Results 1 to 19 of 19
Got a small (
K) grant for "energy efficiency/enviromental" stuff is being discussed in the ControlBooth Stage Management and Facility Operations forum; The local Lions club president (who is a "green believer") got the local Lions to give us a
K grant ...

  1. #1


    Join Date
    Nov 2011
    Location
    Western NC
    Occupation
    Lights, set building
    Posts
    385
    Thanks
    89
    Thanked 11 Times in 7 Posts

    Default Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    The local Lions club president (who is a "green believer") got the local Lions to give us a $1K grant to "improve energy efficiency".

    Works for me - now I have to figure out how to spend the money.

    I can replace all of my work light bulbs (11) with large CFL bulbs. That is actually a bit of change - probably on the order of $200. I've got CFL bulbs in the lobby fixtures (can lights with CFL bulbs). I have tube fluorescent fixtures just about everywhere else. I can go through the building and replace a few bulbs here and there, but that (with the work lights) probably only spends about 1/3 of the money.

    I could replace the bathroom fixtures with fixtures which use T8 style bulbs.

    Any other thoughts? There isn't enough money to replace the back bay door with something more energy efficient. I could replace one or two of the side doors. There isn't enough money to do LED lights and fixtures.

  2. #2
    cpf
    cpf is offline


    Join Date
    Aug 2010
    Location
    I miss Alberta
    Occupation
    Volunteer
    Posts
    959
    Thanks
    12
    Thanked 44 Times in 43 Posts

    Default

    Additional weather sealing on all the exterior man doors? Motion-sensing light switches in bathrooms, etc? Professional tuneup of the heating/cooling controls?
    cat /dev/urandom > /dev/tty.dmx-out

  3. #3
    Senior Team gafftaper's Avatar
    Join Date
    Jan 2006
    Location
    Seattle, Washington
    Occupation
    Got one for me?
    Posts
    9,596
    Thanks
    83
    Thanked 583 Times in 436 Posts

    Blog Entries
    7

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    -Automatic faucets/hand dryers in the rest rooms.

    -New high efficiency hot water tank, Fridge/Freezer, or instant hot water in the concessions area

    -No CFL's in the house! You will hate the results! There are some high quality LED replacement lamps out there that dim pretty well and could be used in the house. However they are $50+ each. So if you need more than 20 lamps you are over the budget.

    I think your most likely target will be ways to save, water, heat, or electricity in non-stage areas. You don't have enough money to do anything major on stage.


  4. #4


    Join Date
    Mar 2011
    Location
    Wisconsin
    Posts
    344
    Thanks
    6
    Thanked 7 Times in 7 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by gafftaper View Post
    -Automatic faucets/hand dryers in the rest rooms.

    -New high efficiency hot water tank, Fridge/Freezer, or instant hot water in the concessions area

    -No CFL's in the house! You will hate the results! There are some high quality LED replacement lamps out there that dim pretty well and could be used in the house. However they are $50+ each. So if you need more than 20 lamps you are over the budget.

    I think your most likely target will be ways to save, water, heat, or electricity in non-stage areas. You don't have enough money to do anything major on stage.
    Re-circulation pumps, aka instant hot water, are great, but they will cost you a noticeable amount on your electric bill. You could, however, have it on a timer. That way it only turns on around the time you need a lot of hot water.

    I second the automatic faucets/hand dryers. Great way to reduce paper waste and wasted water. Although they will put you over budget very quickly.


    You could simply switch your light bulbs to the energy star bulbs. I don't mean the bulbs in the house, but the ones backstage and in any rooms. Another idea you might be able to do (I did this at my house, not sure if a business qualifies) is to have an energy star representative come out and do an inspection on your building. The rep will then give you a list of things that you could improve to make the building more energy efficient. The government was re-imbursing home owners for the costs of the improvements (which wasn't much). But this way you know you are improving the areas that are costing you the most each month.

    Edit: check out the Energy Star website for more details. http://www.energystar.gov/index.cfm?...ness.bus_bldgs
    www.theatrexchange.factplayers.org

  5. #5
    CBmod  Premium Member 
    museav's Avatar
    Join Date
    Jul 2007
    Location
    Marietta, GA
    Occupation
    President/Owner
    Posts
    3,716
    Thanks
    51
    Thanked 256 Times in 226 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by JLNorthGA View Post
    The local Lions club president (who is a "green believer") got the local Lions to give us a $1K grant to "improve energy efficiency".
    They apparently didn't limit it to the building energy efficiency so how about $1,000 worth of coffee, Red Bull and 5 Hour Energy!

