    Default Checking Voltages

    How many of you actually check the wiring / voltage before plugging your gear in at venues?
    Inspire Create Perform | E.S Entertainment | Venue Management
    Edrick Smith | Boston, MA

  2. #2
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,458
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: Checking Voltages

    Quote Originally Posted by Edrick View Post
    How many of you actually check the wiring / voltage before plugging your gear in at venues?
    Do you mean with an outlet tester or a VOM?

    I'm guessing it would depend on whether or not there was a tie-in for a distro. Or what receptacle was encountered.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  3. #3
     Premium Member 


    Edrick's Avatar
    Join Date
    Mar 2007
    Location
    Boston, MA
    Occupation
    Pro
    Posts
    1,194
    Thanks
    1
    Thanked 19 Times in 13 Posts

    Thread Starter

    Default

    Either or just curious how many people just plug in to outlets without checking. You never know what backwards wiring someone's done.
    Inspire Create Perform | E.S Entertainment | Venue Management
    Edrick Smith | Boston, MA

  4. #4

    Morte615's Avatar
    Join Date
    Sep 2011
    Location
    Sandusky, Ohio, United States
    Occupation
    Consultant Dragon's Fire Design
    Posts
    179
    Thanks
    5
    Thanked 6 Times in 6 Posts

    Default Re: Checking Voltages

    As a former mobile DJ I ran my main audio and lighting rigs through power conditioners that would fix most problems, or at least notify me if something was wrong. Anything I placed around the room that was not part of the main rig, if it was a new location that I had not been in before I would usually use a circuit tester to make sure it had power and ground and the hot and neutral wasn't reversed.

    For my older mobile haunt stuff I didn't usually bother unless I have reason to believe there was something wrong. But most of that stuff is more hardy (and cheaper to replace) than audio and lighting. Currently if I run a mobile haunt I run all my audio and lighting through dedicated temporary circuits, fed from a feeder, much like in a theater.
    Morté aka Matt,
    Ego sum nex
    --------------------
    Dragon's Fire Design: http://www.dragonsfiredesign.com (Beta version of my portfolio, comments welcome!)
    Facebook: http://www.facebook.com/mattdrake
    Deviant Art: http://morte615.deviantart.com/

  5. #5

    rochem's Avatar
    Join Date
    May 2008
    Location
    New York, NY
    Occupation
    Undergrad
    Posts
    1,168
    Thanks
    45
    Thanked 91 Times in 71 Posts

    Default Re: Checking Voltages

    Do you mean individual wall outlets? Never, unless I have some reason to believe that they would be weird. However, now that I think about it, I'm rarely using wall outlets for anything more electrically sensitive than a Genie lift. I do meter anything that I tie in unless I know the venue really well and/or have just been there.

    This begs the question - is there a story behind this question?
    Michael

    "Why be gentle, it's rental!"
    [I]Utinam logica falsa tuam philosophiam totam suffodiant![/I]

  6. #6
     Premium Member 


    Edrick's Avatar
    Join Date
    Mar 2007
    Location
    Boston, MA
    Occupation
    Pro
    Posts
    1,194
    Thanks
    1
    Thanked 19 Times in 13 Posts

    Thread Starter

    Default

    Not me personally but an electrician on another forum I use had a concrete saw and he thought it was a L5-20 receptacle for 120v he was plugging into, but it turned out to be 220v and he cooked the saw after he kept starting it up after it shutdown.

    I myself just installed Furman power conditioners into my racks and know they list protection against stuff. But not everything runs through it.

    At my uncles new place the old owner wired a bunch of 15A straight blade plugs as 240v
    Inspire Create Perform | E.S Entertainment | Venue Management
    Edrick Smith | Boston, MA

  7. #7

    howlingwolf487's Avatar
    Join Date
    Sep 2006
    Location
    Collingswood, NJ
    Occupation
    A/V Technician
    Posts
    288
    Thanks
    13
    Thanked 17 Times in 16 Posts

    Default Re: Checking Voltages

    If I'm not there to see the tie-in, or if I'm in a venue that I'm not familiar with and am using wall power, I absolutely measure my AC. Someone else's mis-wiring could kill somebody…and I don't want that on my conscience.
    A lack of preparation on your part does not constitute an emergency on my part.

    Wolf
    <><

  8. #8


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,912
    Thanks
    146
    Thanked 123 Times in 115 Posts

    Default Re: Checking Voltages

    If it's a new situation I at least use an idiot tester.
    Checking Voltages-outlet-tester.jpg
    Philip LaDue
    9 year member.

  9. #9
    Senior Team  Premium Member 
    derekleffew's Avatar
    Join Date
    Aug 2007
    Location
    Las Vegas, NV, USA
    Occupation
    Academician/Pedantist
    Posts
    5,458
    Thanks
    256
    Thanked 957 Times in 780 Posts

    Blog Entries
    4

    Default Re: Checking Voltages

    Quote Originally Posted by avkid View Post
    If it's a new situation I at least use an idiot tester.
    I've tried that, but they just keep creating better ID10Ts.

    Stick with an outlet tester.
    Good authors too who once knew better words, Now only use four letter words, Writing prose.

