Default Watts/Amps from outlet?

So correct me if I'm wrong here. I believe I read on here that you can draw a maximum of 15 amps / around 1000 watts from a standard Edison outlet. My question is simple (and sorry for so many questions guys! I sense some of you would rather I stop asking so many.) when you mention "per outlet" is that for the singular outlet, or for the entire plate (standard 2 outlet plate). I'm not sure if I'm being clear, I'll try and rephrase if you don't get what I'm trying to ask.
Reply With Quote
Sponsored Links
  #2 (permalink)  
Old February 27th, 2007, 02:00 AM
gafftaper's Avatar
half wisdom and half-wit
CB Supporter 

Technical Director
 
Join Date: Jan 2006
Location: Seattle Washington
Posts: 4,855
Thanks: 36
Thanked 149 Times in 122 Posts
Default Re: Watts/Amps from outlet?

The circuit breakers are typically 15 (or sometimes 20 amps). This means the total draw of EVERY outlet on that circuit can not add up to more than that 15 amps at once. So outlet #1 Can draw 10 amps, outlet #2 o can draw 3 amps, but outlet #3 only has 2 amps left to use or the breaker will blow.

This can be a real problem in old houses (like mine). Back in the day people didn't have as many household electrical appliances. I had a problem at Christmas a few years back where if the Christmas tree, Stereo, and a few lights were on, the breaker would blow when the fridge kicked in. I have since added a few new circuits.
__________________
Community College Technical Director
If you have learned as much from CB as I have, donate now to keep CB alive for others to find and learn from.
Reply With Quote
  #3 (permalink)  
Old February 27th, 2007, 02:03 AM
Footer's Avatar
Senior Team

Technical Director
 
Join Date: Nov 2005
Location: Atlanta, GA
Posts: 2,614
Thanks: 1
Thanked 83 Times in 80 Posts
Default Re: Watts/Amps from outlet?

Its actually per circuit. Most standard house outlets are rated for 15 amps per complete outlet, ie only 15 amps can move in from the wires connected to the physical hardware. There are 20 amp rated outlets, they are the ones with one blade at a 90 deg angle. Theoretically, the breaker that supples power to the circuit is rated at the maximum allowable amperage of the cable and the hardware at the end of the cable. Sometimes this is not done in residential situations where they will put in a 20 amp breaker and cable to support 20 amps but put in 15 amp outlets saying that the 20 amps is spread over X # of outlets. From what I can recall this is against current code (but its how my current apt is wired...). When it comes to how a building is wired, very rarely do they put in 15 amp outlets, most industrial/school/what not situations are wired for 20 amp circuits. Go to the breaker box and see what the breakers are rated at, thats the maximum amount of power you can pull from that circuit. Also remember, that the power of one circuit can be spread over multiple outlets. There are cool little tools that can trace circuits to the breaker box and to other outlets, or you can do what most people do, the guess and check method. i.e. load up a circuit till it blows, then load up another cicurit till it blows. Does it work, yes, is it the best solution, no.
Reply With Quote
  #4 (permalink)  
Old February 27th, 2007, 02:04 AM
Footer's Avatar
Senior Team

Technical Director
 
Join Date: Nov 2005
Location: Atlanta, GA
Posts: 2,614
Thanks: 1
Thanked 83 Times in 80 Posts
Default Re: Watts/Amps from outlet?

Quote:
Originally Posted by gafftaper View Post
The circuit breakers are typically 15 (or sometimes 20 amps). This means the total draw of EVERY outlet on that circuit can not add up to more than that 15 amps at once. So outlet #1 Can draw 10 amps, outlet #2 o can draw 3 amps, but outlet #3 only has 2 amps left to use or the breaker will blow.
This can be a real problem in old houses (like mine). Back in the day people didn't have as many household electrical appliances. I had a problem at Christmas a few years back where if the Christmas tree, Stereo, and a few lights were on, the breaker would blow when the fridge kicked in. I have since added a few new circuits.
My apt is like that, if i have my PC, my TV, my DVR going, and my AC on, it blows. Its no fun to have to draft on a hot day.
Reply With Quote
  #5 (permalink)  
Old February 27th, 2007, 10:13 AM

Technical Director
 
Join Date: Nov 2003
Location: New York
Posts: 1,281
Thanks: 2
Thanked 8 Times in 8 Posts
Send a message via AIM to zac850
Default Re: Watts/Amps from outlet?

The way it generally works is that you have 15 amps running out of one beaker for a normal household edison outlet.

From this point on, all it matters is how that circuit is wired. Some houses all the outlets in one room are on one circuit breaker. Other places, especially kitchens and other places where they expect large loads to be plugged in, every outlet is a different circuit breaker.

In one of my old theater spaces we had a breaker wired to several wall outlets. This was specially wired up for us to use some shoebox dimmers. In this case, each outlet was wired to a different circuit, in some cases there were two circuits in each outlet box.

