@ David Ashton Posting in support. This is a major reason why 3 phase feeds originally installed to power a bank of (for example) 42 x 6 Kw SCR dimmers had their neutrals catching fire when the original racks were replaced with a greater quantity of appreciably smaller dimmers; racks of 2.4 Kw SCR dimmers for example. Here in Canada inspectors were initially caught off guard then, over a period of years ( and several fires ) eventually moved to double, and in some cases, even triple neutrals once the effects of triplen harmonics became more widely understood. I recall one senior electrician thinking something had to be wrong with his equipment when he found 60 Hz on each phase but three times 60 Hz on the single neutral. Thanks for your post.It's way more complex than P.F. in the old days a capacitive or inductive load would shift the P.F. and factories would have rooms of capacitors to correct it but with wave chopping and switch mode power supplies the wave forms are being distorted to hell and neutral currents can be more than per phase current, dimmers load up the beginning or end of the waveform and switch mode load up the middle, all in multiple constantly changing ways.
Toodleoo!
Ron Hebbard