Old October 27th, 2005, 09:32 PM

Assistant TD
 
Join Date: Aug 2004
Location: Stamford, CT
Posts: 341
Thanks: 0
Thanked 0 Times in 0 Posts
Send a message via AIM to JP12687
Default VOLTAGE HELP ASAP

as stated previously i am renting a 24x2.4k dimmer rack and hooking it up to a generator, the question is, what is the voltage on the dimmers? Can it operate at 120? 240? or what is the range?

I need help ASAP.

Josh
__________________
Josh Perlman
Event Manager
Scharff Weisberg
Reply With Quote
Sponsored Links
  #2 (permalink)  
Old October 27th, 2005, 09:54 PM
Radman's Avatar
CB Supporter 

Technical Director
 
Join Date: Apr 2004
Location: The Woodlands, TX
Posts: 1,277
Thanks: 9
Thanked 5 Times in 4 Posts
Send a message via AIM to Radman Send a message via MSN to Radman
Default

They should operate at close to 115 volts phase to neutral, three phases. There's a little bubble though, anywhere 110-120 should be fine I think.
__________________
"We can rebuild him, we have the technology, but I don't want to spend a lot of money."
Reply With Quote
  #3 (permalink)  
Old October 27th, 2005, 10:24 PM

Assistant TD
 
Join Date: Aug 2004
Location: Stamford, CT
Posts: 341
Thanks: 0
Thanked 0 Times in 0 Posts
Send a message via AIM to JP12687
Default

**** the generator they wanted to give me was a 208v. hm can anyone confirm rads comment. or tell me if they come at higher voltages
__________________
Josh Perlman
Event Manager
Scharff Weisberg
Reply With Quote
  #4 (permalink)  
Old October 27th, 2005, 10:47 PM

Technical Director
 
Join Date: Mar 2005
Posts: 593
Thanks: 2
Thanked 3 Times in 3 Posts
Send a message via AIM to koncept Send a message via MSN to koncept Send a message via Yahoo to koncept
Default

it depends upon the dimmers. there are both 110-120ish dimmers and 208 - 220ish dimmers in the 2.4 kw size. you should ask the rental company. the generator will probaly need 3 legs plus neutral n ground. Make sure it can handle the amps.
Reply With Quote
  #5 (permalink)  
Old October 27th, 2005, 10:50 PM

Techie
 
Join Date: Oct 2005
Location: Berkeley, Ca
Posts: 189
Thanks: 0
Thanked 9 Times in 7 Posts
Send a message via AIM to jbeutt Send a message via MSN to jbeutt
Default

i'm sure if it's a large enough rental house, they'll be able to supply a 120v.
Reply With Quote
Sponsored Links
  #6 (permalink)  
Old October 27th, 2005, 10:56 PM
Asst. Webmaster
Wireless Freak

Technical Director
 
Join Date: Sep 2003
Location: Charlottesville, VA
Posts: 951
Thanks: 8
Thanked 38 Times in 25 Posts
Send a message via AIM to mbenonis
Default

You say 208V, but what is that referenced to? Remember that voltage is not an absolute value, it is always compared to something. You also don't mention what kind of power the dimmer pack requires. For instance, the dimmer packs I used in high school required three phase/five wire 120/208V power.

As far as that "208V" generator - my guess is that the 208V you specify is between hots - that is, the generator generates three phases of AC, each of which measure a voltage of 120V to ground and 208V from hot to hot. Chances are, it will work fine for you, as long as it provides outlets that are 120V to ground, as well as 208V hot-to-hot.

If there is any doubt, ask the rental house to tell you exactly what kind of power the dimmer pack requires, and what kind of power the generator provides. If they don't match, tell them to get you something that does match.
__________________
Mike Benonis
Electrical Engineering '09
Sound Engineer - Department of Drama
University of Virginia
KI4RIX
Reply With Quote
  #7 (permalink)  
Old October 27th, 2005, 11:29 PM
Radman's Avatar
CB Supporter 

Technical Director
 
Join Date: Apr 2004
Location: The Woodlands, TX
Posts: 1,277
Thanks: 9
Thanked 5 Times in 4 Posts
Send a message via AIM to Radman Send a message via MSN to Radman
Default

Sorry about the confusion. I should have mentioned that it is 120 phase to neutral, as well as 208 phase to phase.
__________________
"We can rebuild him, we have the technology, but I don't want to spend a lot of money."
Reply With Quote
  #8 (permalink)  
Old October 29th, 2005, 12:12 PM

Junior Techie
 
Join Date: Oct 2004
Location: Lindenhurst, IL
Posts: 37
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Like others have stated, the specification on the Genny is phase-phase... so 208v would be correct.

I have run sensor racks from 110v to 126 volts without issue.
__________________
Wholehog II and III, GrandMA, Avolites, ETC, etc etc programmer. Also do Wysiwyg pre-viz Vision pre-viz. On or off-site

[url]www.SandalsDesign.com[/url]
Reply With Quote
  #9 (permalink)  
Old October 29th, 2005, 08:57 PM

Techie
 
Join Date: Dec 2003
Location: Illinois
Posts: 52
Thanks: 0
Thanked 0 Times in 0 Posts
Send a message via AIM to drumbum
Default

OK, the reason they told you it was a 208 dimmer rack is beacuse its 3 phase . . which means that your rack needs 3 hots, 1 ground and one neutral to opporate properly. Once hooked up PROPERLY, you should have 120* going through your dimmers. Which means that you can use 120 fixtures on it. The only time that you should ever use 208/220 fixtures is when you are wither outside of this country . . . using equipment manufactured for outside of this country, or specialised equipment designed for 208/220. A great example is intelligent lighting, most fixtures can be switched from 120 to 208 with a jumper inside.
Reply With Quote
  #10 (permalink)  
Old October 30th, 2005, 01:30 AM
Senior Team
CB Supporter 

Technical Director
 
Join Date: Mar 2003
Location: Illinois
Posts: 3,950
Thanks: 2
Thanked 64 Times in 52 Posts
Default

Smaller dimmer racks often have the option of switcing between single phase three wire (120/240v) and Three Phase (120/208v) power supplies. Dependant upon what type and size of generator you have available you can also at times have the rental company adjust the dimmer pack for what type of power you have.
Reply With Quote
Reply

Tags
asap, voltage

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
AC or DC....that is the question propmonkey Lighting 34 November 28th, 2006 01:23 PM
Longer life BTR? fosstech Lighting 4 October 27th, 2005 02:24 AM
Dimming mercury lamps... mixsa Lighting 1 October 13th, 2005 01:19 AM
Battery powered fixtures, take two Dark Lighting 8 June 5th, 2004 10:20 PM


All times are UTC -4. The time now is 03:42 AM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0
Powered by NuWiki v1.3 RC1 Copyright ©2006-2007, NuHit, LLC
Advertisement System V2.5 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54