Default Balanced Phases?

At which point does it have to be balanced? Since most buildings have systems to automatically balance the phases, do we still have to follow the 10%max unbalanced law?

And by using a generator for power, do I really need to balance them as much as I can?

I always try to balance my phases as much as i can, but i would like to know more about how people works with it. f

Last question; if i am not using any motors or generator in the events, what should my phases have to be well balanced? Let's say I do have 75 amps returning through my neutral (2/0 feeder), what this could be dangerous for?
Reply With Quote
Old November 6th, 2009, 03:38 PM
Footer's Avatar
Senior Team
 Premium Member 
 
Join Date: Nov 2005
Location: Saratoga Springs, NY
Posts: 3,753
Thanks: 1
Thanked 134 Times in 129 Posts
Default Re: Balanced Phases?

Quote:
Originally Posted by mrb View Post

What are these systems buildings have to automatically balance phases? -thats a new one....
Agreed.... more elaboration on that... if these do exist... and I don't think they do.. why are they not built into every company switch or dimmer/distro?
__________________
Kyle Van Sandt
Technical Director
Home Made Theater
Van Sandt Designs
Reply With Quote
Old November 6th, 2009, 04:03 PM
icewolf08's Avatar
CBmod
 Premium Member 
 
Join Date: Jan 2007
Location: Salt Lake City, UT
Posts: 3,103
Thanks: 21
Thanked 150 Times in 134 Posts
Send a message via AIM to icewolf08 Send a message via MSN to icewolf08 Send a message via Yahoo to icewolf08 Send a message via Skype™ to icewolf08
Default Re: Balanced Phases?

As far as I know there are no systems that automatically balance loads on phases. When a building is built the electrical contractors have to design the systems so that during normal operation the phases stay as close to balanced as possible. This means that they need to calculate the average loads of all the electrical systems including HVAC, dimmers, wall outlets, room lighting, etc. and then distribute accordingly.

Generally (not always) permanent installed dimmers are wired such that each dimmer module alternates phases. As most current installed racks have two dimmers on each module, you have two dimmers alternating. So, dimmers 1&2 would be phase A, 3&4 B, 5&6 C, 7&8 A and so on. This allows for the "arbitrary" loading that occurs when you hang and circuit a show.

On the other hand, touring and portable racks are often just divided into thirds. In a 48 channel rack, dimmers 1-16 would be phase A, 17-32 B, and 33-48 C. This is when you have to pay attention to how you load up your rack. Generally in this situation, you would look at the loads that are on each circuit and then patch them into the rack to make as close to a balanced system as possible. You have to consider that when balancing a dimming system, not all the lights will be on at full at the same time. Thus, the farther out of balance you start at, the more potential there is to be way out of balance when you start running the show.

I can't speak to use of generators as I don't work with them all to often. Just know that when using a generator it can be even more important to have as close to a balanced load as you can.
__________________
Alex Weisman
Master Electrician - Pioneer Theatre Company
IceWolf Photography
[email address]

Soup or art?

"Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me

Love CB? Upgrade to premium today!
Reply With Quote
Old November 6th, 2009, 03:04 PM

 
Join Date: Sep 2008
Location: Montréal
Posts: 39
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Balanced Phases?

i had just read somewhere that electricity distributor did not care as much as (...as much as!...) before about balanced phases.. I may have not well said what I meant on this point, but it was actually far to be my question. Am i wrong or right, this is not what I need to know now..
Reply With Quote
Old November 6th, 2009, 03:11 PM

 
Join Date: Sep 2008
Location: Montréal
Posts: 39
Thanks: 1
Thanked 0 Times in 0 Posts
Default Re: Balanced Phases?

Quote:
Originally Posted by icewolf08 View Post
As far as I know there are no systems that automatically balance loads on phases. When a building is built the electrical contractors have to design the systems so that during normal operation the phases stay as close to balanced as possible. This means that they need to calculate the average loads of all the electrical systems including HVAC, dimmers, wall outlets, room lighting, etc. and then distribute accordingly.

Generally (not always) permanent installed dimmers are wired such that each dimmer module alternates phases. As most current installed racks have two dimmers on each module, you have two dimmers alternating. So, dimmers 1&2 would be phase A, 3&4 B, 5&6 C, 7&8 A and so on. This allows for the "arbitrary" loading that occurs when you hang and circuit a show.