  10. #10
    CBmod  Premium Member 
    museav's Avatar
    Join Date
    Jul 2007
    Location
    Marietta, GA
    Occupation
    President/Owner
    Posts
    3,717
    Thanks
    51
    Thanked 256 Times in 226 Posts

    Default Re: Checking Voltages

    Quote Originally Posted by Morte615 View Post
    As a former mobile DJ I ran my main audio and lighting rigs through power conditioners that would fix most problems, or at least notify me if something was wrong. Anything I placed around the room that was not part of the main rig, if it was a new location that I had not been in before I would usually use a circuit tester to make sure it had power and ground and the hot and neutral wasn't reversed.
    Checking the receptacles is a good idea but most 'power conditioners' won't do much of anything other than probably provide some high frequency filtering of the power, perhaps provide some surge suppression (with many being MOV based) and maybe shutting down if the voltage drops too low, but they won't fix or compensate for any electrical system or wiring issues.

    If you want something that will tell you more than just that the outlet is wired correctly, then you might want something like http://www.idealindustries.com/produ..._analyzers.jsp.
    Brad Weber
    audio, audiovisual and acoustical consultant
    www.museav.com

  11. #11


    Join Date
    May 2011
    Location
    Northern Lower Michigan
    Occupation
    Anything Tech
    Posts
    274
    Thanks
    27
    Thanked 9 Times in 8 Posts

    Default Re: Checking Voltages

    I don't test, but maybe I should start when I'm in an unusual space. Never really thought about it until now.
    I'm GELlin'...

  12. #12

    Morte615's Avatar
    Join Date
    Sep 2011
    Location
    Sandusky, Ohio, United States
    Occupation
    Consultant Dragon's Fire Design
    Posts
    179
    Thanks
    5
    Thanked 6 Times in 6 Posts

    Default Re: Checking Voltages

    I seem to remember (or mis-remember, it was over 10 years ago that I sold my company) that mine had something in it that would flip the hot and neutral if they were incorrect, as well as offer surge and brown-out protection (it had a built in ups) I do remember that I paid way too much for it at the time!
    Morté aka Matt,
    Ego sum nex
    --------------------
    Dragon's Fire Design: http://www.dragonsfiredesign.com (Beta version of my portfolio, comments welcome!)
    Facebook: http://www.facebook.com/mattdrake
    Deviant Art: http://morte615.deviantart.com/

  13. #13
    CBmod  Premium Member 
    museav's Avatar
    Join Date
    Jul 2007
    Location
    Marietta, GA
    Occupation
    President/Owner
    Posts
    3,717
    Thanks
    51
    Thanked 256 Times in 226 Posts

    Default Re: Checking Voltages

    Quote Originally Posted by Morte615 View Post
    I seem to remember (or mis-remember, it was over 10 years ago that I sold my company) that mine had something in it that would flip the hot and neutral if they were incorrect, as well as offer surge and brown-out protection (it had a built in ups) I do remember that I paid way too much for it at the time!
    There are power devices that incorporate UPS, voltage regulation, real surge protection and so on but those are much more comprehensive, and as you noted more expensive, devices than the simple and relatively inexpensive 'power conditioners' that many people use. An online or double conversion UPS can also often resolve many power issues as it always runs off the battery and inverter, thus providing clean, isolated power while a true sine wave UPS will give a clean waveform rather than a stepped waveform. But many and probably most power regulation and UPS units will not address wiring or grounding issues.
    Brad Weber
    audio, audiovisual and acoustical consultant
    www.museav.com

  14. #14
    Senior Team  Premium Member 
    Footer's Avatar
    Join Date
    Nov 2005
    Location
    Saratoga Springs, NY
    Occupation
    Production Coordinator
    Posts
    7,602
    Thanks
    2
    Thanked 535 Times in 429 Posts

    Default Re: Checking Voltages

    I would say about half the groups we have in will check voltages before they throw the switch on their distro. Most distros anymore have meters built in that make is fairly easy to do. I also have metering built into my company switches so that helps people a bit. Still does not protect against a hot/neutral switch.

    Now, what really does trip people up is our stage is wired with L5-20, L5-30, L6-20, and L6-30. All of them are 120v. One is sound/band power, one is not.
    Kyle Van Sandt
    Production Coordinator
    The Egg
    Van Sandt Designs

    "Pull rope, push box, push button, get a banana."

  15. #15


    Join Date
    Mar 2008
    Location
    SW Michigan
    Occupation
    Educator
    Posts
    32
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Default Re: Checking Voltages

    Quote Originally Posted by Footer View Post
    Now, what really does trip people up is our stage is wired with L5-20, L5-30, L6-20, and L6-30. All of them are 120v.
    How did that get by the electrical inspector? (Or is one of those time where your ownership makes you special?)

    Philip

  16. #16

    howlingwolf487's Avatar
    Join Date
    Sep 2006
    Location
    Collingswood, NJ
    Occupation
    A/V Technician
    Posts
    288
    Thanks
    13
    Thanked 17 Times in 16 Posts

    Default Re: Checking Voltages

    Quote Originally Posted by museav View Post
    If you want something that will tell you more than just that the outlet is wired correctly, then you might want something like IDEAL INDUSTRIES, INC. - SureTest® Circuit Analyzers.
    Ooh…pretty.

    I use the higher-end version of this one. It's cheap enough that, if I lost it or it got fried, I wouldn't be too sad. I may get a Fluke MM in the future, but can't justify the price right now.
    A lack of preparation on your part does not constitute an emergency on my part.

    Wolf
    <><

  17. #17


    Join Date
    Oct 2009
    Location
    Minneapolis, MN
    Occupation
    Manager/Administrator
    Posts
    232
    Thanks
    18
    Thanked 8 Times in 8 Posts

    Default

    All my tours are supposed to meter all tie ins before hook up. I recently had an electrician tie into a generator set for 240/480.... Every mover setup for 208 had $1800 in damage... 40 fixtures or so....
    That was a bad day.