Default Running a Follow spot through our dimmer rack

I sent an email to a local ME but I thought I'd get good responses here too.
For an upcoming show the renters want to put 2 of our follow spots in two of our box booms. There is not a 20a circuit anywhere close to the position. We have plenty of open dimmer circuits in the box. We have two Constant Current Units that we can use. So the spotlight would not be running through a dimmer.
They are Lycian follow spots, on the ballast it says its rated for 20a. The Sensor + constant current units are rated at 20a. I would have to put a 20a plug on the 3pin to Edison converter.
The thing I am worried about is pulling too much from one leg. The circuits would not be next to each other, so in theory I can put them on different legs.

Is it alright to run the spotlights through the dimmers? Or should we run dedicated circuits to the boxes?
__________________
- Will
When you do things right, people won’t be sure you’ve done anything at all." - God - Futurama
Reply With Quote
Old April 15th, 2009, 01:18 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,535
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Running a Follow spot through our dimmer rack

The exact model of Lycian followspot would have been helpful information, but assuming it's a 120V unit (1209, 1266, 1271, etc.)...
Quote:
Originally Posted by willbb123 View Post
...We have two Constant Current Units that we can use. So the spotlight would not be running through a dimmer. ...
Quote:
Originally Posted by willbb123 View Post
...Is it alright to run the spotlights through the dimmers? ...
If you're using ETC CC-20 modules, you're not running the followspots through the dimmers. You are running them through the dimmer rack, but they are not on a dimmer.

Quote:
Originally Posted by willbb123 View Post
...They are Lycian follow spots, on the ballast it says its rated for 20a. The Sensor + constant current units are rated at 20a. I would have to put a 20a plug on the 3pin to Edison converter.
What input connector is on the ballast now? Just use the mating female connector on your 2P&G to (NEMA 5-15?) adapter.

Quote:
Originally Posted by willbb123 View Post
...The thing I am worried about is pulling too much from one leg. The circuits would not be next to each other, so in theory I can put them on different legs. ...
A 20A differential will not even be noticed in any dimmer rack larger than 12x2.4kW. If this is an installed rack, the feeder was sized with load diversity in mind. Unless your input power is severely undersized, you needn't worry.
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
Old April 15th, 2009, 02:09 PM
icewolf08's Avatar
CBmod
 Premium Member 
 
Join Date: Jan 2007
Location: Salt Lake City, UT
Posts: 3,099
Thanks: 21
Thanked 150 Times in 134 Posts
Send a message via AIM to icewolf08 Send a message via MSN to icewolf08 Send a message via Yahoo to icewolf08 Send a message via Skype™ to icewolf08
Default Re: Running a Follow spot through our dimmer rack

I second Derek. We run followspots through our racks all the time using CC-20 or R-20 modules. Either way it is not a dimmer and thus it works fine. Just remember that if you use R-20 modules that oyu need to park them on or make sure they stay on for the entire show or you might have some angry spot ops!
__________________
Alex Weisman
Master Electrician - Pioneer Theatre Company
IceWolf Photography
[email address]

Soup or art?

"Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me

Love CB? Upgrade to premium today!
Reply With Quote
Old April 15th, 2009, 03:11 PM
JD's Avatar
JD JD is offline

 
Join Date: Jan 2005
Posts: 933
Thanks: 7
Thanked 57 Times in 52 Posts
Default Re: Running a Follow spot through our dimmer rack

You can run a followspot on a constant on module (as in breaker only) but do not run them on a SSR or other solid state module. When the igniter fires, it can "backfire" through the ac cord. No problem whatsoever as long as the device is in conduction at the time, but if you are unlucky enough for the SSR to be at ZVC (and thus "off") when the flyback voltage hits, then you will cook the device due to overvoltage. This is true only on magnetic ballasts that use series PF caps as compared an input parallel PF cap.
__________________
John Dziel
DAE Concert Lighting
founded 1971
Intelligent Lighting Solutions
"Oh, that switch also fed the Hotel ?"
Reply With Quote
Old April 15th, 2009, 03:48 PM

 
Join Date: Feb 2008
Location: What city are we in again?
Posts: 525
Thanks: 1
Thanked 10 Times in 10 Posts
Send a message via AIM to porkchop Send a message via MSN to porkchop Send a message via Yahoo to porkchop
Default Re: Running a Follow spot through our dimmer rack

Model would still be a good thing to give us, Lycian makes a few model numbers that can be several voltages. I know with the 1290XLTs if you only have 20A you need to have them on 208V - 240V service where they can also run at 120V but only on a 30A service. I doubt if you're running through the box booms that your lights are that big (you'd probably melting performers onstage) but still it's a good thing to check.
__________________
Brett Smith
Electrician Assistant Feld Entertainment
Computer Guru
Avid Shoe Wearer
Reply With Quote
Old April 15th, 2009, 06:29 PM
willbb123's Avatar
 Premium Member 