There are really only two ways to find out. First would be to dig up the electrical plans of the building. Second would be to go and flip on and off the breakers, and see which outlets stop working. (make sure not to flip off anything important)
__________________
http://www.zacphotos.com
Reply With Quote
Sponsored Links
  #6 (permalink)  
Old February 27th, 2007, 11:23 AM
Foxinabox10's Avatar

Technical Director
 
Join Date: May 2004
Location: Audubon, PA
Posts: 819
Thanks: 3
Thanked 1 Time in 1 Post
Send a message via AIM to Foxinabox10
Default Re: Watts/Amps from outlet?

Although it is necessary to have the blade turned 90 degrees to pull 20 amps on one cable, most places do not have the blade turned when the breaker is 20 amps. In general, most commercial buildings and schools run only 20 amp circuits.
__________________
Foxinabox10
[I]Formerly[/I]
Lighting Operator, Lighting Designer, Technical Director, President
Methacton High School Theatre Co.
Reply With Quote
  #7 (permalink)  
Old February 27th, 2007, 12:16 PM

Technical Director
 
Join Date: Aug 2005
Location: Kilmarnock, VA
Posts: 672
Thanks: 20
Thanked 15 Times in 14 Posts
Default Re: Watts/Amps from outlet?

To clear up one misstatement, a 15 amp outlet (or circuit) will supply 1800w of power. The formula is Amps X Volts = Wattage.

15 X 120 = 1800
__________________
Thanks,
Bill - ESC
Entertainment Systems Corporation
Innovative production assistance since 1973
Sales - Rentals - Design - Consulting
800-582-2421 - bill@entsyscorp.com
Reply With Quote
  #8 (permalink)  
Old February 27th, 2007, 12:24 PM

Junior Techie
 
Join Date: Feb 2007
Location: Michigan
Posts: 45
Thanks: 0
Thanked 3 Times in 3 Posts
Default Re: Watts/Amps from outlet?

I've toured for a number of years with different organizations (often performing in churches/schools). We'd travel with all our own sound, lighting, and spotlight. For each set-up we'd need 5-8 different circuts for our set-up. It can take a LONG time to just guess.

I def. recommend getting a circuit tracker. Spend 30-60 bucks and you're good to go. of course, you'll have to test the breaker to double check that the tracker was right, but most of them are fairly accurate.
Reply With Quote
  #9 (permalink)  
Old February 27th, 2007, 06:01 PM
Van's Avatar
Van Van is online now
CB Supporter 

Technical Director
 
Join Date: Jul 2006
Location: Portland, Or.
Posts: 3,098
Thanks: 37
Thanked 109 Times in 105 Posts
Default Re: Watts/Amps from outlet?

Quote:
Originally Posted by BillESC View Post
To clear up one misstatement, a 15 amp outlet (or circuit) will supply 1800w of power. The formula is Amps X Volts = Wattage.

15 X 120 = 1800

15 x 110 = 1650

15 x 115 = 1725

As supply voltages can vary according to a number of different factors.
Always check your voltage prior to guessing how many watts you can load a breaker with. Always use a 10% rule, that is, load a breaker only to within 10% of it's maximum allowable. Sometimes breakers get "weak" and will shut down below thier rated amprerage.
__________________
Van J. McQueen
Technical Director
Artists Repertory Theatre

Remember:
If you light a man a fire,
you warm him for the night.
If you light a man ON fire,
You warm him for the rest of his life.
Reply With Quote
  #10 (permalink)  
Old February 27th, 2007, 07:38 PM

Junior Techie
 
Join Date: Aug 2006
Posts: 10
Thanks: 3
Thanked 0 Times in 0 Posts
Default Re: Watts/Amps from outlet?

If you want to go a step further, the National Electrical Code allows one to load a circuit up to 80% of the circuit rating for a permanently connected load. Although what we do is never really permanent, the reliability of our operation is certainly enhanced by following the 80% rule.
The configuration of the outlet may or may not have any relationship to the circuit rating. If I connect a duplex NEMA 5-15 receptacle (the normal edison receptacle) to a 20 amp circuit it is acceptable. If I am going to connect a single receptacle (not duplex) as the only receptacle on the circuit, and it is a 20 Amp circuit, then the NEMA 5-20 recptacle (the receptacle with the blade turned at right angles) is required. One may always use a higher rated device with a lower rated circuit, but the opposite is not true if there is only one device on the circuit. If you are going to be dealing with a variety of different circuit ratings then you should get a copy of a NEMA ratings chart to be sure you are using the correct plugs and receptacles since there is a different device for every different circuit configuration.
Oldman
Reply With Quote
Reply

Tags
outlet, watts or amps

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Three phase power and distribution beam_1973 Lighting 41 September 7th, 2006 12:03 PM
NSI dimmer pack question JahJahwarrior Lighting 18 July 22nd, 2004 12:40 PM
Installation of a stage pin plug on a cable, plus history ship Lighting 15 March 3rd, 2004 02:01 AM


All times are UTC -4. The time now is 06:39 PM.


Powered by vBulletin® Version 3.7.4
Copyright ©2000 - 2008, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.2.0
Powered by NuWiki v1.3 RC1 Copyright ©2006-2007, NuHit, LLC
Advertisement System V2.5 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54