JD is right. Let's do some math here:
12 x 20A dimmers = 240A total
4 x 20A = total load per each of the three neutral conductors
Assume best case that three of the four dimmers are on different phases. In that case 20A (max imbalance load) x 1.30 (non linear load ampacity adjustment)=26A
Now add the fourth dimmer, which is a straight imbalance: 26A + 20A =46A
Now, it is entirely possible that a #10AWG 125C conductor could handle 46A to UL's satisfaction. Here's the problem: the outlet terminations are rated at 60C, and they are used as part of the daisy chain.
75C per HUBBELL HBL2310 AC Receptacle NEMA L5-20 Female Black 125 Volt 20 Amp - Our Item #: 5879, Category: Receptacles / Wall Plate : StayOnline.com... But you're right, that's far less than 125C (Probably why I'm replacing connectors with some nasty damage...)
[edit to remove idiocy]*see post further on*
While the CD-80 pack is a venerable example of portable dimming, this neutral daisy chaining is an extremely marginal design, and one that can be easily improved by wiring a single neutral conductor to each pair of outlets on a dimmer, as long as you're in there tearing out burned wires and outlets. After all, there's a reason they burned, and I don't buy the male plugs as the culprit.
Based on the damage I saw, I don't see anything else possible as the culprit... The neutral's further down the line are fine. The damage was isolated locally to the damaged connectors.
Please, don't misread disrespect into these posts If I'm being completely braindead, let me know!