In the 2014 NEC, new section 406.15 was added:
406.15 Dimmer-Controlled Receptacles. A receptacle supplying lighting loads shall not be connected to a dimmer unless the plug/receptacle combination is a nonstandard configuration type that is specifically listed and identified for each such unique combination.
This section is intended to address misapplication of dimmers to receptacles in residential applications. The example cited by the submitter was a dimmer feeding under-cabinet LED rope lights not designed to be dimmed.
Leaving aside for the moment the validity (or not) of this new section, it has the potential to cause havoc in article 520 theatres and article 530 studios, where as a matter of course, dimmers feed all types of receptacles including E1.24 pin connectors and NEMA parallel blade and twist-lock connectors. Outlets may even change from dimmed to switched to constant power based on the configuration of the control system for a given production.
As such, your entertainment industry NEC team (Ken Vannice, Steve Terry, Mitch Hefter, Eddie Kramer, Mike Skinner) has created proposals for two Tentative Interim Amendments to section 520.45 and 530.21(A). If accepted, these TIA's will exempt theatres and studios from new section 406.15. TIA's are considered by the NFPA "of an emergency nature". That's good, because we view the potential negative effects of section 406.15 as an emergency.
You can find these TIA's (numbers 1151 and 1152) here:
http://www.nfpa.org/~/media/Files/Codes and standards/nfpa news/NFPANews0514.pdf
These TIA's are open to public comment until June 20, 2014. Please feel free to submit a comment in support.
If they pass, these TIA's will become part of the NEC until the next cycle, where they will go through the normal proposal process.
If you run into issues with consultants, engineers, inspectors, contractors, or others regarding section 406.15 in article 520 or 530 venues, I suggest you refer them to proposed TIA's 1151 and 1152 on the NFPA website.
ST
406.15 Dimmer-Controlled Receptacles. A receptacle supplying lighting loads shall not be connected to a dimmer unless the plug/receptacle combination is a nonstandard configuration type that is specifically listed and identified for each such unique combination.
This section is intended to address misapplication of dimmers to receptacles in residential applications. The example cited by the submitter was a dimmer feeding under-cabinet LED rope lights not designed to be dimmed.
Leaving aside for the moment the validity (or not) of this new section, it has the potential to cause havoc in article 520 theatres and article 530 studios, where as a matter of course, dimmers feed all types of receptacles including E1.24 pin connectors and NEMA parallel blade and twist-lock connectors. Outlets may even change from dimmed to switched to constant power based on the configuration of the control system for a given production.
As such, your entertainment industry NEC team (Ken Vannice, Steve Terry, Mitch Hefter, Eddie Kramer, Mike Skinner) has created proposals for two Tentative Interim Amendments to section 520.45 and 530.21(A). If accepted, these TIA's will exempt theatres and studios from new section 406.15. TIA's are considered by the NFPA "of an emergency nature". That's good, because we view the potential negative effects of section 406.15 as an emergency.
You can find these TIA's (numbers 1151 and 1152) here:
http://www.nfpa.org/~/media/Files/Codes and standards/nfpa news/NFPANews0514.pdf
These TIA's are open to public comment until June 20, 2014. Please feel free to submit a comment in support.
If they pass, these TIA's will become part of the NEC until the next cycle, where they will go through the normal proposal process.
If you run into issues with consultants, engineers, inspectors, contractors, or others regarding section 406.15 in article 520 or 530 venues, I suggest you refer them to proposed TIA's 1151 and 1152 on the NFPA website.