I haven't posted here in a while, and now I have a very strange question. At the theatre at my university, they used to have a couple different lighting systems that worked together in the theatre. One was an ATD system of some sort, and the other was a Kliegpac. Around 1996 I think they got a new system (ETC Express console and whatnot), but they kept the Kliegpac because they thought they might use it in some other space at some point. Well, that didn't happen, so now it's sitting around, unused, and they don't really want to keep it. It looks to be complete as far as I know; it's got the controller and the dimmer (main) unit. I don't remember if the cable to go from the controller to the dimmer pack is there, but I'm sure I could come up with that. Here's my question:
Bear in mind, I know nothing about how this thing was hooked up, in terms of voltage, pinout, etc. Would it be possible (though some modification perhaps) to wire the unit so that it could be used with standard 120v current? I doubt that's what it's set up for now, but I could be mistaken. Basically I would use it as my own "mini" unit for the four Kliegl ERS fixtures I got from the same theatre. I realize I probably couldn't use the full dimming capabilites as there wouldn't be ample power, but I only have these four instruments which can only take a maximum 750 watt lamp. I also realize that means I would be drawing 25 amps at full power on every instrument. So, my idea then is to modify the Kliegpac such that it could be taken to some location, plugged into two separate circuits (so that it would get a maximum of 30-35 amps allowed), and used to dim at least these four instruments. Is this in any way possible, or am I totally crazy? I do know how to work with electricity (I'm not an electrician, but I have worked on electronics and done wiring, etc.). Basically I'm not looking for the Kliegpac to take, say, a 220 source and break it down into several 120V dimmers, I'm just looking to use it as a portable (heavy) dimmer unit. Any ideas as to whether or not this is possible? -Dan |
| Sponsored Links |
|
|||
|
Thanks for the info.
I checked around, and found the Kliegpac 9 Manual on the klieglbros.com website here. It seems to imply that the Kliegpac can be run off of 3 phase or single phase power if I understand correctly. I realize that I can't use the full potential of the dimming system using only 20A circuits, but it seems from the looks of this that I could possibly connect it using two separate 20A circuits, though again phase could be an issue (though it does seem that it has separate transformers judging by the way the connections change). However, I am not well versed in how this would work out. Any ideas? -Dan |
|
|||
|
Quote:
Please, do not attempt this yourself. ST |
| Sponsored Links |
|
||||
|
We really can't give electrical advice (or advice on rigging, scaffolding, ect) on this forum due to the liability issue. I can at least give you an "idea" of your chance of success when taking the unit to a qualified technician or shop:
The fact that the owners manual shows that you can reassigned channels to different phase legs is a good sign that each has it's own ramp generator. The fact that there is multiple neutral terminals also is a good sign. Here is the pitfall to watch out for. When you are operating dimmers off of standard wall outlets, the neutrals can have no interconnection! For instance, if channel 1 is on one plug and channel 2 is on another, the neutral for channel 1 needs to return to the same plug as the hot came from. Most dimmers have a buss jumper between the neutral terminals. This produces a fire hazard if you are plugging it in multiple wall outlets. Although each outlet is protected by a 15 or 20 amp circuit breaker, only the "hot" wire is protected. Here's an example of trouble: You happen to plug your channels into two outlets that are on different circuits but on the same phase leg. Unknown to you, there is a defective or dirty plug that interrupts the neutral connection on one of your plugs. Everything seams to work correctly BUT you are unknowingly sending 40 amps back through one 12 gauge wire through one prong on a 20 amp plug!
__________________
John Dziel DAE Concert Lighting founded 1971 Intelligent Lighting Solutions "Oh, that switch also fed the Hotel ?" |
|
|||
|
Thanks JD, I certainly understand about not giving direct advice. I do have a question about what you just said though: you say that dimmers have a buss jumper between the neutrals. So that means that in a normal dimming system, the neutral is common to all the circuits no matter what phase they are connected to. That makes sense in a polyphase system from what I understand. What I don't understand is what exactly you mean about the fire hazard. Are you saying that if the neutrals of the dimmers were still connected together and the dimmers were run off separate outlets I could have a fire hazard, or are you saying that BECAUSE they don't have a common neutral there is a fire hazard?
-Dan |
|
||||
|
Quote:
Another example of a "sneak" danger: You are in a building that has had many additions made. You could end up plugging into two outlets that come off of different service panels! (Worse case scenario I admit.) In this case, if there is a neutral imbalance between the panels, you could have hundreds of amps finding their way from one panel to another through your equipment without even turning on a single light!
__________________
John Dziel DAE Concert Lighting founded 1971 Intelligent Lighting Solutions "Oh, that switch also fed the Hotel ?" Last edited by JD; November 10th, 2007 at 03:40 PM.. Reason: more added |
|
||||
|
It looks like the moral of the story is put in a lighting museum or your garage until you have the knowledge to fix it properly.
Be aware also that modifying it would obliterate any regulatory approvals(UL,CE, etc..)
__________________
Philip LaDue EAA "The loudspeaker has more of an effect on the sound we hear than anything else in the audio reproduction chain"- Alan Frank Support Version 3.0 of ControlBooth.com by Donating |