On the other hand, touring and portable racks are often just divided into thirds. In a 48 channel rack, dimmers 1-16 would be phase A, 17-32 B, and 33-48 C. This is when you have to pay attention to how you load up your rack. Generally in this situation, you would look at the loads that are on each circuit and then patch them into the rack to make as close to a balanced system as possible. You have to consider that when balancing a dimming system, not all the lights will be on at full at the same time. Thus, the farther out of balance you start at, the more potential there is to be way out of balance when you start running the show.

I can't speak to use of generators as I don't work with them all to often. Just know that when using a generator it can be even more important to have as close to a balanced load as you can.

thanks Icewolf for this.. Actually, i did know how phases were working.. but I was mostly trying to know what could happen if the phases were not well balanced... I know it can become a problem when using a generator somewhere, but if it isn't the case, why this HAS to be done. Where in the whole circuit, it becomes a problem. let's say again, in an extreme situation, i do have a phases lower than the two others, and then my neutral got 60 amps going through it.. why would it become a problem for me?

Byt the way, it never happened to me.. I always balance my phases as much as I can.. This is just a question up here.
Reply With Quote
Old November 6th, 2009, 03:23 PM
icewolf08's Avatar
CBmod
 Premium Member 
 
Join Date: Jan 2007
Location: Salt Lake City, UT
Posts: 3,103
Thanks: 21
Thanked 150 Times in 134 Posts
Send a message via AIM to icewolf08 Send a message via MSN to icewolf08 Send a message via Yahoo to icewolf08 Send a message via Skype™ to icewolf08
Default Re: Balanced Phases?

I have to say, I am with McCready00 here. This forum is about asking questions and getting answers. As he has stated, this is a hypothetical situation and he wants to know why it is bad. There doesn't have to be a real situation behind every question, there doesn't even have to be a class assignment either. Also, so far as I can tell, the question does not violate the CB TOS. he is not asking for wiring advice, or how-tos, just why things are the way they are. This forum is here so that people can ask questions that they want to know the answers to. I don't see why everyone who has answered here has given him a hard time.
__________________
Alex Weisman
Master Electrician - Pioneer Theatre Company
IceWolf Photography
[email address]

Soup or art?

"Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me

Love CB? Upgrade to premium today!

Last edited by icewolf08; November 6th, 2009 at 03:36 PM..
Reply With Quote
Old November 6th, 2009, 03:36 PM
mrb mrb is offline

 
Join Date: Dec 2008
Posts: 226
Thanks: 0
Thanked 6 Times in 6 Posts
Default Re: Balanced Phases?

Quote:
Originally Posted by icewolf08 View Post
I have to say, I am with McCready00 here. This forum is about asking questions and getting answers. As he has stated, this is a hypothetical situation and he wants to know why it is bad. There doesn't have to be a real situation behind every question, there doesn't even have to be a class assignment either. This forum is here so that people can ask questions that they want to know the answers to. I don't see why everyone who has answered here has given him a hard time.
I agree with you 100%. The way the question was written is what triggered the responses. If the question had been along the lines of "i have some theoretical questions about phase balancing, can you guys please help me understand this?" he would have received the help he was looking for.

The way the question was posed, there appeared to be an actual situation the OP was seeking assistance with. This combined with mention of "most buildings have systems to automatically balance the phase (this pretty much does not exist), and questioning 75 amps of neutral current on a 2/0 feeder led to the responses received.

In an attempt to help the OP, here are some issues with severe unbalance:
-voltage drop as one phase becomes fully loaded
-harmonics increase with unbalance
-3ph transformers like to see a balanced load
-as i mentioned before, an unbalanced load of x% (i forget what it is, there may be some documentation from gen mfgr which has more info) of a generator's total capacity can be a problem especially on smaller generators.

I am talking about extreme situations here, ex a 400a 3ph supply with 380 amps on one leg and 20 on the other two. For the most part, if you make an effort to keep things evenly balanced across phases you should be in good shape.
Reply With Quote
Old November 6th, 2009, 04:37 PM
MNicolai's Avatar
 Premium Member 

 
Join Date: Mar 2008
Location: Oconomowoc, WI
Posts: 488
Thanks: 26
Thanked 23 Times in 22 Posts
Default Re: Balanced Phases?

Quote:
Originally Posted by McCready00 View Post
i don't know what kind of extreme situation you are usually working in, but having 380amps on one leg and 20 on the two other... with a 400a 3ph supply.. this is not only extreme, but crazy...
For transformers, the efficiency at which they step-down the voltage and provide current to devices drops significantly when phases are out of balance. A single-phase example would be in a residential application. There are typically three wires coming in the main panel from the service; Phase A, Phase B, and a Neutral.

