Download the BCMC report for the basis of the IBC and close to LSC.
http://theatreconsultants.org/archives/position-papers/
http://theatreconsultants.org/archives/position-papers/
I am sure Bill deals with these subjects more than I have recently. But it appears the requirement for a fire curtain is triggered by the code applicable to the proscenium wall:
Two minor clarifications:My Understanding of the current code is that as long as your "fly space" the distance from the deck to the bottom of the grid, is under 50' No fire curtain is required. Most theatres being built in High schools and the the like are coming in at 48' to the grid.
48' aff = no fire curtain
50' aff = fire curtain
Types of acceptable curtains are usually dictated by the AHJ.
How many HTG (Honest To God) deluge curtains are you seeing installed these days. I keep thinking back to one that destroyed a building under construction in downtown NYC back in about 1990.Download the BCMC report for the basis of the IBC and close to LSC.
http://theatreconsultants.org/archives/position-papers/
A few. Just did Alley Theatre. I've done quite a few over past 35 years. They need to have pre-action controls per the sprinkler standard however.How many HTG (Honest To God) deluge curtains are you seeing installed these days. I keep thinking back to one that destroyed a building under construction in downtown NYC back in about 1990.