Woah, you totally lost me there.
We think of the
SSR (Solid State
Relay) as a part. Often called a "
power cube." The
SSR however is actually a
circuit composed of a couple of SCRs, a photo optic isolator, and a handful of resistors, capacitors, and other parts all potted in an
epoxy block. On the outside, it is a cube that mounts to a
heat-sink with input and output terminals, but there is a lot inside. Some of what goes on inside allows some
voltage to pass at a very low
current. Under normal conditions with a load attached you will not see this leakage, but it is why we get crazy
voltage readings from dimmers that have no load attached. It is normal and does not indicate a defect. It is also why you should flip off the
circuit breaker before you can be sure there is no output
voltage.
If you turned on the
circuit and the lamp only went to half brightness and that is when you got the 67 volt reading, It would indicate one of two problems:
1) A gating failure inside the
SSR is only operating one of the SCRs inside the cube.
2) It is an
ETC dimmer that accidentally got switched into
dimmer-doubling mode and is only turning on one of the two
SCR's inside the cube.
In either case, the reading should be closer to 77 volts, but due to
meter limitations may be giving you the 67 number.
One other note: When there is no load on the
dimmer, you may get an arbitrary output reading when the
dimmer is full on as there is really not enough
current in the
circuit to latch the SCRs when they are gated. This may vary among SSRs just due to parts tolerances.