Quote:
Originally Posted by mrb
Is SJO cable allowed to be used in a theater (for use other than breakouts and two-fers)? I saw a new install and all the cable was SJO. I was under the impression the NEC calls for pretty much everything except breakouts and two-fers to be SO cable. I appreciate any info
|
For areas covered by NEC article 520, it has to be extra-hard usage cable, that is type S and derivatives. Junior hard service cord, type SJ and derivatives is only allowed for twofers and breakouts under certain length and mounting restrictions.
520.1 Scope.
This article covers all buildings or that part of a building or structure, indoor or outdoor, designed or used for presentation, dramatic, musical, motion picture projection, or similar purposes and to specific audience seating areas within motion picture or television studios.
For assembly occupancies covered by Article 518 , both types are acceptable. However, Article 520 rules, even in 518 spaces, under certain conditions:
518.1 Scope.
Except for the assembly occupancies explicitly covered by 520.1, this article covers all buildings or portions of buildings or structures designed or intended for the gathering together of 100 or more persons for such purposes as deliberation, worship, entertainment, eating, drinking, amusement, awaiting transportation, or similar purposes.
518.2 General Classification.
(A) Examples. Assembly occupancies shall include, but not be limited to, the following:
Armories Exhibition halls
Assembly halls Gymnasiums
Auditoriums Mortuary chapels
Bowling lanes Multipurpose rooms
Club rooms Museums
Conference rooms Places of awaiting transportation
Courtrooms Places of religious worship
Dance halls Pool rooms
Dining and drinking
facilities Restaurants
Skating rinks
(B) Multiple Occupancies. Where an assembly occupancy forms a portion of a building containing other occupancies, Article 518 applies only to that portion of the building considered an assembly occupancy. Occupancy of any room or space for assembly purposes by less than 100 persons in a building of other occupancy, and incidental to such other occupancy, shall be classified as part of the other occupancy and subject to the provisions applicable thereto.
(C) Theatrical Areas. Where any such building structure, or portion thereof, contains a projection booth or stage platform or area for the presentation of theatrical or musical productions, either fixed or portable, the wiring for that area, including associated audience seating areas, and all equipment that is used in the referenced area, and portable equipment and wiring for use in the production that will not be connected to permanently installed wiring, shall comply with Article 520.
FPN: For methods of determining population capacity, see local building code or, in its absence, NFPA 101-2006, Life Safety Code.
(copyright NFPA)
ST
|