I've had a question hanging around in the back of my head for quite a while...
My understanding of a clamp meter, is that you just take a cable, put the cable in between the jaws of the clamp and then it tells you the current going through the cable,and dependent upon how good the clamp meter is, it tells you the voltage etc. Is that right? The reason for all this confusion, is that we have a clamp meter at school, and when we clamp it around a cable, it doesn't work... and the rather ambiguous instructions don't say whether they refer to a complete cable, or just one conductor of that, as in a live wire... It might just be that our clamp meter is dodgy, but I thought I'd make sure, before I get one in the post christmas sales.. Thanks for your help!
__________________
Techies Do it in the Dark!! |
| Sponsored Links |
|
||||
|
First, the clamp meter must be used only around a single wire conductor, not around cable. Second, the clamp meter will only tell you amperage, not voltage, without physical contact using the included probes. Disclaimer: Always use every available precaution when working around live electrical circuits! Here's the one I use, Fluke 30--it's not the best, but adequate for my purposes. It has been replaced by the Fluke 333A, MSRP $149.95 US.
Sounds like yours is not a very good manual. Out of curiosity, what make and model is your meter? Here is a link to the manual for the Fluke 333. It will probably help clear up your confusion.
__________________
Better questions produce better answers! Last edited by derekleffew; December 24th, 2007 at 06:01 PM.. |
|
|||
|
Quote:
Or am I thinking of something else ?. Steve B. |
|
||||
|
I certainly hope you are mistaken, SteveB, as I've used my Fluke 30 to measure amperage loads on many touring dimmer racks and ML Distros, and never been challenged on the results. I think you may be confused on the measurement of output voltage of a given dimmer, for which you need a "true RMS" (Root Mean Square) meter.
__________________
Better questions produce better answers! |
|
|||
|
I'm not sure the make and model of ours, because it is at school, but I'll try and find out...
And if it can only be clamped around the live conductor, would I be right to suggest that in most applications it can't be much use? I guess if you had like a 3 phase system, with all the different phases on seperate inputs, then it would be ok... but as it can't be used for actual cables, for installed systems and such, it can't be used very effectivley? Thanks for the help.
__________________
Techies Do it in the Dark!! |
| Sponsored Links |
|
|||
|
Clamp meters do have practical limitations in getting to the single conductor which generally involves getting close to live wires, a clamp on meter loses accuracy on dimmed settings as the waveforms become too complex to analyze accurately and they do not read the dc content of the waveform, but they are near enough for all practical purposes.There are cheap rms meters on the market which are perfectly useful for the type of work we do.
__________________
David Ashton All Things Theatre Perth,Australia "for every complex problem there is a solution which is neat, simple,and wrong" H. L. Menken |
|
|||
|
Quote:
BTW, the clamp meter does not care if it's measuring the neutral or hot conductor--the current is the same in both for a single-phase circuit. For higher current feeder applications where you may be clamping around live conductors on equipment with the covers off, you are now under the rules of NFPA 70E "Standard for Electrical Safety in the Workplace" in North America. This defines the protective gear you must wear, and the various boundaries and voltages where different rules apply. DO NOT ATTEMPT THIS without training and expert help! Of course, this does not apply if you are clamping around insulated, single conductor feeder cables or branch circuit conductors outside equipment or switchgear. ST |
|
|||
|
Quote:
Thanks
__________________
Techies Do it in the Dark!! |
|
|||
|
Quote:
As further clarification, the typical clamp around amperage measuring meter - here's a photo of an Amp-Probe model, has a set of jaws that open to allow you to wrap the jaws around an insulated conductor, the jaws then close to create a loop around the conductor. There's usually a few inches of clearance between the conductors and the insulated jaws of the meter. Care and attention needs to be in place to do this measuring safely and Steve T. has listed a link as to the methods now required. As to usage. One typical example would be attempting to get a rough measurement of the normal load on an electrical panel that has space(s) for additional breakers, but whose existing loading is undetermined. Removing the panel cover and testing the hot legs, presumably while the loading is as close to maximum current usage, would then yield a reading. SB Last edited by SteveB; September 8th, 2008 at 04:36 PM.. |
|
|||
|
To Steve Terry
By the way - a Merry Christmas to all you folks at ETC !. A question arose as to whether a clamping amp-probe will accurately measure a dimmed load ?. Does the distorted sine-wave affect the readings ?. That's what I was told years ago and is why I stopped using my personal Amp-Probe to measure portable dimming systems. Steve B. |
![]() |
| Tags |
| clamp, meters |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| VU Meters | tomed101 | Sound | 11 | December 11th, 2007 11:38 AM |
| Seachangers and sidearms? | gafftapegreenia | Lighting | 21 | November 2nd, 2007 08:35 PM |
| Another clamp question... | JohnA | Lighting | 16 | October 9th, 2007 01:49 AM |
| 5 line trim clamp | rwolfe | New Member Board | 2 | February 21st, 2007 05:12 PM |
| standard insturment maitnenance | moojoe | General Advice | 13 | May 11th, 2005 11:31 AM |