Default Twistlock conversion

I managed to get my old school's theatre to donate their unused borderlights to my high school's theatre. They're old Strand/Century R40 strips, 4 circuit, 6 feet long, 12 lamps. We got 12 of them, plus an equivalent Altman strip for a total of 13. Anyways, here's the problem. Their theatre has twistlock connector strips, and we have parallel blade (Edison). There's something like 104 connectors total on these things (with the outputs for daisy-chaining), and I'm certainly not going to change all of these things, nor will the school want to pay for 104 plugs at $4 a piece. Since we'll only be plugging one in to each strip, and then daisy-chaining the other three off the first one, would you just replace the plugs on that one end unit with Edison plugs, or would you just leave them all as is and use adapters? There are advantages and disadvantages to each approach. Adapters are more expensive, but not too much more expensive. They offer greater flexibility in the long run, since they can be used on any fixture. Hard wired plugs are cheaper, but the flexibility is limited because that one must be plugged into the strip.

Any thoughts before I start hanging these things?
__________________
Dale Skyllingstad
[size=1]BFA Theatrical Production Arts
Technology Concentration
Class of 2010
Ithaca College
Ithaca, NY[/size]
Reply With Quote
Old April 24th, 2006, 12:38 PM
Mayhem's Avatar
Senior Team
 
Join Date: Jan 2004
Location: Australia
Posts: 1,843
Thanks: 0
Thanked 4 Times in 4 Posts
Default Re: Twistlock conversion

Well I think that based on what you have just said that adaptors would be the sensible thing to use and provide you with the flexibility that you want.
__________________
You are not the messiah wolf, you're just a very naughty boy.
Reply With Quote
Old April 24th, 2006, 12:38 PM
CBmod
 Premium Member 
 
Join Date: Jul 2005
Location: Sydney, Australia
Posts: 1,799
Thanks: 13
Thanked 37 Times in 33 Posts
Default Re: Twistlock conversion

I am guessing that an adaptor would mean that if they got hung and you went to plug them in that it would not matter which one was where. Same idea if they are used in a different application. Though they would be one more thing that could fail. So I guess it depends on what you think would work best in your situation.
Reply With Quote
Old April 24th, 2006, 07:15 PM

 
Join Date: Jul 2005
Posts: 385
Thanks: 1
Thanked 0 Times in 0 Posts
Send a message via AIM to kingfisher1
Default Re: Twistlock conversion

i'd go with the adapter, for flexibility, and also you'll be able to use it for any other conversions, and just out of curiosity, how much of a price gap are we talking here?
__________________
Ian Heller
Technical theater is just like sailing, except for the wind
Reply With Quote
Old April 24th, 2006, 08:33 PM

 
Join Date: Mar 2005
Posts: 593
Thanks: 2
Thanked 3 Times in 3 Posts
Send a message via AIM to koncept Send a message via MSN to koncept Send a message via Yahoo to koncept
Default Re: Twistlock conversion

i would go with adapter, and then down the road maybe do an upgrade on a few of the fixtures as needed. adapters are nice because htey can be used for many different things later on.
Reply With Quote
Old April 25th, 2006, 12:14 AM

 
Join Date: Aug 2005
Location: Kilmarnock, VA
Posts: 1,069
Thanks: 41
Thanked 41 Times in 39 Posts
Default Re: Twistlock conversion

I'll disagree, adapters are simply a waste of money for your application. Border lights are rarely moved once hung. Just change out the male ends on one unit for each rail and you're good to go for under $ 60.00 (5 rails.)

Should you find use for one of your spares in new locations in the future it is still only $ 12.00 to convert another one. Each adapter will cost you around $ 15.00 due to the cost of the twist lock connectors, so for the cost of adapters for only one fixture you could convert 4 to edisons.
__________________
Thanks,
Bill - ESC
Entertainment Systems Corporation
Innovative production assistance since 1973
Sales - Rentals - Design - Consulting
800-582-2421 - bill@entsyscorp.com
Reply With Quote
Old April 25th, 2006, 01:10 AM

 
Join Date: Jun 2004
Location: Tacoma, WA USA
Posts: 194
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Twistlock conversion

Thanks for all the opinions. After coming back to them today, I remembered that some of them are missing plugs. The theatre that owned them knew they weren't going to use them anymore, so they canabalized some of the plugs for some of the new instruments they were buying. So there were a couple with no plugs on the male end at all. Those are going to be the ones that receive the new edison plugs. Some others are missing twistlocks as well, so we're just going to replace them with more twistlocks so they can chain together.

