PLEASE do not take offense but some of the assumptions you are making and questions you're asking are making me unsure
you understand how dimming systems work but of course that's probably why you are here!
You are not connecting 18 volts to the demultiplexer board... the demultiplexer board is sending 18v to the dimmers!
If you don"t feel comfortable working on this equipment, please
call in a technician who is.
On the diagram I provided earlier in this thread, the "signal flow" goes from top to bottom, so the control
voltage goes FROM a
console or demultiplexer TO a
dimmer. Zero control
voltage tells the
dimmer to not output AC
voltage to a
circuit/
fixture; 15 or 18 vdc tells the
dimmer to output full AC
voltage to the
circuit/
fixture. IF the control
voltage for full output of the
dimmer is indeed 18v, 15v will tell the
dimmer to output slightly less than full
voltage to the
circuit/
fixture.
The first issue is the 18 volts. This is an odd but not unrealistic number.
As
@FMEng has been saying, you need to use your
meter. Set it to the DC Volts mode with a range of 20 volts or higher.
To find the actual control
voltage to the dimmers, take a reading on the 48-channel demultiplexer
circuit board by placing the negative (black) lead on one of the two COM terminals on
connector J1 and the positive lead (red) on an easily accessible output
terminal of
connector J4 or J5. Slowly bring up the
fader on your main
console that corresponds to this number
terminal and see if the
meter slowly goes from zero to 15 (or 18) volts as you move the
channel fader to full. If the
meter needle tries to go below zero or if a digital
meter shows a minus sign, you may have a negative control
voltage!
Assuming this goes as expected, you should then do the same on the
houselight control
system.
BUT, there may be extra wires with other voltages in this
system that operate "take control" relays or light up
fader scales or buttons. Please post some photos of
terminal blocks /
houselight control wiring before trying to measure this.
And don't get in over your head so you're around to report back!