Star Silly Power Question

Hi all,

I'm working on a show in an old venue. I have access to a 60A 240VAC event power plug (NEMA 18-60 Plug).

My desire is to bring in a few moving lights and wash units and supplement it with a small conventional package.

I was thinking I would build a custom distro for this. I was going to basically wire the first hot leg to Phase A on my dimmer pack and throw a 20A breaker on the end for half of my intelligents, and do the same with the second hot leg, for Phase C and the other half of my intelligents.

Right now, my current plot requires that my total intelligent light load is about 10A/120V on each breaker.
My total conventional light load is about 40A/120V on each phase.

My question is:

If I rent an ETC 12 x 2.4kw Sensor dimmer pack, which should really use 120A, will it still work given that my available power is less than that? Does it matter since I'm only loading each phase to 40A/120V, which is available, or will the pack not work at all without 120A?

Any responses, ideas, alternatives, or suggestions will be greatly appreciated.

Happy Holidays!

--liteman
Reply With Quote
Old December 27th, 2007, 10:20 AM
 Premium Member 

 
Join Date: Sep 2007
Location: perth W Australia
Posts: 511
Thanks: 13
Thanked 16 Times in 14 Posts
Default Re: Silly Power Question

The dimmer pack will only draw less than 100 watts, it is the load that you plug in and bring up that is the crucial factor.You can load up the dimmer but as long as you only bring up a balance of power at any time you can get away with it.The pack will work perfectly well.
__________________
David Ashton
All Things Theatre
Perth,Australia

"for every complex problem there is a solution which is neat, simple,and wrong"
H. L. Menken
Reply With Quote
The Following User Says Thank You to David Ashton For This Useful Post:
liteman (December 27th, 2007)
Old December 27th, 2007, 10:34 AM

 
Join Date: Dec 2007
Posts: 5
Thanks: 6
Thanked 0 Times in 0 Posts
Default Re: Silly Power Question

Excellent. That's just what I wanted to hear.
Thanks!

One more silly power question:
I know that most moving lights these days can run at 120V or 220V. When they run at 220V, are they running off of a single leg at 220V, or two legs of 110V?

My real question is, using the above event power, can I hookup my moving lights directly to the 240V interface? If so, how do both legs of power get into the moving light? Do I need special power cables?

Also, what's the safest way for me to get the cam cables for the Sensor Pack hooked up into my custom distro without me having to wire cams out of my distro?

Thanks again for all of your help and your (incredibly speedy!) responses.

--liteman
Reply With Quote
Old December 27th, 2007, 11:23 AM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,536
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Silly Power Question

liteman: STOP! If this is indeed the plug to which you are referring, it cannot safely be used for stage lighting, or anything else for that matter, as there's no electrical ground.

Secondly, you haven't told us what size the circuit breaker or fuses are supplying that receptacle, which is more important that the plug specifications.

Thirdly, your questions indicate that you don't have enough knowledge or experience to do what you're attempting without a Licensed Electrician.

Sorry to be blunt, but I don't want you or anyone else to be harmed.
allthingstheatre is only partially correct regarding underrating dimmer loading, and didn't pick up on the fact that you refer to a NEMA 18-60 as a 60A 240VAC device, when it is actually a 4wire, 3ø, 120/208VAC connector, with no ground.

Welcome to the Control Booth! We'll do our best to help you with any question, but we'll also tell you when we can't, for safety reasons.
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.
Reply With Quote
The Following User Says Thank You to derekleffew For This Useful Post:
liteman (December 27th, 2007)
Old December 27th, 2007, 11:35 AM
wolf825's Avatar
Senior Team
 
Join Date: Apr 2003
Location: Eastcoast USA
Posts: 997
Thanks: 0
Thanked 7 Times in 7 Posts
Default Re: Silly Power Question

Howdy liteman,
When it comes to electricity--the rule of "if you have to ask, you should not be doing it" applies.

Aside from not knowing how or what that 60a 'event plug' is wired (is it WYE power, is it delta power, what guage wire, how is the ground or neutral run, is it 'really' 60 amps or is that just cause the plug is rated for 60--it could be 100 or it could be 30--is it breakered or direct tie to a panel and what is THAT say, and is it single or 3 phase etc etc etc)--cause in electricity it is risky and dangerous to assume anything and there are many factors to consider for safety and proper use.