 
Join Date: Oct 2008
Location: Iowa USA
Posts: 369
Thanks: 8
Thanked 4 Times in 4 Posts
Send a message via AIM to willbb123 Send a message via Skype™ to willbb123
Default Re: Running a Follow spot through our dimmer rack

Thanks for the responses.
The spots are Lycian 1271. They all run off 120V.
The two in the booth have been running for years with 15A plugs. I am going to upgrade all of them to 20A plugs first chance I get.
__________________
- Will
When you do things right, people won’t be sure you’ve done anything at all." - God - Futurama
Reply With Quote
Old April 15th, 2009, 10:07 PM

 
Join Date: Mar 2009
Location: Midwest US
Posts: 103
Thanks: 0
Thanked 2 Times in 2 Posts
Default Re: Running a Follow spot through our dimmer rack

Changing the connectors and outlets to 20A is probably not necessary, especially if it's been behaving politely for years already. The unit might draw more than 15 amps at strike, but once the arc is established it should drop under 15 amps - Lycian shows that unit as being a 1200 w HMI lamp. If there isn't an amp meter on the unit, you could get a clamp-on meter and check that way.

Call me at work if you can't find one in IC (I did a power tie-in for you at the children's museum a month or so ago, if you haven't figured out who I am), and I'll dig one up for you to borrow.
__________________
The things that can go wrong, will go wrong, in precisely the order you are least prepared for.
Reply With Quote
Old April 15th, 2009, 10:48 PM
willbb123's Avatar
 Premium Member 

 
Join Date: Oct 2008
Location: Iowa USA
Posts: 369
Thanks: 8
Thanked 4 Times in 4 Posts
Send a message via AIM to willbb123 Send a message via Skype™ to willbb123
Default Re: Running a Follow spot through our dimmer rack

Quote:
Originally Posted by FatherMurphy View Post
Changing the connectors and outlets to 20A is probably not necessary, especially if it's been behaving politely for years already. The unit might draw more than 15 amps at strike, but once the arc is established it should drop under 15 amps - Lycian shows that unit as being a 1200 w HMI lamp. If there isn't an amp meter on the unit, you could get a clamp-on meter and check that way.

Call me at work if you can't find one in IC (I did a power tie-in for you at the children's museum a month or so ago, if you haven't figured out who I am), and I'll dig one up for you to borrow.
Holy Cow... I know someone on the forum!!! I sent you a PM by the way.

Once I've realized that they were only 15a, I struck (striked?) the lamp and let it run for like 3-5 min. The prongs were hot, and I regretted touching them (not hot enough to burn). Also the first foot or so of cable was warm. The heat could of just been from striking, I've never tested after it had been on for a show.

I would feel safer with 20a plugs, but if its not necessary we wont get it.
I've got a few weeks before they are needed again, so I will have time to test it.
__________________
- Will
When you do things right, people won’t be sure you’ve done anything at all." - God - Futurama
Reply With Quote
Old April 15th, 2009, 11:03 PM

 
Join Date: Mar 2009
Location: Midwest US
Posts: 103
Thanks: 0
Thanked 2 Times in 2 Posts
Default Re: Running a Follow spot through our dimmer rack

Corrosion on the blades, or loose connections inside the plug could also cause the heat. Was reading a post here recently to the effect that there isn't any more copper in a 5-20 edison than in a 5-15 (the different blade config was to prevent 20A devices from being plugged into 15A breakers), which adds to my doubts that amperage alone is a problem here.

See you tomorrow, perhaps.
__________________
The things that can go wrong, will go wrong, in precisely the order you are least prepared for.
Reply With Quote
Old April 15th, 2009, 11:07 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,535
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Running a Follow spot through our dimmer rack

Quote:
Originally Posted by willbb123 View Post
...I would feel safer with 20a plugs, but if its not necessary we wont get it. ...
It has yet to be proved to me that the NEMA 5-20 plug contains more conductive material or surface area than the NEMA 5-15. Furthermore, I know of no 120V followspot that comes from the manufacturer with anything other than a 5-15 plug (speaking only for US practices).
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
Reply

Tags
dimmer, follow, rack, running, spot

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lamp Questions ship Lighting 57 August 4th, 2009 08:14 AM
Followspot rochem Glossary F-L 0 April 12th, 2009 04:49 AM
Building and Training a Running Crew bendersen Collaborative Articles 0 January 22nd, 2008 03:36 AM
Lamps derekleffew Collaborative Articles 0 October 9th, 2007 12:59 PM
Hooking a Follow Spot into a Dimmer krhodus Lighting 25 November 16th, 2005 04:40 PM


All times are UTC -4. The time now is 06:28 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.1 
Advertisement System V2.6 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80