LesWilson
Well-Known Member
Everything has been fine since we renovated our venue last March. Out of the blue, specific dimmer circuits flickered when used. Others flickered even when not used. Hours later, everything would be fine. Been chasing this for a week. I read this 10 year old CB thread: https://www.controlbooth.com/threads/flickering-fluttering-lights.6422/#post-72085
In my case the 18 flickering circuits are all in Bank 3 of the 96 channel rack. All of the EM64 control module jumpers are set to 1 so the statements about each one being set for different addresses is confusing. The EM64 manual indicates values of 1, 49 or 97. Our unit is 96 channels in 3 banks. [Head scratching here]
Swapping a dimmer tray with a non-flickering circuit in another bank did not resolve the problem. Swapping in a spare controller did not resolve the problem. The 3 legs metered at 118v, 120v and 120v but at the time it was metered, the problem was not manifesting itself. We're running out of ideas of what to try next to isolate the problem.
Could this be a power problem? Interference from something else? What am I getting wrong with the EM64 addressing?
TIA
In my case the 18 flickering circuits are all in Bank 3 of the 96 channel rack. All of the EM64 control module jumpers are set to 1 so the statements about each one being set for different addresses is confusing. The EM64 manual indicates values of 1, 49 or 97. Our unit is 96 channels in 3 banks. [Head scratching here]
Swapping a dimmer tray with a non-flickering circuit in another bank did not resolve the problem. Swapping in a spare controller did not resolve the problem. The 3 legs metered at 118v, 120v and 120v but at the time it was metered, the problem was not manifesting itself. We're running out of ideas of what to try next to isolate the problem.
Could this be a power problem? Interference from something else? What am I getting wrong with the EM64 addressing?
TIA