Electrical Question:
We just did an install, and I'm trying to figure out what label I should toss on the drawing for the space as to any necessary electrical advisements.
Our system is fed via a 25KVA 120/240V (104A Max) transformer. The OCP breakers are 2-pole 120V/125A breakers. The feed to the dimmers is behind a 120/240V 100A 2-pole breaker, giving us two legs of 120V. There are 48 120V/20A dimmers in the Unison DR system, wired via a single phase strap kit. So 1/2 of the rack is on one leg, the other 1/2 if on the other leg.
Which advisements should I place on the plot of the space regarding limitations on power? I need this to be an idiot-proof document, so the key is keeping it as simple as possible, but covering all of the bases.
We just did an install, and I'm trying to figure out what label I should toss on the drawing for the space as to any necessary electrical advisements.
Our system is fed via a 25KVA 120/240V (104A Max) transformer. The OCP breakers are 2-pole 120V/125A breakers. The feed to the dimmers is behind a 120/240V 100A 2-pole breaker, giving us two legs of 120V. There are 48 120V/20A dimmers in the Unison DR system, wired via a single phase strap kit. So 1/2 of the rack is on one leg, the other 1/2 if on the other leg.
Which advisements should I place on the plot of the space regarding limitations on power? I need this to be an idiot-proof document, so the key is keeping it as simple as possible, but covering all of the bases.