Just a reminder here:

(I would) make sure each step is individually supported, not in any way supported by steps further down. An installation contractor screwing that up was the root cause behind the Kansas City Hyatt disaster in the 90s.

I'm not sure that's applicable here, but some designs might go that way, so I figured I'd point it out.
Not to keep talking to myself, but I was on a humor website when this video popped up with a break-down of the Hyatt disaster. Not particularly relevant to my mock up for this staircase, but I can see how different designs could bring this into play.
 
Not to keep talking to myself, but I was on a humor website when this video popped up with a break-down of the Hyatt disaster. Not particularly relevant to my mock up for this staircase, but I can see how different designs could bring this into play.

Thanks everyone especially Ed.

So here's the big question-- I could do stringers and 2x12s, or individual platofrms framed with 2x4s and individually supported... All dimesnions being similar, I am thinking the platform approach will be much cheaper. Does everyone agree?
 
Thanks everyone especially Ed.

So here's the big question-- I could do stringers and 2x12s, or individual platofrms framed with 2x4s and individually supported... All dimesnions being similar, I am thinking the platform approach will be much cheaper. Does everyone agree?
The stringers and treads will cost around $380, but that doesn't count the lumber you will use to support the structure. Conversely you could probably do platforms for around $15 for a 2' x 8'. You'll need between 8 and 10 different platforms at which brings you to $150 and then you'll need to build up your steps. So you could be a little more cost effective by going the platform route (especially if you have some in stock). You'll probably end up around $450 with stringers and around $220 with platforms.

I'm trapped in the booth for a couple of hours again this morning, so if I don't come up with any other project to work on in here, I'll mock up how I picture a platform version.
 
It seems the appearance of the two options is significant and I would think a factor. I have no idea how "finished" these should be but two or three stringers and 2 by or 3 by treads would have to be much faster to build.
 
So here is what you originally asked for. 88" tall, ten steps. In my opinion, the worst part about this plan is the measurements. I needed a lot of decimals to make the steps rise evenly so you will need to be very precise with your measurements when making legs for these. Alternatively, make the top height a slightly different number. Currently each step is 8.8" which is 8 13/16". I work with high school students, in general, they don't do well with 1/16" increments. Additionally, the leg units and support structure are going to take quite a bit of time.

Pyramid Steps Platform version angle.jpg Pyramid Steps Platform version side.jpg Pyramid Steps Platform version.jpg
 
Did you forget OSHA? And if it's occupied - by performers or technicians or the public - it is required by law to meet building and fire codes. The person's means of egress at the middle of those stairs is either up or down those stairs and law requires every occupant be provided with a means of egress.
Yeah, About that. The rules, as followed by most theatres producing Plays and Operas should follow OSHA standards Everything backstage, escapes, egress and access should be within "standard" building codes and limits. Onstage as normal all 'normal' standard engineering should be employed, however, Stair Rise and Run, maximum elevation of ramps, surfaces, railings, and fall protection fall into Theatrical/entertainment standards. Equity claims jurisdiction over maximum allowable angle for rakes, ramps and other playing surfaces. When constructing anythingnon standard as a TD I always consulted with the Equity rep on the show and if a deviation from a standard flat surface presented itself as part of the design the equity office in always received copies of the drawings for review.
All theatres should, enforce standard construction site safety measures during the rehearsal process. If there is an elevated walkway (a mountain path per se) it should have adequate railings throughout the rehearsal process. if the railing is not a scenic element, however, it is to be removed during tech rehearsals and performances.
The idea, as I have reviewed with several A'sHJ is that in a performance situation the actors and technicians are trained to the conditions they are working in.
As far as the Stage being a "Means of Egress" no, it is not nor should it EVER be considered a Means of Egress. It is a performance space just like an arena floor. there is to be NO unauthorized or qualified or unattended member of the public on the stage or in ANY performance area without proper approval or Accompaniment.

No, I haven't forgotten about OSHA, and while you "technically" say they have Jurisdiction everywhere, the Local AHJ is the primary arbiter of who has jurisdiction. If Scenic Designers and Technical directors were to follow you interpretation scenery and Stage Design would turn into cubes with soft edges and Handrails everywhere. That does not serve the Art. Acting, Dancing, Performing are more than a factory floor job and to that end they are rehearsed, studied, choreographed.
 
