when the board is on. Ive changed the dmx cable, ive moved the power from one input to another and it still does it. what could be the problem?
|
|
||||
|
I'm sure you'll get some more, and better, input soon but the first question I would address is termination. Go back and double check everythingmake sure your runs are properly terminated. If you are running through a opto splitter then remove all the cables and plug them back in one at a time se if just one of the lines makes all the others freak, if so then you know your issue may be in that line < although if using an Opto-isolated splitter this shouldn't happen at all.> The ghosting issue also sounds like a termination issue.
__________________
Van J. McQueen Technical Director Artists Repertory Theatre Some people are like Slinkies... Not really good for anything, But they still bring a smile to your face......... When you push them down a flight of stairs..... |
|
||||
|
Is there an NSP involved?
__________________
|
|
|||
|
Also, have you re-run any DMX or power cable recently? Running DMX (or any signal cable) next to mains power or even multi or jumper can cause interference in the DMX signal and possibly corruption of data.
We had problems with twitchy scrollers last year during a local dance concert; turned out the DMX run from the console back in the booth to the cove where our scroller power supplies were was lying right next to the five multi's we had running out there. Just moving the cables to the opposite sides of the 3' walkway solved that problem tidily. 73
__________________
Jeff Glass Lightable.Blogspot.com |
|
||||
|
Yeah I've had Swami's problem too. At an unamed location they but the back-up generator for the otherside of the campus next to our dimmers. Someone pushed the test button on the generator and there after it would go into a test mode at the same time each week....really screws up a tech when you're lights flash for no reason.
__________________
6 P's to live by: Piss Poor Planning Prevents Positive Performance 4 P's for LD's Producers Prefer Pretty Photographs. Nothing like being focused and desperate to make me remember how something works. ~Steve B |
|
||||
|
Quote:
I can tell you a story about a generator close to my school that didn't have this feature. A gas main exploded at one of the school buildings on my campus (Don't ask how...we never found out) and caused the fire department to give an order to cut the power to the whole town. Well that causedn a generator close by at a Pre-School to activate, this generator wasn't well maintained and didn't have an exercisor or diagnostic check recently. Well...to make a long story short...it exploded and took out an entire wall of the Pre-School. Luckly it happened at night around 9pm when no one was around. |
|
||||
|
This was years ago Sony....the funny story is that the head of mainenance had to come out to figure out what was going on. His subordinates never could. They fixed that problem after only 6 months.
__________________
6 P's to live by: Piss Poor Planning Prevents Positive Performance 4 P's for LD's Producers Prefer Pretty Photographs. Nothing like being focused and desperate to make me remember how something works. ~Steve B |
|
|||
|
I have zero experience with the MA, but could it be possible that there is a macro set to run on startup? Only reason I have to believe that it is not a problem due to power is that you say it runs on startup of the console, which should really not have anything to do with the powering of the fixtures unless you are powering the fixtures through relays in dimmer rack.
Not really sure about the ColorBlast problem. I would suspect a cabling issue somewhere along the line. |
|
||||
|
Quote:
__________________
6 P's to live by: Piss Poor Planning Prevents Positive Performance 4 P's for LD's Producers Prefer Pretty Photographs. Nothing like being focused and desperate to make me remember how something works. ~Steve B |
![]() |
| Tags |
| (no prefix), ghosting, grandma, lighting, problems |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Cable and plug types for stage jumpers | ship | Lighting | 39 | June 10th, 2009 02:29 AM |
| Was E.G. Craig a time traveler or understanding the past as a concept. | ship | Lighting | 1 | October 17th, 2007 11:44 PM |
| Theatre Books | derekleffew | Collaborative Articles | 2 | October 8th, 2007 04:06 PM |
| book list | ship | General Advice | 13 | February 11th, 2007 01:12 AM |