    There may be some simple areas like sealing leaky ductwork, cleaning or replacing dirty air filters (and saving some funds for ongoing replacement). insulating hot water pipes, repairing or adding exterior door seals and so on. Maybe a low volume toilet or two.
    Brad Weber
    audio, audiovisual and acoustical consultant
    www.museav.com

  6. #6


    Join Date
    Mar 2004
    Occupation
    Other
    Posts
    458
    Thanks
    8
    Thanked 30 Times in 24 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by gafftaper View Post
    -Automatic faucets/hand dryers in the rest rooms.
    Electric hand dryers? Nooooooooo!

    Automatic faucets are OK, but many people (including myself) can't stand the automatic electric hand dryers. I know that the dryers are more environmentally friendly (even though most use more energy than 3 source 4s), but they do a lousy job drying hands. And did you ever wash your face and try drying it with an electric hand dryer? Not fun.

    Use recycled paper and dispensers that only give you one sheet of paper at a time, but I beg you... don't get electric hand dryers!

  7. #7


    Join Date
    Nov 2004
    Location
    topeka, ks
    Occupation
    Freelance
    Posts
    1,095
    Thanks
    3
    Thanked 44 Times in 37 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by DrPinto View Post
    Electric hand dryers? Nooooooooo!

    Automatic faucets are OK, but many people (including myself) can't stand the automatic electric hand dryers. I know that the dryers are more environmentally friendly (even though most use more energy than 3 source 4s), but they do a lousy job drying hands. And did you ever wash your face and try drying it with an electric hand dryer? Not fun.

    Use recycled paper and dispensers that only give you one sheet of paper at a time, but I beg you... don't get electric hand dryers!
    The Dyson Airblade is a great electric hand dryer, but just one would use up the grant money.

  8. #8
     Premium Member 
    sk8rsdad's Avatar
    Join Date
    Aug 2008
    Location
    Ottawa
    Occupation
    Hobbyist
    Posts
    1,100
    Thanks
    29
    Thanked 108 Times in 95 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    One option is replacing all your exit signs with LED. There's certainly an energy saving, but the real saving is in not having to replace all those CFLs over the next 20 years.

  9. #9


    Join Date
    Jan 2012
    Location
    Houston, TX
    Occupation
    Facility Manager
    Posts
    63
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Dyson Airblade is far too noisy for anywhere near a performance space. And they frighten small children. I agree with sk8trsdad -- we're in the process of doing exactly that. I'd recommend considering LEDs anywhere where the lights are on most of the time if not always and dimming/color isn't important -- aisle lights, step lights, vestibule lights, etc.

  10. #10


    Join Date
    Feb 2004
    Location
    NJ Shore
    Occupation
    Pro
    Posts
    5,912
    Thanks
    146
    Thanked 123 Times in 115 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by DrPinto View Post
    Electric hand dryers? Nooooooooo!
    Automatic faucets are OK, but many people (including myself) can't stand the automatic electric hand dryers. I know that the dryers are more environmentally friendly (even though most use more energy than 3 source 4s), but they do a lousy job drying hands.
    We have these, they are the best I have ever encountered.
    Hand Dryers - BluStorm Hand Dryer
    Philip LaDue
    9 year member.

  11. #11
    CBmod  Premium Member 
    museav's Avatar
    Join Date
    Jul 2007
    Location
    Marietta, GA
    Occupation
    President/Owner
    Posts
    3,716
    Thanks
    51
    Thanked 256 Times in 226 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    You might want to consider that the hand dryers typically require a dedicated 15A to 20A, 110-120VAC circuit to the unit, so unless you already have that power availble then the asociated effort and cost may make them impractical within a $1,000 total budget.

    Options such as replacing the exit signs may also have other considerations. For example, if you change the signs then you may be required to also make any other related changes necessary to comply with current code rather than just directly replacing what is there. So you might want to verify any such ideas with the local code officials and AHJ before committing to them.
    Brad Weber
    audio, audiovisual and acoustical consultant
    www.museav.com

  12. #12
     Premium Member 


    gafftapegreenia's Avatar
    Join Date
    Sep 2005
    Location
    Atlanta GA
    Occupation
    Assoc. Technical Director
    Posts
    3,273
    Thanks
    213
    Thanked 111 Times in 99 Posts

    Blog Entries
    1

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    What about buying the latest generation of efficient lamps for your PARs, ERS's and Fresnels? (Assuming your inventory isn't all Source 4)
    One must first know and understand the rules of theatre before one can break them.

  13. #13


    Join Date
    Nov 2011
    Location
    Western NC
    Occupation
    Lights, set building
    Posts
    385
    Thanks
    89
    Thanked 11 Times in 7 Posts

    Thread Starter

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by gafftapegreenia View Post
    What about buying the latest generation of efficient lamps for your PARs, ERS's and Fresnels? (Assuming your inventory isn't all Source 4)
    All of my instruments up on the catwalk are Source Fours. I have 12 Altman Fresnel instruments on the electrics above the stage. All the instruments are new.

