What bulbs, our problem was that we had the wrong bulbs in the lights!
What bulbs, our problem was that we had overloaded the dimmers.
Using what he considered very close voltage tolerances the meter recorded only one event despite nearly constant flickering on our left leg, and the sine waves during that event looked perfectly normal. Total harmonic distortion was about 2% on the right leg and less than 4% on the left leg. If anyone is interested, I can post an image of the voltage and power curves during the one event recorded; they seemed perfectly normal.
He noted the same 3 Amps of current on the ground that we had previously seen, but disagreed that it was the result of induction in the conduit, since each conduit carries a conductor from each leg, which are 100% out-of-phase. The voltage was very low (~1V), which suggests that it must be coming from a resistive load. We are not sure how to proceed with that.
Since the PQA I have spoken to Joel from Century Lighting, who said that he was recently talking to a tech from Europe who has encountered similar problems on single-phase installations there and who said that there are settings in the C21 software that can be tweaked to fix it. He's getting more information for us; hopefully, this will not turn out to be another wild goose chase.
If you are running loads at a dimmed level, with flicker, and getting only Vthd of 2-4%, you are doing great! In fact, that means there is a huge resistive load on your power feed and the dimming system is a small part of the load. On the other hand, if you are getting 2-4% Vthd with dimmers at full or at zero, then you have some disturbances on your grid but they should not be significant enough to cause problems.
Interesting. Single-phase power in Europe almost always refers to a single pole of power. If they have more poles of power, they will be called two-phase or three-phase. Only in the US does single-phase mean two poles of power, which is why I am on a crusade at work to use the terms split-phase and bi-phase so that we can better converse with people from around the world.
i had a similar issue one time with our house lights flickering and it was on one row of lights, all just conventional ETC Pars using 750w lamps. The issue turned out to be a bad Power Block in the Dimmer itself. We used the ETC Smartpack and it was found in there. We checked the temperature and it was wildly hot compared to the others and that was because the Block itself was going out. May be something to check out in your setup...hope this helps.
Sounds like there is a N/G bonding strap somewhere where it should not be. Defiantly something that requires a qualified person with proper protection, but with the rack locked out and tagged, the neutral would have to be lifted and then and metered with respect to ground. Since the only bond should be at the mains, the N/G should read an open circuit facing the dimmer rack. It will most likely read as a short. From there, it is a matter of following the neutral back and doing the same at each branch point.
EDIT: Just some more thoughts- Since the current flow in the ground is so much lower than what you would expect on the neutral, it indicates the ground path is of a much higher resistance. This would be a good indicator that the problem is pretty far out on a branch. No matter where this connection is, current will back-feed to that location, so even if the circuit is off, the loop will still be present. I don't think this is at a fixture level, but I have seen stranger things. If continuity shows at the rack neutral buss, it may be faster to remove the individual home-run neutrals from the circuits there then chase around the building.
In summary, this problem may have nothing to do with your primary issue, but it is a good place to start and should be corrected anyhow. In any diagnostic procedure, you always try to eliminate the things you know are wrong first.
We turned off the power to the whole building at the main cutoff and disconnected the ground and neutral in the sub panel that feeds our theater. We tested for resistance across neutral and ground, expecting (or at least hoping!) to see infinite resistance. Instead we found only about 1 Ohm. So it appears that there is definitely some extraneous bonding somewhere. We're going to have to get an electrician in to track it down, I think.
Again, we don't know for sure that this is related to our flicker, but it's always a good idea to eliminate known problems when troubleshooting.
Anyone have any other suggestions?
One Ohm.... Provided the meter was accurate, that may be pretty far out on a branch. (Higher resistance then I would suspect for a solid bond.) Might be worth the time to unplug all the fixtures. Since the dimmers and breakers only affect the "hot" carrier, a single fixture with an N/G short would provide back-feed for the whole system even if the breaker on the offending circuit was switched off. As labor intensive as it is, the full "unplug" test still sounds like the least expensive experiment on the list.
Yet another possible problem may be a simple N/G reversal on a fixture plug. The fixture would still work fine, but the neutral would be tied to the frame of the fixture and find it's path to the ground through any of the other fixtures mounted on the same pipe.
I won't say "I told you so"
" logged this earlier, now disappeared, the most obvious, common problem causing flickering is a bad neutral connection in the dimmer and this could cause load related flickering, another vaguely possible fault is an earth neutral swap on a light, sending current down the earth and lifting it."