The exact model of Lycian followspot would have been helpful information, but assuming it's a 120V unit (1209, 1266, 1271, etc.)...
Quote:
Quote:
Quote:
A 20A differential will not even be noticed in any dimmer rack larger than 12x2.4kW. If this is an installed rack, the feeder was sized with load diversity in mind. Unless your input power is severely undersized, you needn't worry.
__________________
|
|
||||
|
I second Derek. We run followspots through our racks all the time using CC-20 or R-20 modules. Either way it is not a dimmer and thus it works fine. Just remember that if you use R-20 modules that oyu need to park them on or make sure they stay on for the entire show or you might have some angry spot ops!
__________________
Alex Weisman Master Electrician - Pioneer Theatre Company IceWolf Photography Soup or art? "Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me Love CB? Upgrade to premium today! |
|
||||
|
You can run a followspot on a constant on module (as in breaker only) but do not run them on a SSR or other solid state module. When the igniter fires, it can "backfire" through the ac cord. No problem whatsoever as long as the device is in conduction at the time, but if you are unlucky enough for the SSR to be at ZVC (and thus "off") when the flyback voltage hits, then you will cook the device due to overvoltage. This is true only on magnetic ballasts that use series PF caps as compared an input parallel PF cap.
__________________
John Dziel DAE Concert Lighting founded 1971 Intelligent Lighting Solutions "Oh, that switch also fed the Hotel ?" |
|
|||
|
Model would still be a good thing to give us, Lycian makes a few model numbers that can be several voltages. I know with the 1290XLTs if you only have 20A you need to have them on 208V - 240V service where they can also run at 120V but only on a 30A service. I doubt if you're running through the box booms that your lights are that big (you'd probably melting performers onstage) but still it's a good thing to check.
__________________
Brett Smith Electrician Assistant Feld Entertainment Computer Guru Avid Shoe Wearer |
|
||||
|
Thanks for the responses.
The spots are Lycian 1271. They all run off 120V. The two in the booth have been running for years with 15A plugs. I am going to upgrade all of them to 20A plugs first chance I get.
__________________
- Will When you do things right, people won’t be sure you’ve done anything at all." - God - Futurama
|
|
|||
|
Changing the connectors and outlets to 20A is probably not necessary, especially if it's been behaving politely for years already. The unit might draw more than 15 amps at strike, but once the arc is established it should drop under 15 amps - Lycian shows that unit as being a 1200 w HMI lamp. If there isn't an amp meter on the unit, you could get a clamp-on meter and check that way.
Call me at work if you can't find one in IC (I did a power tie-in for you at the children's museum a month or so ago, if you haven't figured out who I am), and I'll dig one up for you to borrow.
__________________
The things that can go wrong, will go wrong, in precisely the order you are least prepared for. |
|
||||
|
Quote:
Once I've realized that they were only 15a, I struck (striked?) the lamp and let it run for like 3-5 min. The prongs were hot, and I regretted touching them (not hot enough to burn). Also the first foot or so of cable was warm. The heat could of just been from striking, I've never tested after it had been on for a show. I would feel safer with 20a plugs, but if its not necessary we wont get it. I've got a few weeks before they are needed again, so I will have time to test it.
__________________
- Will When you do things right, people won’t be sure you’ve done anything at all." - God - Futurama
|
|
|||
|
Corrosion on the blades, or loose connections inside the plug could also cause the heat. Was reading a post here recently to the effect that there isn't any more copper in a 5-20 edison than in a 5-15 (the different blade config was to prevent 20A devices from being plugged into 15A breakers), which adds to my doubts that amperage alone is a problem here.
See you tomorrow, perhaps.
__________________
The things that can go wrong, will go wrong, in precisely the order you are least prepared for. |
|
||||
|
It has yet to be proved to me that the NEMA 5-20 plug contains more conductive material or surface area than the NEMA 5-15. Furthermore, I know of no 120V followspot that comes from the manufacturer with anything other than a 5-15 plug (speaking only for US practices).
__________________
|
![]() |
| Tags |
| dimmer, follow, rack, running, spot |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Lamp Questions | ship | Lighting | 57 | August 4th, 2009 08:14 AM |
| Followspot | rochem | Glossary F-L | 0 | April 12th, 2009 04:49 AM |
| Building and Training a Running Crew | bendersen | Collaborative Articles | 0 | January 22nd, 2008 03:36 AM |
| Lamps | derekleffew | Collaborative Articles | 0 | October 9th, 2007 12:59 PM |
| Hooking a Follow Spot into a Dimmer | krhodus | Lighting | 25 | November 16th, 2005 04:40 PM |