Phase A and B, relative to Neutral, are both 120v. Relative to each other, they are 240v. (That is strictly in this example and is not necessarily the case in other countries or other wire arrangements out of transformers)

If Phase A and Phase B are loaded to 60A, the Neutral wire out of that panel sees zero current. In this sense, they are balanced. However, if Phase A is loaded at 20A and Phase B is loaded at 50A, the Neutral wire will pick up the imbalance between the two. Now, the Neutral is a current-carrying conductor with 30A of current running through it.

(FYI, I am not speaking in terms of generators because my expertise is not with them.)

In entertainment industry applications, the neutral wire can often pass a lot more current through it than it should. Let's face it, when people are patching their light plot, they may be somewhat concerned about how many they have on each phase, but when it comes to show time, they simply aren't concerned about how many lights are on in a given cue on Phase A, or Phase B, or Phase C. I've worked in one space where they were limited in their power needs, and I did have to worry about imbalances, but typically it is not the factor that decides which lights are turned on in a given cue, or not turned on.

For this matter, it is widely-accepted that in theatre, Neutral wires see a lot more current than they do in motor applications, as motor loads tend to be quite balanced, whereas lighting applications minute-to-minute can create large imbalances in a system. To solve this, Neutral wires on phase-controlled dimming systems are considered current-carrying conductors. That means they are appropriately up-sized to accommodate such large imbalances. Also, it is common for transformers to be installed that are able to handle such imbalances better. Often this is a K-rated transformer. They are designed such that non-linear loads like that in theatre that create excess current running through the Neutral do not bring a transformer to an early demise.

(see http://www.centralyacht.com/library/...ransformer.pdf)

Also, the up-sized conductors for the Neutral allow more current to go through them without heating up to a destructive temperature. This is also why on 400A/3p company switches, there are 2 Neutrals. They are connected together on the same paths of conductivity on either end of the conductor run such that they act as one, really large conductor. That means a large imbalance can go through them without melting the insulation down and starting on fire, because now the heat and current are spread across the copper for both Neutral runs.

I strongly advise you check out that PDF on K-rated transformers; it should help shine some light on the problems with non-linear loads that leave phases out of balance with each other.

Here is another PDF that describes out-of-phase loads as they relate to the Entertainment Industry. Also check this out (http://www.saunderselectric.com/PDFs...-harmonics.pdf)
__________________
Mike Nicolai
Oconomowoc, WI, USA
mike skims his id on twitter
mike talks about things that matter to him on tumblr

Last edited by derekleffew; November 6th, 2009 at 07:04 PM..
Reply With Quote
Old November 6th, 2009, 05:50 PM

 
Join Date: Jun 2009
Location: Salisbury,MD
Posts: 303
Thanks: 2
Thanked 8 Times in 8 Posts
Default Re: Balanced Phases?

As things get out of balanced it creates the wire to heat and kicks breakers. I had a lighting contractor that used to have a small system that we would tie into a 225 amp breaker, his system PD had a 100 amp main. He would pop the 225 before his 100 because of the imbalance.
__________________
Michael S. Taylor
Reply With Quote
Old November 6th, 2009, 06:28 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,535
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Balanced Phases?

Can we please concentrate on the original question?
Quote:
Originally Posted by McCready00 View Post
...do we still have to follow the 10% max unbalanced law? ...
I've never heard of any such law, and in fact try to adhere to a "rule of thumb" that the highest phase be no more than 25% above the lowest phase. The reason, with no basis in fact or support that I've found, is that a 3Ø breaker can trip at a substantially lower current than its rating, due to a huge imbalance. I have no idea where I learned that, and it may well be utter garbage.

Must every question of this type end with STEVETERRY? What did we do before he joined Control Booth? I wasn't here, but you get my drift...
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
Reply

Tags
balanced, phases

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Loudspeakers - Converting unbalanced RCA to Balanced XLR skienblack Sound 10 October 30th, 2009 10:42 AM
Balanced and Unbalanced mbenonis Sound 3 May 8th, 2009 10:38 AM
Balanced Line DaveySimps Glossary A-E 0 February 1st, 2009 11:09 AM
Had an interesting thing happen the other day... tenor_singer Sound 19 May 26th, 2006 11:58 PM