Yeah... thats the thing. I saw that, but I've seen lots of things on the internet that code has opinions about
I'm curious how they get all three
neutral and
ground wires into the 21-30 terminals, would expect it to need to be something like a molded
twofer.
Very good
point. It sure doesn't look like it's wired with #10AWG. No way three #10's are going into that
neutral terminal. Oh wait, I just read post #6.
This
NEC wording is germane to this non-compliant device:
520.2 Definitions.
Adapter. A device used to adapt a
circuit from one configuration
of an attachment
plug or
receptacle to another configuration
with the same current rating.
The we have 520.68(B):
(B) Conductor Ampacity. The ampacity of conductors shall be
as given in 400.5, except multiconductor, listed, extra-hard
usage
portable cords that are not in direct contact with equipment
containing heat-producing elements shall be permitted
to have their
ampacity determined by Table 520.44(C)(3).
Maximum load
current in any
conductor with an
ampacity
determined by Table 520.44(C)(3) shall not exceed the values
in Table 520.44(C)(3). Where the
ampacity adjustment factors
of Table 520.44(C)(3)(a) are applied for more than three
current-carrying conductors in a
portable cord, the
load diversity
shall be 50 percent or less.
And then we have 520.69 (A):
520.69 Adapters. Adapters, two-fers, and other single- and
multiple-circuit
outlet devices shall comply with 520.69(A), (B),
and (C).
(A) No Reduction in
Current Rating. Each
receptacle and its
corresponding cable shall have the same
current and
voltage
rating as the
plug supplying it. It shall not be utilized in a
stage
circuit with a greater
current rating.
ST