Is it acceptable to put 4x S4s on a dimmer?

Discussion in 'Question of the Day' started by derekleffew, Oct 5, 2008.

  1. derekleffew

    derekleffew Resident Curmudgeon Senior Team Premium Member

    Messages:
    4,448
    Likes Received:
    2,849
    Location:
    Las Vegas, NV, USA
    20A (2400W) dimmer. Four fixtures with HPL575/115 lamps. Discuss.
     
  2. Sean

    Sean Active Member

    Messages:
    438
    Likes Received:
    32
    Location:
    Alexandria, VA
    Yes.

    --Sean
     
  3. waynehoskins

    waynehoskins Active Member

    Messages:
    782
    Likes Received:
    49
    Location:
    Arlington, TX
    My opinion = yes.
     
  4. seanandkate

    seanandkate Well-Known Member Fight Leukemia

    Messages:
    711
    Likes Received:
    165
    Occupation:
    Educator
    Location:
    Stouffville, Ontario
    Barring obnoxiously long cable runs, yes.
     
  5. len

    len Well-Known Member

    Messages:
    2,709
    Likes Received:
    204
    Location:
    Chicagoland
    Theoretically, yes.

    Real world, probably not.
     
  6. clbarker

    clbarker Member

    Messages:
    22
    Likes Received:
    0
    Location:
    Lynchburg, VA
    Works for me everytime! So, yes!
     
  7. soundlight

    soundlight Well-Known Member

    Messages:
    3,666
    Likes Received:
    330
    Location:
    PA & NJ
    Done it multiple times, and it hasn't tripped a breaker yet.
     
  8. propmonkey

    propmonkey Well-Known Member

    Messages:
    990
    Likes Received:
    3
    Location:
    Beloit/Milwaukee, WI
    isnt that way they made the lamps 575w?
     
  9. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    Yes and no, while 4 certainly can run off a dimmer if you blow a lamp it will almost certainly take out the breaker and you lose 4 lights out of your rig,-black hole.If you can split them it's safer.
     
  10. Pip

    Pip Active Member

    Messages:
    142
    Likes Received:
    4
    Location:
    Greeley, CO
    Well, it's possible, but I wouldn't say it's advisable.

    Consider the almighty power equation:
    Watts equals Volts times Amps:
    W = V * A

    You have 4 instruments, 575W each, for a total of 2,300W (2.3kW):
    4 * 575W = 2300 W
    That's cutting it fairly close if you're on a 2.4kW dimmer. Let's look at that in terms of current (Amperage)

    Going back to our power equation...
    2300W = 120V * A
    A = 2300 / 120 = 19.17A

    :)
     
  11. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    Bear in mind that 2.4k is a conservative rating, there is a built in tolerance so that it is quite safe to run at that output.Your output devices are normally 40A and the breaker will not trip unless there is a prolonged or severe overload.
     
  12. Pip

    Pip Active Member

    Messages:
    142
    Likes Received:
    4
    Location:
    Greeley, CO
    Yes, but that is a built in safety feature. By saying that and going about business in that manner, you're circumventing one of the ways these things are designed to keep you (and your audiences, your facilities, etc) safe.

    It's not just about the inconvenience of popping the breaker - it's about actual safety when dealing with dangerous electrical equipment.
     
  13. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    What I said is that it is safe to run 2.4k on a 2.4k dimmer because there is a safety factor built in, unlike others who were saying that you should further de-rate it to be on the safe side, I am sure no-one would ever consider pushing them a bit further even though you could possibly get away with it.
     
  14. Chris15

    Chris15 CBMod CB Mods Premium Member

    Messages:
    4,140
    Likes Received:
    419
    Location:
    Sydney, Australia
    And the average mains supply voltage is?
     
  15. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    I think we have to assume that we are talking 115 or 120v with the appropriate lamp, in Australia or UK the above discussion would revolve around 10A 240v dimmers, also 2.4kw.
     
  16. Chris15

    Chris15 CBMod CB Mods Premium Member

    Messages:
    4,140
    Likes Received:
    419
    Location:
    Sydney, Australia
    I was taking that voltage range as a given, but at 120V, 115V 575W lamps draw more that 575W... Rather my sums put it at about 626W, 5.2A. 4 times that and you are into the range where a fuse will trip in time but a breaker may not...

    Put a voltage spike on that and I think you'll find breakers going tripsies.

    Can you do it? Yes. Should you do it? perhaps not...
     
  17. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    If you don't use the correct voltage lamp you're very likely to blow it as the life reduces dramatically, but in answering questions like this it is fair to assume that a 575 lamp is using 575w.If you look at fuse ratings you will see that they run at a slight overload for a long time, certainly up to an hour.Over-running a lamp is not a linear increase as the resistance is very non linear with temperature so a simple calculation is inaccurate.
     
  18. STEVETERRY

    STEVETERRY Well-Known Member

    Messages:
    1,368
    Likes Received:
    719
    Location:
    New York
    ETC Sensor dimmers are Listed for 100% loading, 100% duty-cycle operation. Four x 575W is no problem.

    Some dimmers with thermal breakers can only be loaded to 80%, or 1920W on a 2400W dimmer.

    You need to determine the rating of your dimmer to answer this question.

    ST
     
  19. David Ashton

    David Ashton Active Member

    Messages:
    829
    Likes Received:
    89
    Occupation:
    truck driver
    Location:
    perth W Australia
    Steve, could we have some examples of 2.4k dimmers which only take 1.9k as I've never come across any in Australia?.
     
  20. Chris15

    Chris15 CBMod CB Mods Premium Member

    Messages:
    4,140
    Likes Received:
    419
    Location:
    Sydney, Australia
    Err I thought it was a not uncommon practice for our American brothers to use a 115V lamp on a 120V supply to get some extra brightness. Someone wanting brownie points can go back into the archives and find Ship's percentages for lamp life change, colour temperature change, output change etc with over or under voltaging a lamp.

    I looked at a breaker curve a while back and from memory, you could run indefinitely at 127%... Fuses are normally a little more sensitive.

    Yes the resistance is very non linear, a 500w flood lamp is only a few ohms cold at DC... I suspect current draw will still go up, though it won't be linear and hence my number will be out...
     