Grounded Conductor

derekleffew

Resident Curmudgeon
Senior Team
Premium Member
GroundED Conductor. The white wire, most often called the neutral conductor. Always carries some current, but may or may not be considered current-carrying by the NEC for de-rating and conduit fill purposes. A neutral conductor in a three-phase circuit that supplies only linear loads (lamps and other resisitive loads) is not considered current-carrying since it only carries the imbalance current of the three phases. If the conductor is supplying non-linear loads (Phase-control dimmers, switch mode power supplies and the like), it is considered a current-carrying conductor.

Neutrals in two-wire, single phase applications are always considered current carrying conductors.

Compare to Grounding Conductor.
 