The nipple on the end of the conduit and the tape around the wires may be throwing what I think I see off. It looks like 3 pieces of #4. What bothers me is the ground lug being mounted on the nipple. It also appears this is only a frame ground as I see what looks like both ends of the ground line (one cut off near the knockout.) Looks a lot like #12 ! Love the shredded wire strands laying about the bottom of the box! You need to call someone in big time.
the ground lug on the conduit coming in is a bonding bushing which appears to be installed correctly. I cant however tell what the lug on the end of the EGC (frame ground as you call it) is attached to. Is it just sitting there?
The EGC appears to be a #10 which would be the proper size for a circuit up to 60 amps. (Unless its a 60 amp circuit using #4 conductors due to voltage drop, then you would have to bump the EGC up a size)