2. There are two different ways of wiring the female
Socapex outlets, and each requires the same wiring in the
break-out. This is to idiot-proof plugging a 120V BO into a 208V
outlet, and is used by Christie and some others (like the
Strand LightRack, as discussed here:
https://www.controlbooth.com/threads/etc-sensor-or-strand-light-rack.15476/ )
The "normal" way:_____The "ChristieLites and
Strand" way:
Pin#
Ckt# Use:
Phase:_Pin#
Ckt# Use:
Phase:
1 1-LOAD L1 A__________1 1-LOAD L1 A
2 1-LOAD L2 B__________2 2-LOAD L1 A
3 2-LOAD L1 C__________3 1-LOAD L2 B
4 2-LOAD L2 A__________4 2-LOAD L2 B
5 3-LOAD L1 B__________5 3-LOAD L1 B
6 3-LOAD L2 C__________6 4-LOAD L1 B
7 4-LOAD L1 A__________7 3-LOAD L2 C
8 4-LOAD L2 B__________8 4-LOAD L2 C
9 5-LOAD L1 C__________9 5-LOAD L1 C
10 5-LOAD L2 A________10 6-LOAD L1 C
11 6-LOAD L1 B________11 5-LOAD L2 A
12 6-LOAD L2 C________12 6-LOAD L2 A
13-18
GROUND -________13-18
GROUND -
19 N/C -_______________19 N/C -
(Phasing may not be accurate for all distros. Some go AB,CA,BC,AB,CA,BC... Others go AB,BC,CA,AB,BC,CA...)
The "normal"
break-out can be used for either 120 or 208, one just has to change the six female outlets. The "other" offers the benefit of passing no
power if a 120 is connected to a 208, as the
potential difference between hot and
neutral is zero.