Most Sensor Racks have 2 DMX Inputs, Port A and Port B, If your rack says No Data On Port A it means your rack isn't getting any DMX Data into the first Port. From the sounds of it though these two new rack you said are for the Black Box which sounds like it's not finished yet so the DMX isn't hooked up. However it could also just mean the Board isn't turned on in your black box. It will show that error whenever your control board is turned off because it wont be getting any DMX Signal.
Your most serious problem is your Ambient Overtemp Alarm....this is REALLY bad. It means your Rack CEM is getting too hot and is basically cooking. It could fry soon if you're not careful. It sounds like 2 of your racks were just recently installed...I bet it's gotten warmer then it was before in there with 2 MORE racks outputing another 192 Dimmers worth of heat. (They are 96 Racks aren't they, or are they 48's or 24's?) I bet you this has caused your original 4 racks to overheat much more often then they used to. As one other person said, the original Sensor Rack CEM's had an overheating problem that they fixed in the newer CEM's.
I would call ETC....try to stress to this "Smith" person that this is a serious problem that needs to be addressed before the CEM fails in the middle of a show and leaves you stranded without a paddle. It's better to replace the DEM on YOUR schedule rather then WHEN it dies. Replacing a CEM is an easy procedure that takes about 15 minutes...if that. It's litterally about 5 Steps, Cutting the Power, Popping out the old CEM, Plugging in the new one, Restoring the Power and then checking to make sure all the Programming is right. ETC has a record of every install they have ever done and will be able to pull up and programm all of your CEM's exactly how they are right now so there will be no change in Functionality. ETC might even replace the defective units for free since it was a design flaw.
There is no harm in calling ETC and asking them, they are really nice people.