Actors Equity can't "claim jurisdiction over" OSHA for employees in the US. They can have more stringent requirements but they cannot relax or usurp OSHA regulation. AHJ's and building officials are municipal or state employees most often, and are not responsible nor empowered to enforce federal law. With rare exception, no one is out there "enforcing" OSHA - but they can show up as a result of an incident. They certainly did when the panda bear fell into the orchestra pit at the Fox in Atlanta during a Christmas Carol, and OSHA has investigated other stage falls and cited the owner. I ofetn complain that no one at OSHA will say this is OK or that isn't, and that is why I support the codes with a local presence who for the most part are willing to try to work with you.

And every occupant of every part of of every building that is covered by the usual building and fire codes are required by law to have a means of egress. There is no getting around that. Can you talk to and get some variance for what we do? Often yes, but not guaranteed, and rarely expressly stated. Find a building official that disagrees - that it's OK to effectively "lock" someone on a stage and not afford then a way out.

Check here https://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=INTERPRETATIONS&p_id=22337 where an OSHA director states it pretty clearly. Yes, is a guard rail or compliant rise and run geometry always required? No - but to say that because it's a stage you don't have to concern yourselves with such things is irresponsible and bull pucky. Even NFPA's Life Safety Code now requires you to protect people at the stage edge form falls where the exception from the requirement for a standard guardrail is used - which is for any fall hazard over 30".
 
So here is what you originally asked for. 88" tall, ten steps. In my opinion, the worst part about this plan is the measurements. I needed a lot of decimals to make the steps rise evenly so you will need to be very precise with your measurements when making legs for these. Alternatively, make the top height a slightly different number. Currently each step is 8.8" which is 8 13/16". I work with high school students, in general, they don't do well with 1/16" increments. Additionally, the leg units and support structure are going to take quite a bit of time.

View attachment 14538 View attachment 14539 View attachment 14540

Thanks Ed! This helps tremendously.
 
Actors Equity can't "claim jurisdiction over" OSHA for employees in the US. They can have more stringent requirements but they cannot relax or usurp OSHA regulation. AHJ's and building officials are municipal or state employees most often, and are not responsible nor empowered to enforce federal law. With rare exception, no one is out there "enforcing" OSHA - but they can show up as a result of an incident. They certainly did when the panda bear fell into the orchestra pit at the Fox in Atlanta during a Christmas Carol, and OSHA has investigated other stage falls and cited the owner. I ofetn complain that no one at OSHA will say this is OK or that isn't, and that is why I support the codes with a local presence who for the most part are willing to try to work with you.

And every occupant of every part of of every building that is covered by the usual building and fire codes are required by law to have a means of egress. There is no getting around that. Can you talk to and get some variance for what we do? Often yes, but not guaranteed, and rarely expressly stated. Find a building official that disagrees - that it's OK to effectively "lock" someone on a stage and not afford then a way out.

Check here https://www.osha.gov/pls/oshaweb/owadisp.show_document?p_table=INTERPRETATIONS&p_id=22337 where an OSHA director states it pretty clearly. Yes, is a guard rail or compliant rise and run geometry always required? No - but to say that because it's a stage you don't have to concern yourselves with such things is irresponsible and bull pucky. Even NFPA's Life Safety Code now requires you to protect people at the stage edge form falls where the exception from the requirement for a standard guardrail is used - which is for any fall hazard over 30".

I'll take my thirty five years of actually doing theatrical productions and working with AHJ's in practical application of codes on the state and national level and bank on it it over your comments of 'Bull Puckey'.

I do not believe ANYONE mentioned locking someone on stage, did they? Was I not Paying attention to the OP? I believe the question was concerning whether or not one could deviate from the 8/12 7/11 "standard" stair rise/run
The simple answer without hyperbolic "Well according to..." is Yes, you may. on Stage. as a scenic element. as long as proper training and safety measures are taking by the actors and people working on stage. it is NOT a public space.
The stage is NOT a means of Egress for the Audience. It never has been and NO theatre is designed for that as an intention unless we're talking a Blackbox in which case you better make damn sure you provide adequate exit lighting and fire lanes for escape. . Show me a "means of egress within 32'" of a performer on a wire in Ka.

Actors and Technicians are trained for use of the Set. It is a Tool. EVERY backstage area MUST comply with standard Life Safety codes. But please, show me the handrails and "No more than 3/4" rise to a foot" ramp on Ka.
 
I'll take my thirty five years of actually doing theatrical productions and working with AHJ's in practical application of codes on the state and national level and bank on it it over your comments of 'Bull Puckey'.

