its going to be 60 amps per
leg. So you will need either 6 60 amp single pole breakers or 3 60 amp 2 pole breakers. I would use a minimum of 6
awg, just you are going to be losing about 5 volts, so I'd personally go with at least 4
awg. For the
feeder i'd go with 2/0, just because of the distance. (I am using an electrical calculator to calculate the loads, am I no is CB responsible for any advice given or taken on here). If in doubt contact a qualified electrican. (and now the software disclamer) The Author cannot and does not warrant that any functions contained