Not for nuttin, but at some point the parts and labor swapping to rated breakers may not be worth your while and the Lex Product box becomes cost effective. They are, if nothing else, very, very durable and worth the expense.
I stopped making my own orchestra music stand light distro's for this reason, finding the Lex E-Strings to be a better built solution for the long run. I see a LOT of these Lex boxes and I know they are heavily used in the film business, where stuff gets kicked around (unlike us civilized theatre folks)
@ Derek. I cannot understand the WiKi. I'm dense sometimes. I KNOW there's a rational reason as to why trying to pull 17 plus amps thru cable rated for 15 will heat the cable, making the breakers pop. I've experienced this. Please put on your "Academcian" cap for a second and learn us (or me).
Thanks in advance
Just to be clear, a piece of 14/3 type SO with two current-carrying conductors is rated at 18 amps per NEC table 400.5(A)(1) column B.
If a cable is used at more than its rated current it will overheat. This overheating can be transferred to circuit breaker thermal trip mechanism via the breaker terminals. This will cause the breaker to trip at lower than its rating. However, 17A on 14/3 is unlikely to cause this problem.
ST