with regard to the drop:
the power company uses wire with a pretty high temperature rating, and they are paying for the lost power from the voltage drop, so they can get away with smaller wire. #6 is small for 200amp though. Around here they use #2al for 200amps. As far as the transformer, 20kva seems a little small. On my street they have a 50kva feeding a dozen houses. These transformers are under rated and can withstand extreme temperatures. The primary is usually fused at 300%, and if it ever blows they will replace the transformer with a larger one. |
|
|||
|
On the neutral at the service entrance panel or in some cases the meter base it is bonded to ground any way so the guy wire neutral is only a reference between points. That is up here the norm
the feeder is undersized but in free air there is a different rating involved I wonder if it was sized for a 100amp service originally |
|
|||
|
I once had a 50k dollar bill from highend, due to the neutral conductor melting down out on the pole. You could tell where they did a really poor job splicing, and caused the rig to brown out, as it was shorting then caught fire. Of course the electric company has a "no fault clause" and said your screwed have a nice day. Around here its the same story with about #8 feeding our houses. 200A service gets a #8 wire. I am waiting for the day it melts. (same story at my girlfriends, and her 200A service not only feeds her house, but her well, and several other distribution points that have around a 125-200A main by themselves). The main service coming in is on a 200A breaker, so that will pop or the wire will melt. Even bigger story, same way at my uncles house. His house consists of 3 panels. The mobile home panel being main breakered at 200A. Just for some of you guys, a mobile home box has a main breaker installed along with breakers for about 10 or so feeder circuits, but on the bottom of the buss bars, there are lugs for attaching on another panel. So from the lugs off the bottom, there is a run of 2/0 that runs into the race way buss. (everyone should have a raceway with panels behind their house). From here the wire is split off to the other two panels, one being the house, the other being the pool. He is the only one i know who has managed to trip his main breaker before, from everything running off of it. So far no wire melting but we shall see.
There really needs to be a code established for the electric companies. They can actually do what they want as far as what they run, and if their transformer melts down, catches your house on fire, guess what they are not at fault all due to their no fault clause. |
|
||||
|
Quote:
*ground propagation - Basically, the earth is a big resistor. If you stick two metal rods into it a few feet apart, and connect them to a car battery, you can stick a third pole in between the two and measure the voltage with a multimeter. Depending on where you stick the middle pole, you will get a mathematical divide of the source voltage. Of course, soil varies greatly in conduction so it will rarely be liner.
__________________
John Dziel DAE Concert Lighting founded 1971 Intelligent Lighting Solutions "Oh, that switch also fed the Hotel ?" |
|
|||
|
First off, the power company can use smaller conductors on the drop because of the insulation type and because it is in free air, which allows it to dissipate heat readily.
Secondly, transformers are seldom sized to handle the full rated current of all the disconnect breakers. The NEC recognizes that all of the loads in a building are not used all at the same time. Common types of home loads, such as stoves, ovens, water heaters are computed with a use factor. Some commercial and industrial loads would be calculated at 100%, but not in homes. Put another way, if your home's service is 200 Amps, chances are you'd never come close to actually drawing that amount. I'd be surprised to measure half of that with several major appliances running. The power company knows that, so they factor it in when sizing their equipment. Electrical service transformers are also built with a huge safety margin. Several years ago, I had the electrical service for a tower site with two FM stations redone. We discovered that the transformer was rated at 40 kVA. The measured load was about 80 kVA. That transformer survived doing that for decades, 24 hours a day. Last edited by FMEng; March 7th, 2009 at 04:32 PM.. |
|
|||
|
The only time they get very concerned about the transformer size is usually if the wireing permit is specified with electric heating being installed When I wired my parents new house because of the fact natural gas wasn't available we installed a electric furnace and heat pump system based on its square footage we were compelled under the code to install a 400amp service
The utility company did have to provide a different pole transformer based on the load |
![]() |
| Tags |
| code , code…, companies, electric, follow |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Lamp Questions | ship | Lighting | 57 | August 4th, 2009 09:14 AM |
| Your opinions of Cordless Drill-Drivers | ship | Scenery | 84 | January 29th, 2009 12:49 AM |
| Was E.G. Craig a time traveler or understanding the past as a concept. | ship | Lighting | 1 | October 17th, 2007 11:44 PM |
| Lamps | derekleffew | Collaborative Articles | 0 | October 9th, 2007 01:59 PM |
| Electric | gafftaper | Glossary A-E | 0 | July 14th, 2007 03:46 AM |