Well-Known Member
I was reading over the BSR E1.6-4 - 201x, Portable Control of Fixed-Speed Electric Chain Hoists in the Entertainment Industry standard that's in review right now and I saw one line item that I thought was unintentionally tricky:
Would this mean that CM would have to stop using Aircraft cable for the ground in their control cables? I think it's a good idea to have it in there. The aircraft cable does a similar purpose as the support strands described later for single power/control cable systems described here:
Since it is insulated and made out of metal it is conducting and can serve as a grounding wire. I'm pretty sure Underwriters Laboratories signed off on that. But being a support strand seems to be an additional purpose other than grounding.
Thoughts anyone?
6.2 A grounding terminal or grounding type device shall not be used for purposes other than grounding.
Would this mean that CM would have to stop using Aircraft cable for the ground in their control cables? I think it's a good idea to have it in there. The aircraft cable does a similar purpose as the support strands described later for single power/control cable systems described here:
8.2.4...It shall be acceptable to have center core filler that eliminates any conductor from stress of movement. Support strands shall be acceptable as center filler.
Since it is insulated and made out of metal it is conducting and can serve as a grounding wire. I'm pretty sure Underwriters Laboratories signed off on that. But being a support strand seems to be an additional purpose other than grounding.
Thoughts anyone?