There is a liability restriction to questions that can be answered here on CB (most being for rigging and high voltage electrical wiring) for reasons of safety and liability because many of the participants on CB are learning students in HS and college. The Senior-Team Moderators & Controlbooth Owners, who are all experienced professionals, have drawn this line for its CB members so as not to permit posting of potentially dangerous or unsupervised 'DIY instructions' which may cause injury or harm to someone less experienced or just learning.... We do not wish to seem to play down the dangers and risks of doing certain rigging or electrical work. Reading a post on a web forum is not "formal training" or can cover completely all the safety aspects of any project... Supervision and proper training in certain aspects of live entertainment is required and a must before anyone should take on such a project. I am not saying you may not have some experience in electricity--I am simply saying that when in doubt always yeild to a professional electrician or rigger and consult them first.

Please consult a licensed electrician for your project and please be safe--we want our members to stay around. At the least, you could damage or destroy your equipment with improper wiring, and at the worse you could cause injury, death, electrocution and fire from mis-wiring or overloading...

-w
__________________
--Wolf
LD, ME, FOH, MON,A1/A2/L1/L2, MLRT, MLP...blah blah blah....

I will ALWAYS mess with my pal Mayhem!
Reply With Quote
The Following User Says Thank You to wolf825 For This Useful Post:
liteman (December 27th, 2007)
Old December 27th, 2007, 11:51 AM

 
Join Date: Dec 2007
Posts: 5
Thanks: 6
Thanked 0 Times in 0 Posts
Default Re: Silly Power Question

Thanks for your replies,

I apologize, I should have been more specific. I didn't assume that it was wired at 240V/60A because of the plug rating, it is clearly labeled on the disconnect that the plug is wired to.

In addition, each of the poles on the plug itself is labeled, as well. I've attached a picture of the plug that I took on the first site survey.

You're correct in picking up in my lack of knowledge about some of these things. I am really more of lighting designer, and usually let the production companies handle the setup, but this is for a small, non-profit organization, and I'm friends with the director, so it's a special circumstance. But I do have a fairly strong understanding of electricity and what is safe and what is not.

I would have never known that the Nema 18-60 is normally used as a 3-phase with no ground. i just assumed that it is normally used as it was wired in this situation, but clearly, the original electricians retrofitted it, into what seems like event power.

The top pole is labeled as neutral, left and right as the hot legs, and the bottom as ground.

Based on these labels, and the labels on the disconnect, I came to the conclusion that it was a single phase 240V/60A with two hot legs, a neutral, and a ground.

I certainly appreciate all of your concerns. I would never want anyone, including myself, to be harmed or put in danger by anything that had my hand in it, and I assure you that I will be the first person to step back if I even have an ounce a doubt in what I am doing.

I was a little weary about a few things that I had never had to deal with before, as I've always worked with an abundance of power and normally let others worry about power issues, which is why I came with my original question.

Again, thank you all for your responses, and your concerns - I appreciate them all.

-liteman
Attached Thumbnails
Silly Power Question-photo.jpg  
Reply With Quote
Old December 27th, 2007, 12:05 PM
jonhirsh's Avatar

 
Join Date: Dec 2004
Location: Toronto, Ontario and Valencia, California
Posts: 850
Thanks: 13
Thanked 15 Times in 13 Posts
Send a message via Yahoo to jonhirsh
Default Re: Silly Power Question

In that photo it looks like top, left, and right are labeled H for hot and the bottom G for ground. That is a type of three phase power. Are you positive that the top said neutral?
__________________
Jonathan Hirsh
Black Horse Productions
[url]www.JonathanHirsh.com[/url]
Reply With Quote
Old December 27th, 2007, 12:13 PM
derekleffew's Avatar
Senior Team
 Premium Member 
 
Join Date: Aug 2007
Location: Las Vegas, NV, USA
Posts: 3,536
Thanks: 98
Thanked 261 Times in 227 Posts
Blog Entries: 1
Default Re: Silly Power Question

Glad we didn't scare you away. I'll now address some of your questions, but I'd feel better if you had a more experienced electrician helping you.

