Hi all,
I'm working on a show in an old venue. I have access to a 60A 240VAC event power plug (NEMA 18-60 Plug). My desire is to bring in a few moving lights and wash units and supplement it with a small conventional package. I was thinking I would build a custom distro for this. I was going to basically wire the first hot leg to Phase A on my dimmer pack and throw a 20A breaker on the end for half of my intelligents, and do the same with the second hot leg, for Phase C and the other half of my intelligents. Right now, my current plot requires that my total intelligent light load is about 10A/120V on each breaker. My total conventional light load is about 40A/120V on each phase. My question is: If I rent an ETC 12 x 2.4kw Sensor dimmer pack, which should really use 120A, will it still work given that my available power is less than that? Does it matter since I'm only loading each phase to 40A/120V, which is available, or will the pack not work at all without 120A? Any responses, ideas, alternatives, or suggestions will be greatly appreciated. Happy Holidays! --liteman |
|
|||
|
The dimmer pack will only draw less than 100 watts, it is the load that you plug in and bring up that is the crucial factor.You can load up the dimmer but as long as you only bring up a balance of power at any time you can get away with it.The pack will work perfectly well.
__________________
David Ashton All Things Theatre Perth,Australia "for every complex problem there is a solution which is neat, simple,and wrong" H. L. Menken |
| The Following User Says Thank You to David Ashton For This Useful Post: | ||
liteman (December 27th, 2007) | ||
|
|||
|
Excellent. That's just what I wanted to hear.
Thanks! One more silly power question: I know that most moving lights these days can run at 120V or 220V. When they run at 220V, are they running off of a single leg at 220V, or two legs of 110V? My real question is, using the above event power, can I hookup my moving lights directly to the 240V interface? If so, how do both legs of power get into the moving light? Do I need special power cables? Also, what's the safest way for me to get the cam cables for the Sensor Pack hooked up into my custom distro without me having to wire cams out of my distro? Thanks again for all of your help and your (incredibly speedy!) responses. --liteman |
|
||||
|
liteman: STOP! If this is indeed the plug to which you are referring, it cannot safely be used for stage lighting, or anything else for that matter, as there's no electrical ground.
Secondly, you haven't told us what size the circuit breaker or fuses are supplying that receptacle, which is more important that the plug specifications. Thirdly, your questions indicate that you don't have enough knowledge or experience to do what you're attempting without a Licensed Electrician. Sorry to be blunt, but I don't want you or anyone else to be harmed. allthingstheatre is only partially correct regarding underrating dimmer loading, and didn't pick up on the fact that you refer to a NEMA 18-60 as a 60A 240VAC device, when it is actually a 4wire, 3ø, 120/208VAC connector, with no ground. Welcome to the Control Booth! We'll do our best to help you with any question, but we'll also tell you when we can't, for safety reasons.
__________________
|
| The Following User Says Thank You to derekleffew For This Useful Post: | ||
liteman (December 27th, 2007) | ||
| The Following User Says Thank You to wolf825 For This Useful Post: | ||
liteman (December 27th, 2007) | ||
|
|||
|
Thanks for your replies,
I apologize, I should have been more specific. I didn't assume that it was wired at 240V/60A because of the plug rating, it is clearly labeled on the disconnect that the plug is wired to. In addition, each of the poles on the plug itself is labeled, as well. I've attached a picture of the plug that I took on the first site survey. You're correct in picking up in my lack of knowledge about some of these things. I am really more of lighting designer, and usually let the production companies handle the setup, but this is for a small, non-profit organization, and I'm friends with the director, so it's a special circumstance. But I do have a fairly strong understanding of electricity and what is safe and what is not. I would have never known that the Nema 18-60 is normally used as a 3-phase with no ground. i just assumed that it is normally used as it was wired in this situation, but clearly, the original electricians retrofitted it, into what seems like event power. The top pole is labeled as neutral, left and right as the hot legs, and the bottom as ground. Based on these labels, and the labels on the disconnect, I came to the conclusion that it was a single phase 240V/60A with two hot legs, a neutral, and a ground. I certainly appreciate all of your concerns. I would never want anyone, including myself, to be harmed or put in danger by anything that had my hand in it, and I assure you that I will be the first person to step back if I even have an ounce a doubt in what I am doing. I was a little weary about a few things that I had never had to deal with before, as I've always worked with an abundance of power and normally let others worry about power issues, which is why I came with my original question. Again, thank you all for your responses, and your concerns - I appreciate them all. -liteman |
|
||||
|
Glad we didn't scare you away. I'll now address some of your questions, but I'd feel better if you had a more experienced electrician helping you.