  14. #14


    Join Date
    Jan 2012
    Location
    Houston, TX
    Occupation
    Facility Manager
    Posts
    63
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by museav View Post
    You might want to consider that the hand dryers typically require a dedicated 15A to 20A, 110-120VAC circuit to the unit, so unless you already have that power availble then the asociated effort and cost may make them impractical within a $1,000 total budget.

    Options such as replacing the exit signs may also have other considerations. For example, if you change the signs then you may be required to also make any other related changes necessary to comply with current code rather than just directly replacing what is there. So you might want to verify any such ideas with the local code officials and AHJ before committing to them.
    We've run into this before. Relamping with LED equivalents is generally OK but it you change the actual sign or lighting fixture it may trigger other code requirements. We have had very good luck with direct-replacement LED lamps for exit signs.

  15. #15


    Join Date
    Nov 2004
    Location
    topeka, ks
    Occupation
    Freelance
    Posts
    1,095
    Thanks
    3
    Thanked 44 Times in 37 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by marmer View Post
    We've run into this before. Relamping with LED equivalents is generally OK but it you change the actual sign or lighting fixture it may trigger other code requirements. We have had very good luck with direct-replacement LED lamps for exit signs.
    We've had terrible luck with our LED replacements. After about 2 years we slowly started losing them, now 5 years after the install almost all but a few of them have been replaced. I'm sure a lot of our problem is from having the city (we are attached to city hall) test the emergency generator weekly. And I'm not sure how "green" they are but if I was buying exit lights I would go for the radioactive ones.

  16. #16


    Join Date
    Jan 2012
    Location
    Houston, TX
    Occupation
    Facility Manager
    Posts
    63
    Thanks
    1
    Thanked 4 Times in 4 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by techieman33 View Post
    We've had terrible luck with our LED replacements. After about 2 years we slowly started losing them, now 5 years after the install almost all but a few of them have been replaced. I'm sure a lot of our problem is from having the city (we are attached to city hall) test the emergency generator weekly. And I'm not sure how "green" they are but if I was buying exit lights I would go for the radioactive ones.
    I have dozens of exit lights in my building, and most of them are hard to reach. Some of them require a Genie. Changing them in two to five years instead of every six months seems like a good deal to me, especially if someone else is picking up the cost. Actually, we'd be doing it anyway because the incandescents they use are being discontinued, we hear. We test the generator every week, too, we'll see how long our exit signs last. (they're new enough that none have failed yet.)

  17. #17
     Premium Member 


    gafftapegreenia's Avatar
    Join Date
    Sep 2005
    Location
    Atlanta GA
    Occupation
    Assoc. Technical Director
    Posts
    3,273
    Thanks
    213
    Thanked 111 Times in 99 Posts

    Blog Entries
    1

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by techieman33 View Post
    We've had terrible luck with our LED replacements. After about 2 years we slowly started losing them, now 5 years after the install almost all but a few of them have been replaced. I'm sure a lot of our problem is from having the city (we are attached to city hall) test the emergency generator weekly. And I'm not sure how "green" they are but if I was buying exit lights I would go for the radioactive ones.
    I'll have to see if I can find it, but recently I was reading a big report about this contractor that got fined for improperly disposing hundreds on the radioactive ones,and how many buildings are currently ditching those because of the associated disposal costs.
    One must first know and understand the rules of theatre before one can break them.

  18. #18
    CBmod  Premium Member 
    museav's Avatar
    Join Date
    Jul 2007
    Location
    Marietta, GA
    Occupation
    President/Owner
    Posts
    3,716
    Thanks
    51
    Thanked 256 Times in 226 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by gafftapegreenia View Post
    I'll have to see if I can find it, but recently I was reading a big report about this contractor that got fined for improperly disposing hundreds on the radioactive ones,and how many buildings are currently ditching those because of the associated disposal costs.
    Of course CFLs have their own issues in regards to cleanup and disposal.
    Brad Weber
    audio, audiovisual and acoustical consultant
    www.museav.com

  19. #19
    zmb
    zmb is offline


    Join Date
    Mar 2010
    Location
    Redmond, WA
    Occupation
    High School Student
    Posts
    1,039
    Thanks
    27
    Thanked 27 Times in 24 Posts

    Default Re: Got a small ($1K) grant for "energy efficiency/enviromental" stuff

    Quote Originally Posted by museav View Post
    Of course CFLs have their own issues in regards to cleanup and disposal.
    Those can make their way to a collection bin at a hardware store instead of shipping to some nuclear waste site

    And if you're going to replace existing lamps with T8, maybe look at going to T5 as long as you're doing work.