The Sensor Pack, SP6, is normally set up for 3ø operation. It needs to be modified by its owner for single phase, GNHH, operation. I'm not positive, but I think dimmers 1-6 are on one leg and 7-12 are on the other, when used in single phase mode.

All of your intelligent lights are set to operate on 120V, correct?

You never told us the size of the fuses or breakers, or wire feeding the 60A receptacle. Measure the voltage on the receptacle to verify that the pencil labels are correct. Are you dealing with a venue maintenance person or some other building representative?

Another issue. If it is in fact a 60amp breaker protecting that outlet, you'll need to wire your plug with #6 or better #4 wire. Then find a set of E1016series-compatible Camlok-type connectors to mate with the Sensor pack. Those connectors wired with #4 or #6 wire are not a common item, in any company's rental stock. Plus the neutral MUST be oversized.

That's as much as I feel I can give you. Start a new thread in the New Member Board introducing yourself. We're lovable, but nosy. Tell us where you are and what you've done, and where you'd like to be and do. We like other's websites, and definitely post pictures of your benefit when it's done. We love pictures, there's a lengthy thread here.
__________________
"It's a shame there couldn't have been more LED fixtures at this year's LDI."
.

Last edited by derekleffew; December 27th, 2007 at 02:33 PM..
Reply With Quote
The Following User Says Thank You to derekleffew For This Useful Post:
liteman (December 27th, 2007)
Old December 27th, 2007, 12:24 PM
icewolf08's Avatar
CBmod
 Premium Member 
 
Join Date: Jan 2007
Location: Salt Lake City, UT
Posts: 3,103
Thanks: 21
Thanked 150 Times in 134 Posts
Send a message via AIM to icewolf08 Send a message via MSN to icewolf08 Send a message via Yahoo to icewolf08 Send a message via Skype™ to icewolf08
Default Re: Silly Power Question

If your Intellignet lights really only have a total load of 10A it would be a lot safter to just put them on a dimmer. I know that most intelligent gear doesn't like being on an SCR, so if you can spare two slots in your 12-pack you could put a CC-20 or R20 module in to feed the MLs constant power. In a pinch if you set the dimmer to switched mode you could probably get a way with running the MLs on a dimmer. This would be by far safer and easier than building a custom adapter.
__________________
Alex Weisman
Master Electrician - Pioneer Theatre Company
IceWolf Photography
[email address]

Soup or art?

"Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me

Love CB? Upgrade to premium today!
Reply With Quote
Old December 27th, 2007, 01:18 PM
JD's Avatar
JD JD is offline

 
Join Date: Jan 2005
Posts: 933
Thanks: 7
Thanked 57 Times in 52 Posts
Default Re: Silly Power Question

A plug like that would give me pause for thought. Three phase components cost a heck of a lot more that single phase parts. So, beyond the question of why a contractor would put the wrong receptacle in, is why would they pay so much extra money to put the wrong one in? (!)
The two answers that come to mind are:
1) It really is that type of power.
2) It wasn't a licensed contractor that installed it.
In any case, "Danger Danger Will Robinson!" Someone indicated to you that it is HHNG, but it needs to be checked out or better yet avoided!
__________________
John Dziel
DAE Concert Lighting
founded 1971
Intelligent Lighting Solutions
"Oh, that switch also fed the Hotel ?"
Reply With Quote
The Following User Says Thank You to JD For This Useful Post:
liteman (December 27th, 2007)
Reply

Tags
power, question, silly

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Stage Revolve (Motor and Power Question) rapscaLLion General Advice 20 February 22nd, 2009 12:40 AM
Phantom Power Question tenor_singer Sound 13 September 18th, 2007 10:25 PM
Homemade Electric on/off box TupeloTechie Lighting 21 January 24th, 2007 01:03 AM
Dimming mercury lamps... mixsa Lighting 1 October 13th, 2005 12:19 AM


All times are UTC -4. The time now is 01:05 AM.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.1 
Advertisement System V2.6 By   Branden

1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80