The Sensor Pack, SP6, is normally set up for 3ø operation. It needs to be modified by its owner for single phase, GNHH, operation. I'm not positive, but I think dimmers 1-6 are on one leg and 7-12 are on the other, when used in single phase mode. All of your intelligent lights are set to operate on 120V, correct? You never told us the size of the fuses or breakers, or wire feeding the 60A receptacle. Measure the voltage on the receptacle to verify that the pencil labels are correct. Are you dealing with a venue maintenance person or some other building representative? Another issue. If it is in fact a 60amp breaker protecting that outlet, you'll need to wire your plug with #6 or better #4 wire. Then find a set of E1016series-compatible Camlok-type connectors to mate with the Sensor pack. Those connectors wired with #4 or #6 wire are not a common item, in any company's rental stock. Plus the neutral MUST be oversized. That's as much as I feel I can give you. Start a new thread in the New Member Board introducing yourself. We're lovable, but nosy. Tell us where you are and what you've done, and where you'd like to be and do. We like other's websites, and definitely post pictures of your benefit when it's done. We love pictures, there's a lengthy thread here.
__________________
Last edited by derekleffew; December 27th, 2007 at 02:33 PM.. |
| The Following User Says Thank You to derekleffew For This Useful Post: | ||
liteman (December 27th, 2007) | ||
|
||||
|
If your Intellignet lights really only have a total load of 10A it would be a lot safter to just put them on a dimmer. I know that most intelligent gear doesn't like being on an SCR, so if you can spare two slots in your 12-pack you could put a CC-20 or R20 module in to feed the MLs constant power. In a pinch if you set the dimmer to switched mode you could probably get a way with running the MLs on a dimmer. This would be by far safer and easier than building a custom adapter.
__________________
Alex Weisman Master Electrician - Pioneer Theatre Company IceWolf Photography Soup or art? "Crap happens, it is our job as technicians to fix the problem and see if it can be avoided. That does not mean yelling at actors or other crew people. We make mistakes, that is life. Welcome to live theatre, if it were the same every night it would be TV." ~Me Love CB? Upgrade to premium today! |
|
||||
|
A plug like that would give me pause for thought. Three phase components cost a heck of a lot more that single phase parts. So, beyond the question of why a contractor would put the wrong receptacle in, is why would they pay so much extra money to put the wrong one in? (!)
The two answers that come to mind are: 1) It really is that type of power. 2) It wasn't a licensed contractor that installed it. In any case, "Danger Danger Will Robinson!" Someone indicated to you that it is HHNG, but it needs to be checked out or better yet avoided!
__________________
John Dziel DAE Concert Lighting founded 1971 Intelligent Lighting Solutions "Oh, that switch also fed the Hotel ?" |
| The Following User Says Thank You to JD For This Useful Post: | ||
liteman (December 27th, 2007) | ||
![]() |
| Tags |
| power, question, silly |
| Thread Tools | Search this Thread |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Stage Revolve (Motor and Power Question) | rapscaLLion | General Advice | 20 | February 22nd, 2009 12:40 AM |
| Phantom Power Question | tenor_singer | Sound | 13 | September 18th, 2007 10:25 PM |
| Homemade Electric on/off box | TupeloTechie | Lighting | 21 | January 24th, 2007 01:03 AM |
| Dimming mercury lamps... | mixsa | Lighting | 1 | October 13th, 2005 12:19 AM |