I also just had a random thought about these units...has anyone tried using them on their ends mounted to some type of vertical pipe for dance sidelight? Given they're 6 feet tall they're the perfect height for 95% of all the dancers out there, and they can change colors without scrollers . The only problem I see is pattern control and intensity. But for gentle toning they may work.
__________________
Dale Skyllingstad
[size=1]BFA Theatrical Production Arts
Technology Concentration
Class of 2010
Ithaca College
Ithaca, NY[/size]
Reply With Quote
Old April 25th, 2006, 03:47 AM
Senior Team
 Premium Member 
 
Join Date: Mar 2003
Location: Illinois
Posts: 4,419
Thanks: 5
Thanked 81 Times in 66 Posts
Default Re: Twistlock conversion

Should work interesting for vertical walls of light.

Wondeing what the total wattage of the fixtures is verses that of your parallel blade (15A) Edison plugs.

Given a single 3-circuit strip with 150w lamps would have 600w per circuit load on them, the Edison plug (adaptor or not) would only allow for three strips per circuit before you have an unsafe condition at the school.

It's probably twist lock in also being rated for 20 amps or four strips per bar.

Can't say not to change or adapt, but were possible, leave what is 20 AMP rated alone in making it difficult to just simply plug in a bunch of them. Perhaps even tag the adapted to Edison fixture at it's plug that only a maximum of three strips can or should be installed on this strip of them at a time. This would look out for future tech people that inherit your good ideas what ever the end result.

Also having a qualified service tech come out to visit them might be a good idea. Just installing plugs on or using obsolete gear from someone else is normally a bad idea short of good detailed inspection.
Reply With Quote
Old April 25th, 2006, 08:49 AM

 
Join Date: Mar 2005
Posts: 593
Thanks: 2
Thanked 3 Times in 3 Posts
Send a message via AIM to koncept Send a message via MSN to koncept Send a message via Yahoo to koncept
Default Re: Twistlock conversion

that is an interesting idea for dance concerts. we have these boom poles that we could probaly mount them on but we normaly use two 6x12's per pole i think.
Reply With Quote
Old April 25th, 2006, 12:12 PM

 
Join Date: Jun 2004
Location: Tacoma, WA USA
Posts: 194
Thanks: 0
Thanked 1 Time in 1 Post
Default Re: Twistlock conversion

Quote:
Originally Posted by ship
Should work interesting for vertical walls of light.

Wondeing what the total wattage of the fixtures is verses that of your parallel blade (15A) Edison plugs.

Given a single 3-circuit strip with 150w lamps would have 600w per circuit load on them, the Edison plug (adaptor or not) would only allow for three strips per circuit before you have an unsafe condition at the school.

It's probably twist lock in also being rated for 20 amps or four strips per bar.

Can't say not to change or adapt, but were possible, leave what is 20 AMP rated alone in making it difficult to just simply plug in a bunch of them. Perhaps even tag the adapted to Edison fixture at it's plug that only a maximum of three strips can or should be installed on this strip of them at a time. This would look out for future tech people that inherit your good ideas what ever the end result.

Also having a qualified service tech come out to visit them might be a good idea. Just installing plugs on or using obsolete gear from someone else is normally a bad idea short of good detailed inspection.
Didn't really give much thought to that, but thanks. We're using 120w 120V R40 lamps (conveniently 1A each ), so with the four circuit models we got (3 banks of four colors), we're only getting 12A per circuit with four units, which is still under the plug's rating. What I would then do if we were going to do more than 15A is get a 5-20P plug like this, since our connector strips are wired and dimmered for 20A.



I'll try that dance light concept once we get all of them up and running, which should be before not too long.
__________________
Dale Skyllingstad
[size=1]BFA Theatrical Production Arts
Technology Concentration
Class of 2010
Ithaca College
Ithaca, NY[/size]
Reply With Quote
Reply

Tags
conversion, twistlock

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mole Light Conversion Project ship Lighting 10 January 8th, 2009 11:15 PM
Gel Conversion Charts ship Lighting 2 December 26th, 2004 06:12 PM
Conversion from Standard Platform to Stress Skins. wemeck Scenery 1 October 3rd, 2003 01:47 AM