I do not believe ANYONE mentioned locking someone on stage, did they? Was I not Paying attention to the OP? I believe the question was concerning whether or not one could deviate from the 8/12 7/11 "standard" stair rise/run
The simple answer without hyperbolic "Well according to..." is Yes, you may. on Stage. as a scenic element. as long as proper training and safety measures are taking by the actors and people working on stage. it is NOT a public space.
The stage is NOT a means of Egress for the Audience. It never has been and NO theatre is designed for that as an intention unless we're talking a Blackbox in which case you better make damn sure you provide adequate exit lighting and fire lanes for escape. . Show me a "means of egress within 32'" of a performer on a wire in Ka.

Actors and Technicians are trained for use of the Set. It is a Tool. EVERY backstage area MUST comply with standard Life Safety codes. But please, show me the handrails and "No more than 3/4" rise to a foot" ramp on Ka.

Any or all parts of the stage are a means of egress for the occupants on the stage. All occupants - audience or actors or technicians or the janitor - must be provided with a means of egress. It's a basic tenet of the building and fire codes, and of OSHA requirements.

I can cite laws that say yes you do have to provide all occupants on stage with a means of egress - an unobstructed way out of the building to the public way. Can you show me where this is contravened by law, or have you just gotten away with it, as many people have?

OSHA does permit alternate means of protection. I believe, for instance, KA has a written plan for getting people out, where each part and action has been considered. They did not just conceive of the act and do it without a plan in place for each case where the normal prescriptive devices - guards, stair geometry, marking, etc. weren't possible. We should encourage the same thought for a high school, college, or community theatre event - to think about and have a plan for safety for everybody in place BEFORE the incident occurs. I reject what seems like an attitude to just ignore safety because it's a stage or art, and that a handrail or normal rise is not possible so do nothing to protect those people from fall hazards. It does seem to be what you are advocating for and claim to have done a lot.

If the OP wants to build a stair with 8.8" risers that's fine - but think about how to protect the people that are using it from the known hazard, just as routinely as one wears a hard hat, high visibility vest, steel soled shoes, and eye protection on a construction site. Those requirements are a result of study and thought and more and do prevent injuries from the normal hazards of construction.
 
I wanted to follow up on this.... I appreciate all of the advice....
I ended up going with individual platforms 1 foot deep, with legs. I went with a 7.25 " rise and they worked flawlessly. This is the first set of stairs I have built not using a stringer, and these things were rock solid once fastened together. I will use this method from here on out.

Here is a pic just after strike and another production photo.

https://drive.google.com/open?id=0B52H4oP6S5zlTDFDYWIwTXo0ckU

https://goo.gl/photos/kxJLgPSjYvC7YUGQ9
 
Just a reminder here:

(I would) make sure each step is individually supported, not in any way supported by steps further down. An installation contractor screwing that up was the root cause behind the Kansas City Hyatt disaster in the 90s.

I'm not sure that's applicable here, but some designs might go that way, so I figured I'd point it out.

Funniest thing:

I'm mostly a booth guy, but I got to help set up some Wenger for the Fringe festival one of my houses recently hosted, and they do exactly the thing I was warning about: the legs of the taller platforms, used for audience seating, *sit on top of* the platforms of lower ones; so each leg carries some of its own platform's load, and some of that above/behind it. And I hadn't known that then.
 
Funniest thing:

I'm mostly a booth guy, but I got to help set up some Wenger for the Fringe festival one of my houses recently hosted, and they do exactly the thing I was warning about: the legs of the taller platforms, used for audience seating, *sit on top of* the platforms of lower ones; so each leg carries some of its own platform's load, and some of that above/behind it. And I hadn't known that then.
Funniest thing:

I'm mostly a booth guy, but I got to help set up some Wenger for the Fringe festival one of my houses recently hosted, and they do exactly the thing I was warning about: the legs of the taller platforms, used for audience seating, *sit on top of* the platforms of lower ones; so each leg carries some of its own platform's load, and some of that above/behind it. And I hadn't known that then.
Funniest thing:

I'm mostly a booth guy, but I got to help set up some Wenger for the Fringe festival one of my houses recently hosted, and they do exactly the thing I was warning about: the legs of the taller platforms, used for audience seating, *sit on top of* the platforms of lower ones; so each leg carries some of its own platform's load, and some of that above/behind it. And I hadn't known that then.